Citeren "Jain, Arvind" <[email protected]>:

This sleeps until AC power returns. When battery runs out, system stop
and reboots when power is back.

First of all, it is a terribly bad idea to run a driver in debug mode on a production system. It should be used for testing purposes only.

The problem is caused by the driver failing to detect a working 'load.on.delay' command for the UPS, which is needed to create the two-step 'shutdown.return' command. Either your UPS doesn't have one, or it is put in a vendor specific HID path. Because of this, the driver will fallback to the 'shutdown.reboot' command, which seems to be horribly broken for your UPS.

It would be helpful if you could post the output of

 /sbin/usbhid-ups -DD -a scups 2>&1

here, so that we can see if there might be another HID path that could be used.

Chances are, that we just need to call 'load.off.delay' and that the device will return power all by itself. This violates the HID Power Device Specification, but since the 'shutdown.reboot' also is non-compliant, I'm not too surprised.

Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)


_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev