Citeren Philip Ward <[email protected]>

However, it is not just unsupported OIDs that are a problem, but also
different OIDs.

output voltage is "1.3.6.1.2.1.33.1.4.4.1.2.1" on the af401a but ietf
has it at "1.3.6.1.2.1.33.1.4.4.1.2.0"
output current is "1.3.6.1.2.1.33.1.4.4.1.3.1" on the af401a but ietf
has it at "1.3.6.1.2.1.33.1.4.4.1.3.0"

Similarly for input.frequency, input.voltage and input.current. I'm not
sure that there is a way around these differences without either a new
mib, or changing the way that the driver scans the OID tree to try and
resolve them.

Have you already checked if there are firmware updates available for your SNMP card? These differences may not be intentional and chances are that there are updates available that make it conform to the IETF standard.

Best regards, Arjen
--