Hi Tim,
> I ran into a portability issue with drivers/bcmxcp.c in nut-2.4.1 on
> my UnixWare 7.1.4 machine. The error I get is
> .....
> UX:acomp: ERROR: "/opt/src/utils/nut-2.4.1/drivers/bcmxcp.c", line 835:
> integral constant expression expected .....
>
> Looking at the code we see
> .....
> int init_outlet(unsigned char len)
> {
> unsigned char answer[len];
> .....
>
> Although gcc can handle it, it's not portable C code.
>
> What size should the answer array be?
>
It depends on the ups.
In the upsdrv_initinfo parsing the ID Block you get the length of the
outlet_block.
---------------------------------
/* Size of outlet monitoring block */
outlet_block_len = get_word(answer+iIndex);
upsdebugx(2, "Length of outlet_block: %d\n", outlet_block_len);
iIndex += 2;
---------------------------------
If this block is larger that 8 this indicate more than one outlet. So we go to
setup and read the outlet. Also add the commands.
---------------------------------
/* Due to a bug in PW5115 firmware, we need to use blocklength > 8.
The protocol state that outlet block is only implemented if there is
at least 2 outlet block. 5115 has only one outlet, but has outlet
block! */
if (outlet_block_len > 8) {
len = init_outlet(outlet_block_len);
for(res = 1 ; res <= len ; res++) {
snprintf(outlet_name, sizeof(outlet_name)-1,
"outlet.%d.shutdown.return", res);
dstate_addcmd(outlet_name);
}
}
---------------------------
So setting the length of the answer from the ID_block. So from 0 - 20 at the
moment.
It would be possible to hardcode this len, and leave some space for 4 outlet.
Would be 2+6+6+6+6 = 26
Regards
Kjell
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev