David C. Rankin wrote:
> Arjen de Korte wrote:
>> Citeren "David C. Rankin" <[email protected]>:
>>
>>> Umm... I can't find a ./configure. I know this is something basic.
>>> What do I
>>> do to get one or turn the configure.in file into one? Thanks.
>> You seem to have grabbed everything from the SVN trunk, right? In that
>> case, you need to have a bunch of autotools installed and run
>> 'autoreconf --install'.
>>
>> Best regards, Arjen
>
> Arjen:
>
> God I hate it when the answer is so simple:
>
> 15:47 nirvana:~/linux/apps/nut-2.2.2-trunk> autoreconf --install
> configure.in:14: installing `./missing'
> configure.in:14: installing `./install-sh'
> clients/Makefile.am: installing `./depcomp'
> 15:48 nirvana:~/linux/apps/nut-2.2.2-trunk> l
> total 1928
> <snip>
> -rwxr-xr-x 1 david dcr 928449 2009-01-14 15:48 configure*
> -rw-r--r-- 1 david dcr 24641 2009-01-13 18:28 configure.in
> <snip>
>
> Worked like a charm. Thanks!
>
Arjen, Arnaud:
I seem to be doing something stupid again with the ./configure options.
I have
compiled r1715 and it starts just fine, but I cannot connect with upsc. I
configured nut on opensuse 10.3 like this:
./configure \
--with-user=upsd \
--with-group=daemon \
--with-usb \
--with-snmp \
--with-cgi
make, make install went fine and all was installed in /usr/local/bin. I
stopped 2.2.2 and then went to start 2.2.2-r1715. Before starting the new
version, I wanted to make sure I was using my working config so I moved all the
/usr/local/nut/etc/*.sample files to /usr/local/nut/etc/orig and then copied
my config and html files from /etc/ups to /usr/local/nut/etc/. Just to make
sure I was using my old config, I also set
First attempt to start failed because I hadn't created the
/var/state/ups
directory. No problem, I created it and then tried starting nut again with a
successful result:
[18:26 nirvana/usr/local/ups] # /usr/local/ups/bin/upsdrvctl start
Network UPS Tools - UPS driver controller 2.4.0-pre1-1715
Network UPS Tools - Generic HID driver 0.34 (2.4.0-pre1-1715)
USB communication driver 0.30
Using subdriver: CyberPower HID 0.2
All looked good. Then I went to check the values with upsc and:
[18:26 nirvana/usr/local/ups] # /usr/local/ups/bin/upsc Nirvana_UPS
Error: Connection failure: Connection refused
Huh? I checked with ps ax to make sure it was running:
31886 ? Ss 0:00 /usr/local/ups/bin/usbhid-ups -a nirvana_ups
I tried one more time to connect and then shutdown and went back to the
rpm
install of nut:
[18:28 nirvana/usr/local/ups] # /usr/local/ups/bin/upsc Nirvana_UPS
Error: Connection failure: Connection refused
[18:29 nirvana/usr/local/ups] # /usr/local/ups/bin/upsdrvctl stop
Network UPS Tools - UPS driver controller 2.4.0-pre1-1715
[18:30 nirvana/usr/local/ups] # rcupsd start
Starting NUT UPS drivers done
Starting NUT UPS server done
Starting NUT UPS monitor done
I then shutdown the rpm version and started r1715 in the debug mode
calling
usbhid-ups directly and everything looks like it is working, [Uh O -- the
voltage is still whacko at 20.3...] but I still can't connect? Here is the
debug output:
[22:54 nirvana/usr/local/ups] # bin/usbhid-ups -DD -a nirvana_ups
Network UPS Tools - Generic HID driver 0.34 (2.4.0-pre1-1715)
USB communication driver 0.30
debug level is '2'
upsdrv_initups...
Checking device (0000/0000) (002/001)
- VendorID: 0000
- ProductID: 0000
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 002
Trying to match device
Device does not match - skipping
Checking device (0764/0501) (001/002)
- VendorID: 0764
- ProductID: 0501
- Manufacturer: CPS
- Product: UPS CP1000AVRLCD
- Serial Number: unknown
- Bus: 001
Trying to match device
Device matches
HID descriptor length 387
Report Descriptor size = 387
Using subdriver: CyberPower HID 0.2
Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x01, Offset: 0,
Size: 8, Value: 1.000000
Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x02, Offset: 0,
Size: 8, Value: 2.000000
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x03, Offset:
0, Size: 8, Value: 4.000000
Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x04, Offset:
0, Size: 8, Value: 3.000000
Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x05, Offset: 0,
Size: 8, Value: 1.000000
Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x06, Offset: 0,
Size: 8, Value: 2.000000
Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x07, Offset:
0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x07,
Offset: 8, Size: 8, Value: 5.000000
Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, ReportID: 0x07,
Offset: 16, Size: 8, Value: 10.000000
Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x07,
Offset: 24, Size: 8, Value: 20.000000
Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x07,
Offset: 32, Size: 8, Value: 10.000000
Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x07,
Offset: 40, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x08, Offset:
0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x08,
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x08, Offset: 8,
Size: 16, Value: 2100.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x08, Offset:
8, Size: 16, Value: 2100.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input, ReportID: 0x08, Offset:
24, Size: 16, Value: 300.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, ReportID: 0x08,
Offset: 24, Size: 16, Value: 300.000000
Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x09, Offset: 0,
Size: 8, Value: 12.000000
Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x0a, Offset: 0, Size:
8, Value: 20.300000
^^^^^^^^^^^^^^^^^^^
Uuugh!
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x0b,
Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x0b,
Offset: 4, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID:
0x0b, Offset: 4, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x0d, Offset: 0,
Size: 8, Value: 3.000000
Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x0e, Offset: 0, Size:
8, Value: 120.000000
Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8,
Value: 122.000000
Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x10, Offset: 0,
Size: 8, Value: 90.000000
Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x10, Offset: 8,
Size: 8, Value: 140.000000
Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8,
Value: 122.000000
Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 0x13, Offset: 0, Size:
8, Value: 18.000000
Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8,
Value: 1.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.Boost, Type: Feature, ReportID: 0x17, Offset: 0, Size: 1,
Value: 0.000000
Path: UPS.Output.Overload, Type: Feature, ReportID: 0x17, Offset: 1, Size: 1,
Value: 0.000000
Path: UPS.Output.ConfigActivePower, Type: Feature, ReportID: 0x18, Offset: 0,
Size: 16, Value: 88.000000
Report descriptor retrieved (Reportlen = 387)
Found HID device
Detected a UPS: CPS/UPS CP1000AVRLCD
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x03, Offset:
0, Size: 8, Value: 4.000000
Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x04, Offset:
0, Size: 8, Value: 3.000000
Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x07,
Offset: 24, Size: 8, Value: 20.000000
Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x07,
Offset: 32, Size: 8, Value: 10.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x08,
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x08, Offset:
8, Size: 16, Value: 2100.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, ReportID: 0x08,
Offset: 24, Size: 16, Value: 300.000000
Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x09, Offset: 0,
Size: 8, Value: 12.000000
Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x0a, Offset: 0, Size:
8, Value: 20.300000
Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 0x13, Offset: 0, Size:
8, Value: 18.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8,
Value: 1.000000
Path: UPS.Output.ConfigActivePower, Type: Feature, ReportID: 0x18, Offset: 0,
Size: 16, Value: 88.000000
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID:
0x0b, Offset: 4, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0.000000
Path: UPS.Output.Boost, Type: Feature, ReportID: 0x17, Offset: 0, Size: 1,
Value: 0.000000
Path: UPS.Output.Overload, Type: Feature, ReportID: 0x17, Offset: 1, Size: 1,
Value: 0.000000
Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x0e, Offset: 0, Size:
8, Value: 120.000000
Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8,
Value: 122.000000
Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x10, Offset: 0,
Size: 8, Value: 90.000000
Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x10, Offset: 8,
Size: 8, Value: 140.000000
Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8,
Value: 122.000000
Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8,
Value: 1.000000
Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8,
Value: 1.000000
Path: UPS.Output.Test, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8,
Value: 1.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x0c,
Offset: 0, Size: 8, Value: 2.000000
upsdrv_initinfo...
upsdrv_updateinfo...
Got 6 HID objects...
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x0b,
Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x0b,
Offset: 4, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0.000000
Quick update...
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
dstate_init: sock /var/state/ups/usbhid-ups-nirvana_ups open on fd 5
upsdrv_updateinfo...
Got -110 HID objects...
Quick update...
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
upsdrv_updateinfo...
Got 3 HID objects...
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x08, Offset:
0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x08, Offset: 8,
Size: 16, Value: 2100.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input, ReportID: 0x08, Offset:
24, Size: 16, Value: 300.000000
Quick update...
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
upsdrv_updateinfo...
Got 6 HID objects...
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x0b,
Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x0b,
Offset: 4, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0.000000
Quick update...
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0.000000
upsdrv_updateinfo...
Got 3 HID objects...
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x08, Offset:
0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x08, Offset: 8,
Size: 16, Value: 2100.000000
Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input, ReportID: 0x08, Offset:
24, Size: 16, Value: 300.000000
Quick update...
Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0,
Size: 16, Value: 0.000000
Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0,
Size: 16, Value: -60.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0b,
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID:
0x0b, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size
I don't know what to make of the problem other than I either have a
./configure problem or I have a problem with my etc/*.conf config for 2.4.
What say the experts.
--
David C. Rankin, J.D.,P.E.
Rankin Law Firm, PLLC
510 Ochiltree Street
Nacogdoches, Texas 75961
Telephone: (936) 715-9333
Facsimile: (936) 715-9339
www.rankinlawfirm.com
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev