Sorry, I did not know reverse engineering is forbidden in this project, not
stated in Your developers guide, removed and repost.
y
tom
Am 01.10.2011 07:53, schrieb thomas schorpp:
Stated above, same for the FSP EP-1K, except of temperature and battery
voltage:
battery.charge: 100
battery.runtime: 4000
battery.voltage: 27.40
battery.voltage.nominal: 24.0
beeper.status: enabled
device.type: ups
driver.flag.novendor: enabled
driver.name: blazer_usb
driver.parameter.chargetime: 8
driver.parameter.idleload: 30
driver.parameter.pollinterval: 15
driver.parameter.port: auto
driver.parameter.productid: 5161
driver.parameter.runtimecal: 1200,100,3200,50
driver.parameter.vendorid: 0665
driver.version: 2.4.3
driver.version.internal: 0.03
input.current.nominal: 5.0
input.frequency: 50.1
input.frequency.nominal: 50
input.voltage: 231.2
input.voltage.fault: 231.2
input.voltage.nominal: 220
output.voltage: 231.2
ups.delay.shutdown: 30
ups.delay.start: 180
ups.load: 27
ups.productid: 5161
ups.status: OL
ups.type: offline / line interactive
Cmds an Alarms untested but the EP-650 is already in the supported
devices list.
Can You confirm no usb req timeouts for Your device at 2sec polling for
hours?
Oct 1 06:24:28 fritz.box blazer_usb[11636]: Communications with UPS
lost: status read failed!
Oct 1 06:24:43 fritz.box blazer_usb[11636]: Communications with UPS
lost: status read failed!
Oct 1 06:24:58 fritz.box blazer_usb[11636]: Communications with UPS
re-established
<Removed> Reverse engineering proprietary protocols implicitely NOT allowed on
NUT.
I will try some replays with a modified blazer_usb driver or dummy-ups
and tools/device-recorder.sh.
y
tom
For the FSP UPS EP-1K and other with the cypress/inno tech usb idVID=0665
PID=5161
the following commands are working so far:
~$ grep -i handled /var/log/syslog*
/var/log/syslog:Oct 3 08:38:30 fritz.box blazer_usb[11636]: instcmd: command
[beeper.toggle] handled
/var/log/syslog:Oct 3 08:38:55 fritz.box blazer_usb[11636]: instcmd: command
[beeper.toggle] handled
/var/log/syslog.1:Oct 2 15:56:12 fritz.box blazer_usb[11636]: instcmd: command
[test.battery.start.quick] handled
according to viewpower 2.08 this ups does support scheduled load switching and
shutdown/restore cmds, too,
BTW is "beeper.toggle" = "Alarms on/off"?
But the usb disconnects and timeouts still occur but are well handled by the
fritz!box usb controller and 2.6.32 kernel:
/var/log/syslog.1:Oct 2 17:58:18 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 17:58:33 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 17:58:48 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 2 18:19:33 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 18:19:48 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 18:20:03 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 2 19:09:19 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 19:09:33 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 2 19:26:19 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 19:26:33 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 19:26:48 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 2 20:39:05 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 20:39:19 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 2 20:45:35 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 2 20:45:49 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 3 00:52:52 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 00:53:06 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 3 03:32:08 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 03:32:23 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 03:32:38 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 3 04:28:54 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 04:29:08 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 04:29:23 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 04:29:38 fritz.box upsd[11637]: Data for UPS [ups] is
stale - check driver
/var/log/syslog.1:Oct 3 04:29:38 tom3 upsmon[3640]: Poll UPS [[email protected]]
failed - Data stale
/var/log/syslog.1:Oct 3 04:29:38 tom3 upsmon[3640]: Communications with UPS
[email protected] lost
/var/log/syslog.1:Oct 3 04:29:43 tom3 upsmon[3640]: Poll UPS [[email protected]]
failed - Data stale
/var/log/syslog.1:Oct 3 04:29:48 tom3 upsmon[3640]: Poll UPS [[email protected]]
failed - Data stale
/var/log/syslog.1:Oct 3 04:29:53 tom3 upsmon[3640]: Poll UPS [[email protected]]
failed - Data stale
/var/log/syslog.1:Oct 3 04:29:53 fritz.box blazer_usb[11636]: Communications
with UPS re-established
/var/log/syslog.1:Oct 3 04:29:53 fritz.box upsd[11637]: UPS [ups] data is no
longer stale
/var/log/syslog.1:Oct 3 04:29:58 tom3 upsmon[3640]: Communications with UPS
[email protected] established
/var/log/syslog.1:Oct 3 04:48:24 fritz.box blazer_usb[11636]: Communications
with UPS lost: status read failed!
/var/log/syslog.1:Oct 3 04:48:38 fritz.box blazer_usb[11636]: Communications
with UPS re-established
Oct 3 17:35:20 tom3 upsmon[3640]: Poll UPS [[email protected]] failed - Data stale
Oct 3 17:35:20 tom3 upsmon[3640]: Communications with UPS [email protected] lost
Oct 3 17:35:25 tom3 upsmon[3640]: Poll UPS [[email protected]] failed - Data stale
Oct 3 17:35:30 tom3 upsmon[3640]: Poll UPS [[email protected]] failed - Data stale
Oct 3 17:35:30 fritz.box blazer_usb[11636]: Communications with UPS
re-established
Oct 3 17:35:30 fritz.box upsd[11637]: UPS [ups] data is no longer stale
root@fritz:/var/mod/root# dmesg |grep usb
usb 1-1.4: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret
-145
usb 1-1.4: reset low speed USB device using musb_hdrc and address 9
root@fritz:/var/mod/root# dmesg |grep usb
usb 1-1.4: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret
-145
usb 1-1.4: reset low speed USB device using musb_hdrc and address 9
usb 1-1.4: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret
-145
usb 1-1.4: reset low speed USB device using musb_hdrc and address 9
usb 1-1.4: usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 33 rq 9 len 8 ret
-145
usb 1-1.4: reset low speed USB device using musb_hdrc and address 9
What is -E 145, cannot find it in 2.6.32 mips kernel source err*.h ?
The via 8237 usb controller with 2.6.38 on the desktop host
00:10.4 USB Controller: VIA Technologies, Inc. USB 2.0 (rev 86)
00:11.0 ISA bridge: VIA Technologies, Inc. VT8237 ISA bridge
[KT600/K8T800/K8T890 South]
did not reset the ups successfully, power cycle of the ups was required.
This does not happen with viewpower even polling at 1/sec according to
viewpower logs.
Fortron Source / Inno-Tech(.in?) should release a firmware fix for better
compatibility with NUT,
since surely not many people use this 230MB big gui java-monster viewpower, not
working on debian 6 like assured in system requirements,
cause the "statically linked" 32bit-java vm needs net.ipv6.bindv6only = 0 to
open sockets
and it does not find the correct ttyUSB device on 2.6.38 if you got another tty*S* devices and there's no customer support at all
to find for viewpower users and using such a power consuming host viewpower
needs to monitor a ups in power failure case
will drain the battery very fast, that's very unreasonably,
a 10Watts router will run for many hours on battery and allows alarm users,
controlling, monitor the ups in line power failure.
You can find an alpha version of the NUT port for avm.de fritzbox and possibly
other SOHO routers here:
http://freetz.org/ticket/1521
For support and contributions add to the ticket, pls.
y
tom
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev