Citeren Kjell Claesson <[EMAIL PROTECTED]>: [ crossposting to nut-upsdev ]
> Hm, maybe I'm wrong this time too. The answer is about 120 mS and the delay > for answer in the read-buf is 250 mS, then a respond delay (sleep) of 200 mS. > > So 250-120=130+200=330 mS > > So the ups have about 330 mS to respond. This should be more than enough, > but I have seen slower equipment. Actually, it is even longer. :-) The delay after the last character is written to the serial port is 50ms. After that the driver sleeps for 200ms. When it wakes up again, within 250ms there must be something available for reading (not necessarily the full status, a single character would be sufficient). Sending one character to the UPS takes about 8ms, so the UPS has close to half a second for the first character of the reply. After reception of the first character, each subsequent read is subject to a new timeout of 250ms. Theoretically this means that it may take up to 100 + 200 + 14 x 250 = 3.8 seconds for a status poll in this driver. Nevertheless, I think it would be worthwhile to make a difference between real timeouts (where we don't get any reply at all) and failure to read full replies (which could also be due to receiver overruns). I will check the compatibility of such a change with the existing drivers before making this change. Best regards, Arjen -- Please keep list traffic on the list _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev