On 07/03/2011 11:42, Arjen de Korte wrote:
Citeren John Bayly <[email protected]>:
Are there any plans to allow us to specify UPS variables in ups.conf,
eg:
We already support this (as a hidden feature) since nut-2.4.0, where
it is possible to set
default.<variable> = value (default to value if UPS doesn't report
this)
override.<variable> = value (same, but override if reported by UPS)
But most likely, this is not what you need.
I'll look into how that works, thanks. These look like they do exactly
the job for specifying the delays for the switched outlets
(outlet.1.delay.start). Is there any reason why they're a "hidden
feature"? Should I rely on this remaining? Is it driver specific?
You probably missed the man page for the usbhid-ups driver. See
'offdelay' and 'ondelay' under EXTRA ARGUMENTS in 'man 8 usbhid-ups'
which are meant to do what you want. Using the
'(default|override).ups.delay.(start|shutdown)' mechanism might also
work, but this is not recommended.
Face-palm, how on earth did I miss that?
The reason I ask is that I'm using FreeBSD & gmirror and need to
extend the gracetime for the system to shutdown. For the moment, I've
created a custom shutdown script that is set in upsmon.conf that does
the job.
I doubt it.
Yup, but for reasons below
#!/usr/local/bin/bash
/usr/local/bin/upsrw -s ups.delay.start=130 -u haltuser -p
somepassword evo_s_3000
/usr/local/bin/upsrw -s ups.delay.shutdown=120 -u haltuser -p
somepassword evo_s_3000
/sbin/shutdown -h +0
This most likely doesn't work, since the changed values of
'ups.delay.start' and 'ups.delay.shutdown' won't stick between
invocations of the driver. Only if you keep the driver running and
send the instcmd 'shutdown.return' this might work, but this is not
what happens if you call 'upsdrvctl shutdown' (where the driver is
restarted with the -k flag). You *must* use ondelay and offdelay instead.
I discovered that about the values not "sticking". To work around this,
instead of issuing `upsdrvctl shutdown`, I've been issuing the
`shutdown.return` command. I imagine your head has now slammed into your
desk upon hearing this :-)
As it is, my setup wasn't ideal, but works exactly as desired (Client &
Master halt, UPS shuts down and comes up no sooner that 10s afterwards,
systems restart when AC is restored).
Best regards, Arjen
I appreciate you clearing things up.
Thanks,
John
Sorry, forgot to reply to the list too <sigh>
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev