Hi Guys,

I have question,

If you changed liebert source file name (liebertgxt2 -> liebert-esp2) then
the driver name will be liebert-esp2 too or don't ?
Because now the source filename is liebert-esp2 and driver name liebertgxt2,
is it right?

Thanks.

Spiros patch:
I will test it and send my output and my experience.



2010/4/21 Spiros Ioannou <siv...@gmail.com>

> Additional info to previous post. Sorry for the big patch but I'm really
> trying to find time between 3 jobs with the economic crisis here :-)
>
>
> Today's patch includes:
> -support for 1 & 3-phase input & output (and all combinations)
> -support for most input & output & bypass & nominal variables (current,
> power (watt+VA), voltage, frequency)
>
> Other new variables:
> -ups.type detection (offline, line-interactive, online)
> -current crest factor detection (3-phase)
> -battery.runtime.low detection
> -ups.delay.start detection (yes, I have it in 900 seconds)
>
> Values were also verified with their snmp equivalents.
>
> Best Regards,
> -Spiros
>
>
> On Wed, Apr 21, 2010 at 5:01 PM, Spiros Ioannou <siv...@gmail.com> wrote:
>
>> Attached. I also attach sample output from upsc OL & OB.
>> I only tested it with 3-phase in/3-phase out ups.
>> Thanks,
>> -Spiros
>>
>>
> _______________________________________________
> Nut-upsdev mailing list
> Nut-upsdev@lists.alioth.debian.org
> http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev
>



-- 
Best Regards,

Robert
_______________________________________________
Nut-upsdev mailing list
Nut-upsdev@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev