2009/3/23 Kjell Claesson <[email protected]>

> måndag 23 mars 2009 21:07:15 skrev  Arjen de Korte:
> Hi Arjen,
> > Citeren Kjell Claesson <[email protected]>:
> > > Author: keyson-guest
> > > Date: Mon Mar 23 17:37:37 2009
> > > New Revision: 1817
> > >
> > > Log:
> > > data/driver.list, add Eaton Powerware 9130 compatibility with bcmxcp
> > > and usbhid-ups.
> >
> > 1) Is this really true? I would have expected that this device would
> > be supported through bcmxcp (serial) and bcmxcp_usb (USB), like other
> > Powerware (now Eaton) devices. I'm actually surprised that one unit
> > does support such vastly different protocols (but I have been
> > surprised before).
> >
> Yes this is a surprise to me to. But to quote our Eaton guy Arnaud.
> "yup, this model is an hybrid one:
> the right way is bcmxcp for the serial port or usbhid-ups for the USB
> port."
>
> And when I asked where I could put it in the driver.list:
> "Eaton, both with the serial (bcmxcp) and usb (usbhid-ups) please."
>

I re confirm this assertion.
and also note that I was the first surprised by that hybridization!


> > 2) If it indeed is a HID PDC UPS, what are the VID:PID that it uses?
> > Just adding it to the list may not work if we don't already use this
> > combination for another device. In any case, I would to see the report
> > descriptor and initial variable dump, to see what level of support we
> > can expect from it (I 'collect' report descriptors for verifying the
> > hidparser and libhid code).
>
> You got me there, we don't know the VID:PID that it use!
> That was a bad mistake. Going to remove the usbhid-ups until it
> is confirmed.
>

VID:PID => 0463:ffff
in fact, this is an MGE base (HID core + USB/HID com) but needed bcmxcp for
compatibility with a big customer iirc.
note that I would otherwise have added this info (lacking VID:PID) ;-)
I've also added for info the 2 upsc outputs (from bcmxcp and usbhid-ups).
If some need the drivers debug output, please let me know.

Arnaud
-- 
Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://people.debian.org/~aquette/
Free Software Developer - http://arnaud.quette.free.fr/
ambient.temperature: 29
ambient.temperature.high: 40
battery.charge: 91
battery.runtime: 21256
battery.voltage:  55.2
driver.name: bcmxcp
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.4.1-1801:1802M
driver.version.internal: 0.21
input.frequency: 50.0
input.frequency.high: 53
input.frequency.low: 47
input.frequency.nominal: 50
input.transfer.boost.high: 195
input.transfer.high: 276
input.transfer.low: 130
input.transfer.trim.low: 253
input.voltage: 233.5
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 0
outlet.1.id: 1
outlet.1.status: Off
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 0
outlet.2.id: 2
outlet.2.status: Off
output.current:  0.0
output.current.nominal:  6.5
output.frequency:  0.0
output.phases: 1
output.voltage:   0.0
output.voltage.nominal: 230
ups.beeper.status: muted
ups.firmware: Cont:00.11 Inve:01.25
ups.load:   0.0
ups.model: PW9130 1500VA-T                  1500VA
ups.power: 0
ups.power.nominal: 1500
ups.serial: RA313A0538
ups.status: OFF
ups.temperature: 27
battery.charge: 92
battery.charge.low: 20
battery.runtime: 21319
battery.type: PbAc
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.1-1801:1802M
driver.version.data: MGE HID 1.12
driver.version.internal: 0.34
input.frequency: 50.0
input.transfer.high: 276
input.transfer.low: 130
input.voltage: 235.0
input.voltage.nominal: 230
outlet.1.delay.shutdown: 65535
outlet.1.delay.start: 0
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 2
outlet.1.status: off
outlet.1.switchable: yes
outlet.2.delay.shutdown: 65535
outlet.2.delay.start: 0
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 3
outlet.2.status: off
outlet.2.switchable: yes
outlet.desc: Main Outlet
outlet.id: 1
outlet.switchable: no
output.current: 0.00
output.frequency: 0.0
output.frequency.nominal: 50
output.voltage: 0.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 0125
ups.load: 0
ups.load.high: 102
ups.mfr: EATON Powerware 
ups.model: 9130  1500VA-T
ups.power: 0
ups.power.nominal: 1500
ups.productid: ffff
ups.realpower: 0
ups.serial: RA313A0538  
ups.status: OL CHRG OFF
ups.temperature: 302.0
ups.test.result: No test initiated
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 0463