Citeren John Bayly <[email protected]>:

I've discovered an issue (which may be unique to my UPS) with this commit.
init_communication now returns -1, instead of 0 if it failed to read the manufacturer info, this makes sense after all.

Not entirely. Previously, the init_communication() function would try to read "BELKIN", but it would settle for a valid reply format (discarding the contents) after 10 retries.

With my UPS (Belkin F6C1400-EUR), the response to the Manufacturer command returns only 6 spaces (rather than "BELKIN"), this means that init_communications fails, and the driver fails with EXIT_FAILURE

Fixed in r2735. The driver seems to ignore the contents of this anyway. The value for 'ups.mfr' is even hard coded, which is already an indication that the original author wasn't sure that we should trust the value returned by the UPS.

Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)


_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev