On Mon, 2010-02-01 at 12:15 +0000, Arjen de Korte wrote: > Why did you remove the three phase support? The unit seems to > correctly report the number of input- and output phases, so leaving > that in wouldn't hurt. Even though it's not tested, you already know > it works for single phase units.
I removed it because requesting a specific 3-phase variable does not work (at least on the units I have to hand). Compare the following: hostadm:/etc/nut# snmpget -v 1 -c public \ ups-pf34-2 .1.3.6.1.4.1.232.165.3.3.4.1.2.1 Error in packet Reason: (noSuchName) There is no such variable name in this MIB. Failed object: CPQPOWER-MIB::upsInputVoltage.1 hostadm:/etc/nut# snmpget -v 1 -c public \ ups-pf34-2 .1.3.6.1.4.1.232.165.3.3.4.1.2 CPQPOWER-MIB::upsInputVoltage.1 = INTEGER: 245 This suggests to me that requesting the 3-phase values will cause an error. Unless I have misunderstood how the driver grabs the values. Does the SU_INPUT_3 flag tell the driver to ask for (for example) .1.3.6.1.4.1.232.165.3.3.4.1.2, and then only grab the one that it asked for? I'll stick the 3-phase stuff back in if this is the case. - Philip Ward Unix Systems Administrator Ext 7274 -- The Sunday Times Scottish University of the Year 2009/2010 The University of Stirling is a charity registered in Scotland, number SC 011159. _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev