Arjen,

        I did it. With the battery half-way out, still connected, and with the
multi-meter leads securely in the connectors, I got the right data this time.
As before, when you get time for a patch, I'm more than happy to test. The data 
is:

"Network UPS Tools upslog 2.2.2"                                
"logging status of ecstasy_ups to - (10s intervals)"

                       Volts    Volts
Time       Charge(%) indicated (actual) "Comments"

10:59:49 AM     100     20.2    13.7    
10:59:59 AM     100     20.2    13.7    
11:00:09 AM     100     20.2    13.7    "Power Loss"
11:00:19 AM     79      16.3    11.75   
11:00:29 AM     81      16.3            
11:00:39 AM     82      16.3    11.7    
11:00:49 AM     81      17.1    11.68   
11:00:59 AM     81      17.1    11.67   
11:01:09 AM     79      17.1    11.65   
11:01:19 AM     79      17.1    11.63   
11:01:29 AM     78      17.1    11.61   
11:01:39 AM     78      17.1    11.6    
11:01:49 AM     78      17      11.58   
11:01:59 AM     75      17      11.57   
11:02:09 AM     74      17      11.54   
11:02:19 AM     70      17      11.52   
11:02:29 AM     70      16.9    11.48   
11:02:39 AM     70      16.9            
11:02:49 AM     74      16.9    11.52   
11:02:59 AM     62      16.9    11.47   
11:03:09 AM     62      16.9    11.41   
11:03:19 AM     62      16.9    11.37   
11:03:29 AM     59      16.6    11.33   
11:03:39 AM     59      16.6    11.33   
11:03:49 AM     56      16.6    11.28   
11:03:59 AM     52      16.5    11.65   "Monitor off"
11:04:09 AM     58      16.5    11.71   
11:04:19 AM     58      16.5            
11:04:29 AM     57      17.1            
11:04:39 AM     47      17.1    11.34   "Monitor on"
11:04:49 AM     46      17.1    11.28   
11:04:59 AM     46      16.3    11.22   
11:05:09 AM     41      16.3    11.16   
11:05:19 AM     35      16.3    11.07   
11:05:29 AM     35      16.3    11      
11:05:39 AM     30      16.2    10.96   
11:05:49 AM     25      16.2    10.92   
11:05:59 AM     21      16.2    10.87   
11:06:09 AM     21      15.9    10.8    
11:06:19 AM     17      15.9    10.73   
11:06:29 AM     13      15.9            
11:06:39 AM     23      16.3    11.18   "Monitor off"
11:06:49 AM     23      16.3    11.16   
11:06:59 AM     23      16.3    11.15   
11:07:09 AM     23      16.3            
11:07:19 AM     22      16.3    10.57   
11:07:29 AM     9       16.3    10.51   "Monitor on"
11:07:39 AM     6       15.4    10.5    

        The .csv file is:

http://www.3111skyline.com/download/ups/CyberPower/voltages_measured-discharge.csv

        The openOffice calc file is:

http://www.3111skyline.com/download/ups/CyberPower/voltages_measured-discharge.ods

Thank you for you help!

-- 
David C. Rankin, J.D.,P.E.      |          openSoftware und SystemEntwicklung
Rankin Law Firm, PLLC           |             Countdown for openSuSE 11.1
www.rankinlawfirm.com           |        http://counter.opensuse.org/11.1/small

-- To the list

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev

Reply via email to