Hi Guys, I tested this driver and I found a bug,
The wrong output: device.serial: GXT2MR15D ups.firmware: 12OCT04 ups.mfr.date: 0428100126AF041 ups.serial: GXT2MR15D The right output: device.serial: 0428100126AF041 ups.firmware: GXT2MR15D ups.mfr.date: 12OCT04 ups.serial: 0428100126AF041 I fix it and attached the patch. 2010/4/7 Spiros Ioannou <[email protected]> > On the battery issue: > I did some tests: > BATTERY_CAPACITY is always 94%, no matter its charge, probably indicating > its decay. > BATTERY_CHARGED is always NO for me > BATTERY_CURRENT does actually indicate when battery is charging or > discharging. In the case of discharging (ups on battery) a negative value is > indicated. > The correct value can be calculated as follows: > > float f; > f=(signed short int)(256*H+L)/(float)100; //100 is the divider to convert > value to Amperes. > > The actual value of BATTERY_CURRENT in Amperes need to be divided by 100: > *CHARGING:* > # ./upsesp2 /dev/ttyS0 BATTERY_CURRENT > SendingM: 001,095,002,001,003,09C BATTERY_CURRENT,bit/divider:100 > READ : 001,095,004,001,003, 001,056 (001 086), 0F5 (returned values > H,L are decimal 001 086) > BATTERY_CURRENT: 3.4 > > *DISCHARGING (on battery)* > # ./upsesp2 /dev/ttyS0 BATTERY_CURRENT > SendingM: 001,095,002,001,003,09C BATTERY_CURRENT,bit/divider:100 > READ : 001,095,004,001,003, 0FC,020 (252 032), 0BA > BATTERY_CURRENT: -9.9 > > -9.9 comes from (255-252)*256 + (255-032) or by casting to signed short int > which does the same. > > After the power comes back on, between discharging and charging there is a > period of no battery current (0 Amp) for a few seconds. > > -S > > On Tue, Apr 6, 2010 at 9:12 PM, Spiros Ioannou <[email protected]> wrote: > >> Hi, >> I managed to find another Liebert UPS, this time a Liebert NXe 20KVA unit, >> so I can help with the driver again. >> This one has 2 serial ports, one gets disabled if you connect the ethernet >> module. The other port is @9600bps. The 9600 is the one I use. >> >> I applied Richard's patch with the bit correction, and tried the driver >> (after changing the bitrate), but it failed at startup because Liebert NXe >> doesn't provide its Serial Number. It seems when trying to read the initial >> UPS model,SN etc, the UPS replies an invalid 5-byte reply instead of the >> usual 8-byte one. I attach a debug output (hex) from my upsesp2.c for >> comparison. Look at line 109 of dbg_hex.txt. >> >> The solution is to replace >> for (i = 0; i < 37; i++) { >> with >> for (i = 0; i < 15; i++) { >> >> to just check for MODEL_NAME >> >> As for the CHARGED, it seems that in my case the battery BATTERY_CHARGED >> is always NO perhaps because the UPS uses a percentage battery charge >> indicator (BATTERY_CAPACITY). I'm not sure I follow your logic with ANDing >> with the OL flag. The Charging could probably be deducted from the >> BATTERY_CURRENT value.This could be negative if the battery is charging, but >> I cannot test it right now. >> >> ./liebertgxt2 -a nxe -DD >> Network UPS Tools - Liebert GXT2 serial UPS driver 0.02 (2.4.3-2420) >> Warning: This is an experimental driver. >> Some features may not function correctly. >> >> 0.000000 debug level is '2' >> 0.000737 send: (6 bytes) => 01 88 02 01 04 90 >> 0.072087 read: (8 bytes) => 01 88 04 01 04 69 4c 47 >> 0.072216 send: (6 bytes) => 01 88 02 01 05 91 >> 0.136206 read: (8 bytes) => 01 88 04 01 05 62 65 5a >> 0.136343 send: (6 bytes) => 01 88 02 01 06 92 >> 0.202086 read: (8 bytes) => 01 88 04 01 06 72 65 6b >> 0.202209 send: (6 bytes) => 01 88 02 01 07 93 >> 0.266083 read: (8 bytes) => 01 88 04 01 07 20 74 29 >> 0.266205 send: (6 bytes) => 01 88 02 01 08 94 >> 0.328099 read: (8 bytes) => 01 88 04 01 08 58 4e 3c >> 0.328222 send: (6 bytes) => 01 88 02 01 09 95 >> 0.402090 read: (8 bytes) => 01 88 04 01 09 00 20 b7 >> 0.402212 send: (6 bytes) => 01 88 02 01 0a 96 >> 0.468096 read: (8 bytes) => 01 88 04 01 0a 00 00 98 >> 0.468220 send: (6 bytes) => 01 88 02 01 0b 97 >> 0.559082 read: (8 bytes) => 01 88 04 01 0b 00 00 99 >> 0.559205 send: (6 bytes) => 01 88 02 01 0c 98 >> 0.623082 read: (8 bytes) => 01 88 04 01 0c 00 00 9a >> 0.623204 send: (6 bytes) => 01 88 02 01 0d 99 >> 0.687179 read: (8 bytes) => 01 88 04 01 0d 00 00 9b >> 0.687316 send: (6 bytes) => 01 88 02 01 0e 9a >> 0.753149 read: (8 bytes) => 01 88 04 01 0e 00 00 9c >> 0.753285 send: (6 bytes) => 01 88 02 01 0f 9b >> 0.818205 read: (8 bytes) => 01 88 04 01 0f 00 00 9d >> 0.818342 send: (6 bytes) => 01 88 02 01 10 9c >> 0.880087 read: (8 bytes) => 01 88 04 01 10 00 00 9e >> 0.880210 send: (6 bytes) => 01 88 02 01 11 9d >> 0.972080 read: (8 bytes) => 01 88 04 01 11 00 00 9f >> 0.972203 send: (6 bytes) => 01 88 02 01 12 9e >> 1.052085 read: (8 bytes) => 01 88 04 01 12 00 00 a0 >> 1.052211 send: (6 bytes) => 01 88 02 01 13 9f >> 1.116147 read: (8 bytes) => 01 88 04 01 13 31 49 1b >> 1.116283 send: (6 bytes) => 01 88 02 01 14 a0 >> 1.180087 read: (8 bytes) => 01 88 04 01 14 30 37 09 >> 1.180210 send: (6 bytes) => 01 88 02 01 15 a1 >> 1.263082 read: (8 bytes) => 01 88 04 01 15 31 52 26 >> 1.263205 send: (6 bytes) => 01 88 02 01 16 a2 >> 1.329086 read: (8 bytes) => 01 88 04 01 16 30 35 09 >> 1.329210 send: (6 bytes) => 01 88 02 01 17 a3 >> 1.395086 read: (8 bytes) => 01 88 04 01 17 32 4d 24 >> 1.395208 send: (6 bytes) => 01 88 02 01 18 a4 >> 1.469080 read: (8 bytes) => 01 88 04 01 18 30 36 0c >> 1.469202 send: (6 bytes) => 01 88 02 01 19 a5 >> 1.533086 read: (8 bytes) => 01 88 04 01 19 00 00 a7 >> 1.533209 send: (6 bytes) => 01 88 02 01 1a a6 >> 1.597114 read: (8 bytes) => 01 88 04 01 1a 00 00 a8 >> 1.597239 send: (6 bytes) => 01 88 02 01 1b a7 >> 1.662085 read: truncated: (5 bytes) => 01 37 01 04 3d >> 1.662194 GTX2 capable UPS not detected >> >> >> >> On Tue, Apr 6, 2010 at 4:32 PM, Richard Gregory < >> [email protected]> wrote: >> >>> Hi All, >>> >>> There were other byte swap issues with the driver, making all the bit >>> field flags wrong. Have swapped them and can confirm the OL, OB and CHRG >>> flags work. CHaRGing is not the inverse of Liebert's BATTERY_CHARGED flag as >>> that means CHRG is set when the UPS is on battery. Is it reasonable to >>> correct for this by ANDing with the OL flag? >>> >>> Byte swapping patch attached. >>> >>> >>> Richard >>> >>> +-- --+ >>> | Biological Sciences, Room 231 | >>> | http://www.csc.liv.ac.uk/~greg <http://www.csc.liv.ac.uk/%7Egreg> | >>> +-- --+ >>> >>> Arjen de Korte wrote: >>> >>>> Citeren Robert Jobbagy <[email protected]>: >>>> >>>> The trouble was in the command reply buffer use. >>>>> You compute the value that value = reply[6]*256+reply[5] <- it's wrong >>>>> >>>>> The right solution: value = reply[5] * 256 + reply[6]; >>>>> >>>> >>>> Thanks for this patch. I just committed it to the development version. >>>> But please note that this is an experimental driver. Most of the >>>> functions >>>> are untested (since nobody took the time to try it out and post the >>>> results >>>> back to the mailing list). >>>> >>>> And other bug, >>>>> >>>>> battery.runtime compute, you divide this value 60 <- it's wrong >>>>> >>>>> right value: divide 1.0 >>>>> >>>> >>>> Probably not. Per the NUT standard, the 'battery.runtime' value is >>>> reported in seconds. As far as I understand, the UPS reports runtime >>>> remaining in minutes, so we need to multiply by 60 here. See >>>> 'docs/new-names.txt' for a listing of (almost) all variables supported in >>>> NUT. >>>> >>>> I continue the work on this driver,and I will write if I make a >>>>> something >>>>> new. >>>>> >>>> >>>> Please do. It should be trivial to add additional commands and >>>> variables to the existing ones. >>>> >>>> Best regards, Arjen >>>> >>> >>> _______________________________________________ >>> Nut-upsdev mailing list >>> [email protected] >>> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev >>> >> >> > > _______________________________________________ > Nut-upsdev mailing list > [email protected] > http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev > -- Best Regards, Robert
liebertgxt2_patch
Description: Binary data
_______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev