Citeren Arnaud Quette <[email protected]>:

we (Eaton) have created a new data to expose efficiency of the UPS
(basically it is the ratio of the output current on the input current).
I know that at least APC should also provide it on some units, since I've
seen evidence in an EPA presentation [1].

So I'd like to create the following new data:

- Name: ups.efficiency
- Description: Efficiency of the UPS (ratio of the output current on the
input current) (percent)
- Example value: 99

As usual, comments and feedback are very welcome...

Two comments:

1) What would be reported if the UPS is running on battery? There clearly would be no input power at that time. What is reported in that case?

2) Calculating the efficiency based on the ratio of input and output *current* leaves a giant loophole to artificially increase the reported efficiency. On an online UPS one could increase the 'efficiency' by setting the output voltage a few percent above the input voltage. Similarly, if a system would have a near unity power factor on the input, but a crappy one on the output, you'd also inflate the reported efficiency by using the RMS figures.

I'd only see some merit in reporting this, if it would be the ratio of input and output real power values. I would be surprised if in a real world scenario however if one would get very close to 99% (if not in running in bypass mode). A more typical value of a double conversion UPS would be something between 90-95% and even then only when the UPS is properly scaled for the designed load. The good thing would be that people might be made aware how much power they are wasting, given that fact that in many cases a UPS will not be operated near the optimum efficieny load.

Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)