Came across this note in section 4.8 of the developers guide before adding FSD to the driver:

Note

upsd injects "FSD" by itself following that command by a master upsmon process. Drivers must not set that value.

Should I try it anyway as suggested?

Thanks,

Bill

At 08:13 AM 2/15/2012, Charles Lepple wrote:
On Feb 14, 2012, at 11:10 PM, William R. Elliot wrote:

OK. Totally missed that I could send FSD as a status from the driver...sorry. I'll give that a shot.

Bill,

Not a problem. I think you are breaking new ground here, but it's something that we should consider for other big UPS models.

Arnaud,

Have you had a chance to follow this discussion? Basically, it sounds like we have a gap in the shutdown mechanism if NUT is set up to monitor an UPS, but the force-shutdown command is sent to the UPS by another system which is not the NUT master. This would probably apply to Eaton's multi-user UPSes like those monitored by snmp-ups and the XML-based cards.

top of the thread: <http://news.gmane.org/find-root.php?message_id=%[email protected]%3E>http://news.gmane.org/find-root.php?message_id=%3c201202092250.q19MoEhE018871%40wreassoc.com%3e

--