On 11-03-06 18:38, Arjen de Korte wrote:
Citeren Michal Soltys <[email protected]>:

As we want the user to be able do issue all shutdown methods manually,
adjust sdcmd_*() to use STAT_INSTCMD_{HANDLED,FAILED}, so they can
be used directly.

The above is a good idea.

Also minor text corrections, and APC specific command renames.

This isn't. You really should stick to the existing set of commands and
try to map the APC specific commands to existing ones. If you think this
is not possible, this should first be discussed here before we will add
them.

Best regards, Arjen

Well, the only apc-custom "commands" are:

CS hack - force OB, then use shutdown.return
@nnn - no equivalent
@nn (hack) - no equivalnet

I renamed the commands I added earlier btw.

Currently:

S - maps to shutdown.return
K - maps to shutdown.stayoff
Z - maps to load.off

but I see no existing candidates for:

@nnn - like shutdown.return, but with additional weakup delay
@nn - as above, but "hack" version (tbh, the idea was borrowed from apcupsd code - I haven't personally heard about such ups, but it could be useful for someone)
CS hack - like shutdown.return, but after forcing OB

Thus the names for apc-specific commands:

shutdown.return.awd
shutdown.return.awd.h
shutdown.return.cs

They would be documented in updated manpage of course.

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev

Reply via email to