Hi,

This appears to be related to a thread from January 2010:
http://lists.alioth.debian.org/pipermail/nut-upsdev/2010-January/004470.html

NB: This is on an HP-UX 11.31 box, using a self compiled and packaged version of NUT 2.6.3, and net-snmp v5.7.1. Therefore some of the search paths and things like that may well be wrong because I've done something dumb. I'm also only just getting started with NUT on account of finding the HP tools don't appear to do the right thing. Therefore, my post may in fact be unwanted gibberish.

I've got an HP "R5500 XR" UPS with an additional network-capable management card (AH401A). On using the client to talk to it I get the following output:

# /usr/local/ups/bin/upsdrvctl start
Network UPS Tools - UPS driver controller 2.6.3
Network UPS Tools - Generic SNMP UPS driver 0.58 (2.6.3)
MIB search path: //.snmp/mibs:/usr/local/share/snmp/mibs
Cannot find module (SNMPv2-MIB): At line 0 in (none)
Cannot find module (IF-MIB): At line 0 in (none)
Cannot find module (IP-MIB): At line 0 in (none)
Cannot find module (TCP-MIB): At line 0 in (none)
Cannot find module (UDP-MIB): At line 0 in (none)
Cannot find module (HOST-RESOURCES-MIB): At line 0 in (none)
Cannot find module (NOTIFICATION-LOG-MIB): At line 0 in (none)
Cannot find module (DISMAN-EVENT-MIB): At line 0 in (none)
Cannot find module (DISMAN-SCHEDULE-MIB): At line 0 in (none)
Cannot find module (UCD-SNMP-MIB): At line 0 in (none)
Cannot find module (UCD-DEMO-MIB): At line 0 in (none)
Cannot find module (SNMP-TARGET-MIB): At line 0 in (none)
Cannot find module (NET-SNMP-AGENT-MIB): At line 0 in (none)
Cannot find module (HOST-RESOURCES-TYPES): At line 0 in (none)
Cannot find module (SNMP-MPD-MIB): At line 0 in (none)
Cannot find module (SNMP-USER-BASED-SM-MIB): At line 0 in (none)
Cannot find module (SNMP-FRAMEWORK-MIB): At line 0 in (none)
Cannot find module (SNMP-VIEW-BASED-ACM-MIB): At line 0 in (none)
Cannot find module (SNMP-COMMUNITY-MIB): At line 0 in (none)
Cannot find module (NET-SNMP-PASS-MIB): At line 0 in (none)
Cannot find module (NET-SNMP-EXTEND-MIB): At line 0 in (none)
Cannot find module (UCD-DLMOD-MIB): At line 0 in (none)
Cannot find module (SNMP-NOTIFICATION-MIB): At line 0 in (none)
Cannot find module (SNMPv2-TM): At line 0 in (none)
Cannot find module (NET-SNMP-VACM-MIB): At line 0 in (none)
No matching MIB found for sysOID '.1.3.6.1.4.1.232.165.3'! Please report it to NUT developers, with the 'mib' paramater for your devices
Detected R5500 XR on host 192.168.24.101 (mib: cpqpower 1.0)
[r5500] snmp_ups_walk: data stale for ups.realpower
[r5500] snmp_ups_walk: data stale for input.voltage
[r5500] snmp_ups_walk: data stale for input.current
[r5500] snmp_ups_walk: data stale for input.realpower


That output suggests to me that the MIB for this UPS is missing or incomplete. 
I tried copying in the file:
ftp://ftp.hp.com/pub/softlib2/software1/pubsw-windows/p104049210/v69218/CPQPOWER1.64.MIB
to /usr/local/share/snmp/mibs in an attempt to fix it, but that doesn't seem to 
change anything.


Happily, upsc seems to communicate successfully:
# ./upsc r5500
ambient.temperature: 22.0
battery.charge: 97.00
battery.current: 0.00
battery.runtime: 46800.00
battery.voltage: 24.60
device.mfr: Hewlett-Packard
device.model: R5500 XR
device.type: ups
driver.name: snmp-ups
driver.parameter.pollinterval: 2
driver.parameter.port: 192.168.24.101
driver.version: 2.6.3
driver.version.internal: 0.58 (mib: cpqpower 1.0)
input.frequency: 50.00
input.phases: 1.00
input.quality: 0.00
output.frequency: 50.00
output.phases: 1.00
ups.firmware:  2.08
ups.load: 49.00
ups.mfr: Hewlett-Packard
ups.model: R5500 XR
ups.model.aux: 12
ups.status: OL DISCHRG
ups.test.result: Done and error
ups.type: normal
#

This UPS actually has dud batteries, which should explain the "error" result.

So, my questions:

Should the snmp-ups driver report this error?
Is it fixable with that MIB file?
Does that MIB file need to be included in a different way, or is it any use to 
you guys?


cheers
jack

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to