Bonjour Arnaud,

 

Both servers are using ietf, here is what I am getting form the 2 versions:

 

***** OLD  0.41*****

 

                battery.runtime: 1080.0

                battery.runtime.low: 3

                battery.voltage: 154.0

                driver.name: snmp-ups

                driver.parameter.mibs: ietf

                driver.parameter.port: 172.30.1.48

                driver.version: 2.0.5

                driver.version.internal: 0.41

*Lost*   input.frequency: 60.0

*Lost*   input.voltage: 115.0

*Lost*   output.voltage: 120.0

                ups.firmware: ConnectUPS Web/SNMP Card V4.20

                ups.firmware.aux:   FP: 1.70

*Lost*   ups.load: 81.0                                  

                ups.mfr: Powerware Corporation

                ups.model: Powerware Profile

                ups.power: 2290.0

                ups.status: OL

 

 

 ***** NEW 0.42 ******

 

                battery.runtime: 1080.0

                battery.runtime.low: 3

                battery.voltage: 154.0

                driver.name: snmp-ups

                driver.parameter.mibs: ietf

*new*  driver.parameter.pollinterval: 2

                driver.parameter.port: 172.30.1.48

                driver.version: 2.2.1-

                driver.version.internal: 0.42 (mib: ietf 1.2)

*new*  input.phases: 2.0

*new*  output.frequency: 59.9

*new*  output.phases: 2.0

                ups.firmware:   FP: 1.70

                ups.firmware.aux: ConnectUPS Web/SNMP Card V4.20

                ups.mfr: Powerware Corporation

                ups.model: Powerware Profile

                ups.power: 2344.0

*new*  ups.serial: ID: TV115W0011, Msg: PF0821114UE0000

                ups.status: OL

 

Luc Comtois

 

From: Arnaud Quette [mailto:[EMAIL PROTECTED] 
Sent: June-13-08 9:29 AM
To: Comtois, Luc
Cc: [email protected]
Subject: [EMAIL PROTECTED] - Bayesian Filter detected spam - Re: [Nut-upsdev] 
Nut-snmp 0.42 vs 0.41

 

Bonjour Luc,

2008/6/12 Comtois, Luc <[EMAIL PROTECTED]>:

I am using nut-snmp driver on ubuntu 8.04 to query a Powerware ConnectUPS 
Web/SNMP Card V4.20.

 

With 0.41 I used to be able to query these field that are now gone with 0.42:

 

input.frequency

input.voltage

output.voltage

ups.load

 

Any idea how I can get ups.load back ?

without having dug (I've not taken care of this driver for an eternity), you're 
possibly using the Powerware mib (at least implicitly by not specifying 
otherwise), while the ietf one mgith be more suitable to get the needed data...
you should see which mib is used from the upsc output.
and you can override this by adding "mibs=ietf" in your ups.conf.

I'm currently firing up a pw with such a card to check and continue my training 
on these products. The above assertion seems confirmed...

Arnaud
-- 
Linux / Unix Expert R&D - MGE Office Protection Systems - http://www.mgeops.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://people.debian.org/~aquette/
Free Software Developer - http://arnaud.quette.free.fr/
--
Conseiller Municipal - Saint Bernard du Touvet -
http://www.SaintBernardDuTouvet.fr/
en charge de la Communication, de l'Informatique et des Technologies 

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev

Reply via email to