Hi Petr,

2011/11/20 Petr Kubánek <[email protected]>:
> Hi,
>
> another UPS piece supported by blazer_usb:
>
> ALLSAI
> model LV 2K
>
> upsc output:
>
> battery.voltage: 82.08
> battery.voltage.nominal: 72.0
> beeper.status: enabled
> device.mfr:
> device.model: LV 2K
> device.type: ups
> driver.name: blazer_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.4.3
> driver.version.internal: 0.03
> input.current.nominal: 18.0
> input.frequency: 59.9
> input.frequency.nominal: 60
> input.voltage: 118.0
> input.voltage.fault: 118.0
> input.voltage.nominal: 110
> output.voltage: 109.8
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.firmware: 00001907
> ups.load: 23
> ups.mfr:
> ups.model: LV 2K
> ups.productid: 5161
> ups.status: OL
> ups.temperature: 16.3
> ups.type: online
> ups.vendorid: 0665
>
> shutdown sequence was so far not attempted; will be hopefully attempted
> during next site visit (CTIO, Chile)
>
> http://www.allsai.com (probably full range of their devices will be
> suported)

thanks for your report.
I will wait for your shutdown test results before adding a new entry.
If you have a chance to do so, please also try "upsrw" and "upscmd -l"
and send us back the output.

cheers,
Arnaud

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to