I have attempted to create cpqpowermib.h for the snmp-ups driver. We use
HP UPSs and version 2 of the firmware for their AF401A management cards
use the CPQPOWER-MIB.

I have attached my current attempt (which builds and almost works
against nut 2.4.1). Once all is working I'll send in the finished
article for consideration. This file is based on ietfmib.h.

There are a couple of issues I'd like input on. Firstly I can't seem to
get input and output voltage to work. The code looks right to me
(compared with the corresponding code in ietfmib.h) but the values are
not showing when running upsc. Perhaps a fresh pair of eyes will spot
what I have missed.

Secondly CPQPOWER-MIB does not have a "Battery Status" field in the same
sense that IETF does. In order to get around this I have used Battery
Capacity instead. This is a percentage, so I've made values above 20 as
normal, and values of 20 and below as LB. If anyone has strong feelings
regarding this, or a better idea then please reply.

Finally, there is a temperature field (upsEnvAmbientTemp) which shows
the environmental temperature. There is no field for internal
temperature. I have used this value for ups.temperature. Is this what it
is for, or should ups.temperature be left blank?

You can find a description of CPQPOWER-MIB at
http://www.oidview.com/mibs/232/CPQPOWER-MIB.html

Regards,
-  
Philip Ward
Unix Systems Administrator
Ext 7274


-- 
The Sunday Times Scottish University of the Year 2009/2010
The University of Stirling is a charity registered in Scotland, 
 number SC 011159.

/*  cpqpowermib.h - data to monitor SNMP UPS with NUT
 *
 *  Copyright (C) 2002-2006 
 *  			Arnaud Quette <[email protected]>
 *  			Niels Baggesen <[email protected]>
 *
 *  Sponsored by MGE UPS SYSTEMS <http://www.mgeups.com>
 *
 *  This program is free software; you can redistribute it and/or modify
 *  it under the terms of the GNU General Public License as published by
 *  the Free Software Foundation; either version 2 of the License, or
 *  (at your option) any later version.
 *
 *  This program is distributed in the hope that it will be useful,
 *  but WITHOUT ANY WARRANTY; without even the implied warranty of
 *  MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE.  See the
 *  GNU General Public License for more details.
 *
 *
 *  You should have received a copy of the GNU General Public License
 *  along with this program; if not, write to the Free Software
 *  Foundation, Inc., 59 Temple Place, Suite 330, Boston, MA 02111-1307 USA
 *
 */

#define CPQPOWER_MIB_VERSION	"1.0"

/* SNMP OIDs set */
#define CPQPOWER_OID_UPS_MIB          "1.3.6.1.4.1.232.165.3"
#define CPQPOWER_OID_MFR_NAME         "1.3.6.1.4.1.232.165.3.1.1.0"	/* UPS-MIB::upsIdentManufacturer */
#define CPQPOWER_OID_MODEL_NAME       "1.3.6.1.4.1.232.165.3.1.2.0"	/* UPS-MIB::upsIdentModel */
#define CPQPOWER_OID_FIRMREV          "1.3.6.1.4.1.232.165.3.1.3.0"	/* UPS-MIB::upsIdentUPSSoftwareVersion */
#define CPQPOWER_OID_OEMCODE          "1.3.6.1.4.1.232.165.3.1.4.0"	/* UPS-MIB::upsIdentAgentSoftwareVersion */

#define CPQPOWER_OID_BATT_RUNTIME     "1.3.6.1.4.1.232.165.3.2.1.0"	/* UPS-MIB::upsEstimatedMinutesRemaining */
#define CPQPOWER_OID_BATT_VOLTAGE     "1.3.6.1.4.1.232.165.3.2.2.0"	/* UPS-MIB::upsBatteryVoltage */
#define CPQPOWER_OID_BATT_CURRENT     "1.3.6.1.4.1.232.165.3.2.3.0"	/* UPS-MIB::upsBatteryCurrent */
#define CPQPOWER_OID_BATT_CHARGE      "1.3.6.1.4.1.232.165.3.2.4.0"	/* UPS-MIB::upsBattCapacity */
#define CPQPOWER_OID_BATT_STATUS      "1.3.6.1.4.1.232.165.3.2.5.0"	/* UPS-MIB::upsBatteryAbmStatus */

#define CPQPOWER_OID_IN_FREQ          "1.3.6.1.4.1.232.165.3.3.1.0"	/* UPS-MIB::upsInputFrequency */
#define CPQPOWER_OID_IN_LINEBADS      "1.3.6.1.4.1.232.165.3.3.2.0"	/* UPS-MIB::upsInputLineBads */
#define CPQPOWER_OID_IN_LINES         "1.3.6.1.4.1.232.165.3.3.3.0"	/* UPS-MIB::upsInputNumPhases */

#define CPQPOWER_OID_IN_PHASE         "1.3.6.1.4.1.232.165.3.3.4.1.1"	/* UPS-MIB::upsInputPhase */
#define CPQPOWER_OID_IN_VOLTAGE       "1.3.6.1.4.1.232.165.3.3.4.1.2"	/* UPS-MIB::upsInputVoltage */
#define CPQPOWER_OID_IN_CURRENT       "1.3.6.1.4.1.232.165.3.3.4.1.3"	/* UPS-MIB::upsInputCurrent */
#define CPQPOWER_OID_IN_POWER         "1.3.6.1.4.1.232.165.3.3.4.1.4"	/* UPS-MIB::upsInputWatts */

#define CPQPOWER_OID_LOAD_LEVEL       "1.3.6.1.4.1.232.165.3.4.1.0"     /* UPS-MIB::upsOutputLoad */
#define CPQPOWER_OID_OUT_FREQUENCY    "1.3.6.1.4.1.232.165.3.4.2.0"	/* UPS-MIB::upsOutputFrequency */
#define CPQPOWER_OID_OUT_LINES        "1.3.6.1.4.1.232.165.3.4.3.0"	/* UPS-MIB::upsOutputNumPhases */

#define CPQPOWER_OID_OUT_PHASE        "1.3.6.1.4.1.232.165.3.4.4.1.1"	/* UPS-MIB::upsOutputPhase */
#define CPQPOWER_OID_OUT_VOLTAGE      "1.3.6.1.4.1.232.165.3.4.4.1.2"	/* UPS-MIB::upsOutputVoltage */
#define CPQPOWER_OID_OUT_CURRENT      "1.3.6.1.4.1.232.165.3.4.4.1.3"	/* UPS-MIB::upsOutputCurrent */
#define CPQPOWER_OID_OUT_POWER        "1.3.6.1.4.1.232.165.3.4.4.1.4"	/* UPS-MIB::upsOutputWatts */

#define CPQPOWER_OID_POWER_STATUS     "1.3.6.1.4.1.232.165.3.4.5.0"	/* UPS-MIB::upsOutputSource */

#define CPQPOWER_OID_AMBIENT_TEMP     "1.3.6.1.4.1.232.165.3.6.1.0"     /* UPS-MIB::upsEnvAmbientTemp */

/* Defines for CPQPOWER_OID_POWER_STATUS (1) */
info_lkp_t cpqpower_pwr_info[] = {
	{ 1, ""       /* other */ },
	{ 2, "OFF"    /* none */ },
	{ 3, "OL"     /* normal */ },
	{ 4, "BYPASS" /* bypass */ },
	{ 5, "OB"     /* battery */ },
	{ 6, "BOOST"  /* booster */ },
	{ 7, "TRIM"   /* reducer */ },
	{ 8, "PCAP"   /* parallelCapacity */ },
	{ 9, "PRED"   /* parallelRedundant */ },
	{ 10, "HIEFF" /* HighEfficiencyMode */ },
	{ 0, "NULL" }
} ;

/* Defines for CPQPOWER_OID_BATT_STATUS (2) */
info_lkp_t cpqpower_batt_info[] = {
	{ 100, ""   /* batteryNormal */ },
	{ 99, ""   /* batteryNormal */ },
	{ 98, ""   /* batteryNormal */ },
	{ 97, ""   /* batteryNormal */ },
	{ 96, ""   /* batteryNormal */ },
	{ 95, ""   /* batteryNormal */ },
	{ 94, ""   /* batteryNormal */ },
	{ 93, ""   /* batteryNormal */ },
	{ 92, ""   /* batteryNormal */ },
	{ 91, ""   /* batteryNormal */ },
	{ 90, ""   /* batteryNormal */ },
	{ 89, ""   /* batteryNormal */ },
	{ 88, ""   /* batteryNormal */ },
	{ 87, ""   /* batteryNormal */ },
	{ 86, ""   /* batteryNormal */ },
	{ 85, ""   /* batteryNormal */ },
	{ 84, ""   /* batteryNormal */ },
	{ 83, ""   /* batteryNormal */ },
	{ 82, ""   /* batteryNormal */ },
	{ 81, ""   /* batteryNormal */ },
	{ 80, ""   /* batteryNormal */ },
	{ 79, ""   /* batteryNormal */ },
	{ 78, ""   /* batteryNormal */ },
	{ 77, ""   /* batteryNormal */ },
	{ 76, ""   /* batteryNormal */ },
	{ 75, ""   /* batteryNormal */ },
	{ 74, ""   /* batteryNormal */ },
	{ 73, ""   /* batteryNormal */ },
	{ 72, ""   /* batteryNormal */ },
	{ 71, ""   /* batteryNormal */ },
	{ 70, ""   /* batteryNormal */ },
	{ 69, ""   /* batteryNormal */ },
	{ 68, ""   /* batteryNormal */ },
	{ 67, ""   /* batteryNormal */ },
	{ 66, ""   /* batteryNormal */ },
	{ 65, ""   /* batteryNormal */ },
	{ 64, ""   /* batteryNormal */ },
	{ 63, ""   /* batteryNormal */ },
	{ 62, ""   /* batteryNormal */ },
	{ 61, ""   /* batteryNormal */ },
	{ 60, ""   /* batteryNormal */ },
	{ 59, ""   /* batteryNormal */ },
	{ 58, ""   /* batteryNormal */ },
	{ 57, ""   /* batteryNormal */ },
	{ 56, ""   /* batteryNormal */ },
	{ 55, ""   /* batteryNormal */ },
	{ 54, ""   /* batteryNormal */ },
	{ 53, ""   /* batteryNormal */ },
	{ 52, ""   /* batteryNormal */ },
	{ 51, ""   /* batteryNormal */ },
	{ 50, ""   /* batteryNormal */ },
	{ 49, ""   /* batteryNormal */ },
	{ 48, ""   /* batteryNormal */ },
	{ 47, ""   /* batteryNormal */ },
	{ 46, ""   /* batteryNormal */ },
	{ 45, ""   /* batteryNormal */ },
	{ 44, ""   /* batteryNormal */ },
	{ 43, ""   /* batteryNormal */ },
	{ 42, ""   /* batteryNormal */ },
	{ 41, ""   /* batteryNormal */ },
	{ 40, ""   /* batteryNormal */ },
	{ 39, ""   /* batteryNormal */ },
	{ 38, ""   /* batteryNormal */ },
	{ 37, ""   /* batteryNormal */ },
	{ 36, ""   /* batteryNormal */ },
	{ 35, ""   /* batteryNormal */ },
	{ 34, ""   /* batteryNormal */ },
	{ 33, ""   /* batteryNormal */ },
	{ 32, ""   /* batteryNormal */ },
	{ 31, ""   /* batteryNormal */ },
	{ 30, ""   /* batteryNormal */ },
	{ 29, ""   /* batteryNormal */ },
	{ 28, ""   /* batteryNormal */ },
	{ 27, ""   /* batteryNormal */ },
	{ 26, ""   /* batteryNormal */ },
	{ 25, ""   /* batteryNormal */ },
	{ 24, ""   /* batteryNormal */ },
	{ 23, ""   /* batteryNormal */ },
	{ 22, ""   /* batteryNormal */ },
	{ 21, ""   /* batteryNormal */ },
	{ 20, "LB" /* batteryLow */ },
	{ 19, "LB" /* batteryLow */ },
	{ 18, "LB" /* batteryLow */ },
	{ 17, "LB" /* batteryLow */ },
	{ 16, "LB" /* batteryLow */ },
	{ 15, "LB" /* batteryLow */ },
	{ 14, "LB" /* batteryLow */ },
	{ 13, "LB" /* batteryLow */ },
	{ 12, "LB" /* batteryLow */ },
	{ 11, "LB" /* batteryLow */ },
	{ 10, "LB" /* batteryLow */ },
	{ 9, "LB" /* batteryLow */ },
	{ 8, "LB" /* batteryLow */ },
	{ 7, "LB" /* batteryLow */ },
	{ 6, "LB" /* batteryLow */ },
	{ 5, "LB" /* batteryLow */ },
	{ 4, "LB" /* batteryLow */ },
	{ 3, "LB" /* batteryLow */ },
	{ 2, "LB" /* batteryLow */ },
	{ 1, "LB" /* batteryLow */ },
} ;

/* Defines for CPQPOWER_OID_TEST_RES */
info_lkp_t cpqpower_test_res_info[] = {
	{ 1, "Done and passed" },
	{ 2, "Done and warning" },
	{ 3, "Done and error" },
	{ 4, "Aborted" },
	{ 5, "In progress" },
	{ 6, "No test initiated" },
	{ 0, "NULL" }
} ;

#define CPQPOWER_OID_SD_AFTER_DELAY	 "1.3.6.1.4.1.232.165.3.1.8.2"	/* UPS-MIB::upsShutdownAfterDelay */
#define CPQPOWER_OFF_DO		0

#define CPQPOWER_OID_ALARM_OB "1.3.6.1.4.1.232.165.3.1.6.3.2"	/* UPS-MIB::upsAlarmOnBattery */

info_lkp_t cpqpower_alarm_ob[] = {
	{ 1, "OB" },
	{ 0, "NULL" }
} ;
		
#define CPQPOWER_OID_ALARM_LB "1.3.6.1.4.1.232.165.3.1.6.3.3"	/* UPS-MIB::upsAlarmLowBattery */

info_lkp_t cpqpower_alarm_lb[] = {
	{ 1, "LB" },
	{ 0, "NULL" }
} ;

/* Missing data
   CAL   - UPS is performing calibration
   OVER  - UPS is overloaded
   RB    - UPS battery needs to be replaced
   FSD   - UPS is in forced shutdown state (slaves take note)
*/

/* Snmp2NUT lookup table */

snmp_info_t cpqpower_mib[] = {
	/* UPS page */
	/* info_type, info_flags, info_len, OID, dfl, flags, oid2info, setvar */
	{ "ups.mfr", ST_FLAG_STRING, SU_INFOSIZE, CPQPOWER_OID_MFR_NAME, "Generic",
		SU_FLAG_STATIC, NULL },
	{ "ups.model", ST_FLAG_STRING, SU_INFOSIZE, CPQPOWER_OID_MODEL_NAME, "Generic SNMP UPS",
		SU_FLAG_STATIC, NULL },
	{ "ups.firmware", ST_FLAG_STRING, SU_INFOSIZE, CPQPOWER_OID_FIRMREV, "",
		SU_FLAG_STATIC, NULL },
	{ "ups.oemcode", ST_FLAG_STRING, SU_INFOSIZE, CPQPOWER_OID_OEMCODE, "",
		SU_FLAG_STATIC, NULL },
	{ "ups.load", 0, 1.0, CPQPOWER_OID_LOAD_LEVEL , "",
		SU_OUTPUT_1, NULL },
	{ "ups.power", 0, 1.0, CPQPOWER_OID_OUT_POWER ".0", "",
		0, NULL },
	{ "ups.status", ST_FLAG_STRING, SU_INFOSIZE, CPQPOWER_OID_POWER_STATUS, "OFF",
		SU_STATUS_PWR, &cpqpower_pwr_info[0] },
	{ "ups.status", ST_FLAG_STRING, SU_INFOSIZE, CPQPOWER_OID_BATT_CHARGE, "",
		SU_STATUS_BATT, &cpqpower_batt_info[0] },
	{ "ups.temperature", 0, 1.0, CPQPOWER_OID_AMBIENT_TEMP, "",
		0, NULL },

	/* Battery page */
	{ "battery.charge", 0, 1.0, CPQPOWER_OID_BATT_CHARGE, "",
		0, NULL },
	{ "battery.runtime", 0, 60.0, CPQPOWER_OID_BATT_RUNTIME, "",
		0, NULL },
	{ "battery.voltage", 0, 0.1, CPQPOWER_OID_BATT_VOLTAGE, "",
		0, NULL },
	{ "battery.current", 0, 0.1, CPQPOWER_OID_BATT_CURRENT, "",
		0, NULL },

	/* Output page */
	{ "output.phases", 0, 1.0, CPQPOWER_OID_OUT_LINES, "",
		SU_FLAG_SETINT, NULL, &output_phases },
	{ "output.frequency", 0, 0.1, CPQPOWER_OID_OUT_FREQUENCY, "",
		0, NULL },
	{ "output.phase", 0, 1.0, CPQPOWER_OID_OUT_PHASE ".1", "",
		SU_OUTPUT_1, NULL },
	{ "output.voltage", 0, 1.0, CPQPOWER_OID_OUT_VOLTAGE ".1", "",
		SU_OUTPUT_1, NULL },
	{ "output.current", 0, 0.1, CPQPOWER_OID_OUT_CURRENT ".1", "",
		SU_OUTPUT_1, NULL },
	{ "output.realpower", 0, 1.0, CPQPOWER_OID_OUT_POWER ".1", "",
		SU_OUTPUT_1, NULL },
	{ "output.L1-N.voltage", 0, 1.0, CPQPOWER_OID_OUT_VOLTAGE ".1", "",
		SU_OUTPUT_3, NULL },
	{ "output.L2-N.voltage", 0, 1.0, CPQPOWER_OID_OUT_VOLTAGE ".2", "",
		SU_OUTPUT_3, NULL },
	{ "output.L3-N.voltage", 0, 1.0, CPQPOWER_OID_OUT_VOLTAGE ".3", "",
		SU_OUTPUT_3, NULL },
	{ "output.L1.current", 0, 0.1, CPQPOWER_OID_OUT_CURRENT ".1", "",
		SU_OUTPUT_3, NULL },
	{ "output.L2.current", 0, 0.1, CPQPOWER_OID_OUT_CURRENT ".2", "",
		SU_OUTPUT_3, NULL },
	{ "output.L3.current", 0, 0.1, CPQPOWER_OID_OUT_CURRENT ".3", "",
		SU_OUTPUT_3, NULL },
	{ "output.L1.realpower", 0, 0.1, CPQPOWER_OID_OUT_POWER ".1", "",
		SU_OUTPUT_3, NULL },
	{ "output.L2.realpower", 0, 0.1, CPQPOWER_OID_OUT_POWER ".2", "",
		SU_OUTPUT_3, NULL },
	{ "output.L3.realpower", 0, 0.1, CPQPOWER_OID_OUT_POWER ".3", "",
		SU_OUTPUT_3, NULL },
	{ "output.power.percent", 0, 1.0, CPQPOWER_OID_LOAD_LEVEL , "",
		SU_OUTPUT_3, NULL },

	/* Input page */
	{ "input.phases", 0, 1.0, CPQPOWER_OID_IN_LINES, "",
		SU_FLAG_SETINT, NULL, &input_phases },
	{ "input.frequency", 0, 0.1, CPQPOWER_OID_IN_FREQ , "",
		SU_INPUT_1, NULL },
	{ "input.phase", 0, 1.0, CPQPOWER_OID_IN_PHASE ".1", "",
		SU_INPUT_1, NULL },
	{ "input.voltage", 0, 1.0, CPQPOWER_OID_IN_VOLTAGE ".1", "",
		SU_INPUT_1, NULL },
	{ "input.current", 0, 0.1, CPQPOWER_OID_IN_CURRENT ".1", "",
		SU_INPUT_1, NULL },
	{ "input.L1-N.phase", 0, 1.0, CPQPOWER_OID_IN_PHASE ".1", "",
		SU_INPUT_3, NULL },
	{ "input.L2-N.phase", 0, 1.0, CPQPOWER_OID_IN_PHASE ".2", "",
		SU_INPUT_3, NULL },
	{ "input.L3-N.phase", 0, 1.0, CPQPOWER_OID_IN_PHASE ".3", "",
		SU_INPUT_3, NULL },
	{ "input.L1-N.voltage", 0, 1.0, CPQPOWER_OID_IN_VOLTAGE ".1", "",
		SU_INPUT_3, NULL },
	{ "input.L2-N.voltage", 0, 1.0, CPQPOWER_OID_IN_VOLTAGE ".2", "",
		SU_INPUT_3, NULL },
	{ "input.L3-N.voltage", 0, 1.0, CPQPOWER_OID_IN_VOLTAGE ".3", "",
		SU_INPUT_3, NULL },
	{ "input.L1.current", 0, 0.1, CPQPOWER_OID_IN_CURRENT ".1", "",
		SU_INPUT_3, NULL },
	{ "input.L2.current", 0, 0.1, CPQPOWER_OID_IN_CURRENT ".2", "",
		SU_INPUT_3, NULL },
	{ "input.L3.current", 0, 0.1, CPQPOWER_OID_IN_CURRENT ".3", "",
		SU_INPUT_3, NULL },
	{ "input.L1.realpower", 0, 0.1, CPQPOWER_OID_IN_POWER ".1", "",
		SU_INPUT_3, NULL },
	{ "input.L2.realpower", 0, 0.1, CPQPOWER_OID_IN_POWER ".2", "",
		SU_INPUT_3, NULL },
	{ "input.L3.realpower", 0, 0.1, CPQPOWER_OID_IN_POWER ".3", "",
		SU_INPUT_3, NULL },
        { "input.quality", 0, 1.0, CPQPOWER_OID_IN_LINEBADS, "",
               0, NULL },

	/* instant commands. */
	{ "load.off", 0, CPQPOWER_OFF_DO, CPQPOWER_OID_SD_AFTER_DELAY, "",
		SU_TYPE_CMD, NULL },
/*	{ CMD_SHUTDOWN, 0, CPQPOWER_OFF_GRACEFUL, CPQPOWER_OID_OFF, "", 0, NULL }, */

	/* end of structure. */
	{ NULL, 0, 0, NULL, NULL, 0, NULL }
};
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev

Reply via email to