Hallo,
I own a NETUPS 450 (Model on the sticker: PRM 450i; upsstats reports
"UPS 450 VA FW -0024") which perfectly works with the upscode2 driver.
Maybe you want to add it to your list, even if the model is >10 years
old. 

I suppose this is true for the whole series. According manual the come
in the 450VA, 700VA, 1000VA and 1500VA strengths.  

They have been sold under different manufactors: powerware, exide and
now they are listed under Eaton's homepage -- I think the companies have
been sold/merged etc. ;-)

Many kudos for your work.

With regards, 
coldtobi

Here are the capabilites reported: 
battery.capacity.nominal : 7.20
battery.charge : 92.7
battery.runtime : 2640
battery.voltage : 13.80
battery.voltage.maximum : 14.10
battery.voltage.minimum : 10.00
battery.voltage.nominal : 12.00
device.mfr : unknown
device.model : UPS 450 VA FW -0024 
device.serial : <removed> 
device.type : ups
driver.name : upscode2
driver.parameter.pollinterval : 2
driver.parameter.port : /dev/ttyUSB0
driver.version : 2.4.3
driver.version.internal : 0.87
input.phases : 1
input.voltage : 228.30
input.voltage.maximum : 276.00
input.voltage.minimum : 162.00
input.voltage.nominal : 230.00
output.current : 0.18
output.current.maximum : 2.23
output.current.nominal : 1.96
output.frequency : 50.00
output.frequency.maximum : 53.00
output.frequency.minimum : 47.00
output.phases : 1
output.power : 0.04
output.realpower : 10.00
output.realpower.nominal : 280.00
output.voltage : 228.30
output.voltage.maximum : 244.00
output.voltage.minimum : 207.00
output.voltage.nominal : 230.00
ups.delay.reboot : 000
ups.delay.shutdown : 000
ups.load : 9.2
ups.mfr : unknown
ups.model : UPS 450 VA FW -0024 
ups.power.nominal : 450.00
ups.serial : <removed> 
ups.status : OL