Follow up.
--- Begin Message ---
Once upon a time, Chris Adams <[email protected]> said:
> I have an older Powerware 9315 UPS that I monitor from a Linux box
> running Network UPS Tools and the bcmxcp driver. I upgraded that
> server, including a much newer version of NUT (2.4.3), and now it can't
> monitor my UPS. You are listed as the current author for that driver,
> and since I haven't been able to subscribe to the mailing list so far
> (I'm not getting the confirmation emails), I thought I'd try a direct
> email to you.
<snip>
> This is a physically different server than before; the old one connected
> via a USB-to-serial adapter (standard old PL2303), while the new one is
> connected through a PCI-E serial card (I know the card is working okay
> because an APC UPS is connected to the other port and is working fine).
Well, I tried re-connecting the old USB-to-serial adapter (I had one
open USB port on the new server), and that has solved the rest of my
problems. I have a long cat-5 run between the UPS and the server (that
cable hasn't changed, as the new server is in the same location as the
old server), and I'm guessing that either the input sensitivity or the
output driver on the PCI-E card is not as good as the USB adapter, and
characters were getting dropped in one direction or the other.
I do still need the patch I sent you, as bcmxcp was broke without that.
--
Chris Adams <[email protected]>
Systems and Network Administrator - HiWAAY Internet Services
I don't speak for anybody but myself - that's enough trouble.
--- End Message ---