Hello

We have an Socomec Sicon Netys PR3000 UPS equipped with NetVision Web/SNMP adaptor. I try to monitor the ups using snmp-ups driver and netvision mibs set. The snmp-ups driver starts correctly and connects to the UPS, upsd confirms it, but upsmon constantly shows "No communication" error

I think the cause is the SNMP adapter reports the UPS status as "ECO mode" (snmpget .1.3.6.1.4.1.4555.1.1.1.1.4.1.0 returns 9), but snmp-ups does not correctly process this. Here is output of 'snmp-ups -a socomec -u nut -D':

Network UPS Tools - Generic SNMP UPS driver 0.50 (2.6.1)
   0.000000     debug level is '1'
   0.000260     SNMP UPS driver : entering upsdrv_initups()
   0.027868     load_mib2nut: trying netvision mib
   0.029798     load_mib2nut: using netvision mib
0.031731 Detected NETYS 3 kVA on host 192.168.0.227 (mib: netvision 0.1)
   0.031751     SNMP UPS driver : entering upsdrv_initinfo()
   0.031785     getting data: ups.mfr (.1.3.6.1.4.1.4555.1.1.1.1.1.3.0)
   0.033823     entering su_setinfo(ups.mfr)
   0.033836     getting data: ups.model (.1.3.6.1.4.1.4555.1.1.1.1.1.1.0)
   0.035731     entering su_setinfo(ups.model)
   0.035744     getting data: ups.serial (.1.3.6.1.4.1.4555.1.1.1.1.1.4.0)
   0.037646     entering su_setinfo(ups.serial)
0.037662 getting data: ups.firmware.aux (.1.3.6.1.4.1.4555.1.1.1.1.1.2.0)
   0.039497     entering su_setinfo(ups.firmware.aux)
   0.039512     getting data: ups.status (.1.3.6.1.4.1.4555.1.1.1.1.2.1.0)
   0.041373     su_find_infoval: found  (value: 2)
   0.041383     getting data: ups.status (.1.3.6.1.4.1.4555.1.1.1.1.4.1.0)
   0.043248     su_find_infoval: found  (value: 9)
0.043258 getting data: ups.load (.1.3.6.1.4.1.4555.1.1.1.1.4.4.1.4.1)
   0.045975     entering su_setinfo(ups.load)
0.045987 getting data: input.voltage (.1.3.6.1.4.1.4555.1.1.1.1.3.3.1.5.1)
   0.047973     entering su_setinfo(input.voltage)
0.047984 getting data: output.voltage (.1.3.6.1.4.1.4555.1.1.1.1.4.4.1.2.1)
   0.050015     entering su_setinfo(output.voltage)
0.050026 getting data: output.current (.1.3.6.1.4.1.4555.1.1.1.1.4.4.1.3.1)
   0.052065     entering su_setinfo(output.current)
0.052076 getting data: battery.charge (.1.3.6.1.4.1.4555.1.1.1.1.2.4.0)
   0.053919     entering su_setinfo(battery.charge)
0.053930 getting data: battery.voltage (.1.3.6.1.4.1.4555.1.1.1.1.2.5.0)
   0.055797     entering su_setinfo(battery.voltage)
0.055807 getting data: battery.runtime (.1.3.6.1.4.1.4555.1.1.1.1.2.3.0)
   0.057690     entering su_setinfo(battery.runtime)
   0.057701     SNMP UPS driver : entering upsdrv_updateinfo()
   0.057712     getting data: ups.status (.1.3.6.1.4.1.4555.1.1.1.1.2.1.0)
   0.059597     su_find_infoval: found  (value: 2)
   0.059606     getting data: ups.status (.1.3.6.1.4.1.4555.1.1.1.1.4.1.0)
   0.061446     su_find_infoval: found  (value: 9)
0.061455 getting data: ups.load (.1.3.6.1.4.1.4555.1.1.1.1.4.4.1.4.1)
   0.063468     entering su_setinfo(ups.load)
0.063478 getting data: input.voltage (.1.3.6.1.4.1.4555.1.1.1.1.3.3.1.5.1)
   0.065502     entering su_setinfo(input.voltage)
0.065515 getting data: output.voltage (.1.3.6.1.4.1.4555.1.1.1.1.4.4.1.2.1)
   0.067566     entering su_setinfo(output.voltage)
0.067576 getting data: output.current (.1.3.6.1.4.1.4555.1.1.1.1.4.4.1.3.1)
   0.069588     entering su_setinfo(output.current)
0.069598 getting data: battery.charge (.1.3.6.1.4.1.4555.1.1.1.1.2.4.0)
   0.071446     entering su_setinfo(battery.charge)
0.071456 getting data: battery.voltage (.1.3.6.1.4.1.4555.1.1.1.1.2.5.0)
   0.073318     entering su_setinfo(battery.voltage)
0.073328 getting data: battery.runtime (.1.3.6.1.4.1.4555.1.1.1.1.2.3.0)
   0.075173     entering su_setinfo(battery.runtime)
   0.075234     SNMP UPS driver : entering upsdrv_updateinfo()

And 'upsmon -u nut -DDD' output:

Network UPS Tools upsmon 2.6.1
   0.000000     UPS: socomec@localhost (master) (power value 1)
   0.000090     Using power down flag file /etc/killpower
   0.000213     debug level is '3'
   0.000705     Trying to connect to UPS [socomec@localhost]
   0.001065     Logged into UPS socomec@localhost
   0.001127     pollups: socomec@localhost
   0.001137     get_var: socomec@localhost / status
   0.001186     parse_status: []
   0.001209     do_notify: ntype 0x0005 (COMMBAD)
   0.001220     Communication with the UPS is lost

In netvision-mib.c I see that ups.status field is constructed from NETVISION_OID_BATTERYSTATUS (.1.3.6.1.4.1.4555.1.1.1.1.2.1.0) and NETVISION_OID_OUTPUT_SOURCE (.1.3.6.1.4.1.4555.1.1.1.1.4.1.0).

Battery status is normal (value 2), value for netvision_batt_info is "" (empty string). Good. Output status has value 9, netvision_output_info is empty string too. Looks false because the UPS is on and works in high-efficiency UPS mode. The result is that ups.status get an empty string value, which confuses upsmon.

--
Ivan Kuznetsov