Arjen de Korte wrote:
> Citeren "David C. Rankin" <[EMAIL PROTECTED]>:
> 
> [...]
> 
>> You can count on me to do whatever dirty work you need done. Just give
>> me my
>> marching orders and I'll promptly provide what ever additional
>> information you
>> need.
> 
> Well, what I need is to correlate the actual battery voltage (as
> measured through a measurement instrument) to what the UPS itself
> reports. A minimum of two measurements is needed, with as much
> difference in battery voltage that is practical between them. Usually, a
> measurement with fully charged and (almost) fully discharged batteries
> will give me what I want. The dirty part here, is that you'll need to
> open the case of your UPS in order to get to the battery terminals.
> You'll also need something to measure voltage with. For the latter, a
> digital voltmeter would be required (a hand held multimeter is probably
> the most practical). Please do note that charged lead acid batteries are
> hazardous. Accidentally shorting out the terminals will cause severe
> personal injury, so if you don't know what you're doing, don't make any
> attempts here.
> 

No worries mate, I plug and switch hot, no need to shut off the breakers, just
takes more time... Just avoid me if I'm on a ladder. less I may reach down and
touch you on the shoulder with the kiss of Edison.....

        Seriously, I'm fine with it and have a great digital multimeter as 
well. At
least this time it will be a hell of a lot easier than measuring the pinout and
DTR, RTS and TD voltages for another little ups problem:

http://www.3111skyline.com/download/ups/rs232_aggie-pin-tester.jpg

        I didn't want to do the yard tomorrow anyway.... I'll see if I can get 
the
measurements to you after dinner along with the <path/to>/usbhid-ups -DD -a
nirvana_ups. Thanks for your help. I have really been meaning to chase this
issue down.

>> First, as requested, lsusb and lsusb -v (just in case):
>>
>> 16:37 nirvana~> lsusb
>> Bus 002 Device 002: ID 0764:0501 Cyber Power System, Inc.
>> Bus 002 Device 001: ID 0000:0000
>> Bus 001 Device 001: ID 0000:0000
> 
> I was just interested in the VID:PID combination here. Thanks.
> 
> [...]
> 
>> Now, I need your help. How do I give you "'usbhid-ups' driver running
>> with
>> debug level 2 (not higher)"? Just let me know and I'll send it
>> immediately.
>> Currently in my ups.conf file I have:
>>
>> [nirvana_ups]
>>         driver = usbhid-ups explore vendor="CPS"
>>         desc = "Nirvana UPS - Cyberpower 1000"
>>         port = /dev/hiddev0
>>
>> Do I need to add the extra parameters here? If so what?
> 
> First you need to kill any existing instances of the 'usbhid-ups'
> driver. Then fire it up as follows:
> 
>     <path/to>/usbhid-ups -DD -a nirvana_ups
> 
> This will run in the foreground until you stop it with ctrl-c or after
> sending it a SIGKILL signal. We're interested in the first 30 seconds
> worth of output only, after that it will only repeat.
> 
> Best regards, Arjen


-- 
David C. Rankin, J.D.,P.E.      |          openSoftware und SystemEntwicklung
Rankin Law Firm, PLLC           |             Countdown for openSuSE 11.1
www.rankinlawfirm.com           |        http://counter.opensuse.org/11.1/small

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev