Hi Arnaud,
On Thu, Jun 28, 2012 at 02:36:31PM +0200, Arnaud Quette wrote:
> 2012/6/13 <[email protected]>
>
> > Hi,
> >
>
> Hi Hong-Gunn,
>
>
> > I updated apc-mib.c to use the high precision values, and added
> > input.transfer.reason.
> > I hope you will find the patch useful.
> >
> > https://alioth.debian.org/tracker/index.php?func=detail&aid=313679
> >
>
> yup, I saw your patch on Alioth, but had no time yet to acknowledge it,
> sorry.
>
> before applying your patch, I need some more validation and information:
> - do "high precision values" complete or replace the existing ones (Ie, are
> the 2 available at the same time)?
The high precision values are in addition to the existing ones, so both values
are available.
> - you've move ambient.*.{high,low} to the first index (Ie, sensor 1) which
> is good since it was planned for the future.
> what puzzles me is that you left ambient.{temperature,humidity}, which
> seems wrong.
> so either there are missing counterpart for ambient.1.*, or the current
> ambient.{temperature,humidity} should be moved to ambient.1...
I did not move them as they are not for the same probes as the .1. ones.
The first ambient.temperature,humidity is for a built-in ups probe.
The second ambient.temperature,humidity is for an integrated probe in the
environmental card.
While the .1. settings are for the external probe 1 of the environmental card.
I can clean this up further if it would be useful, but I didn't do it as I
don't have these results.
> - to complete the above and speed up things (read "to catch up my
> late"...), I would appreciate a numeric + a string walk of your APC
> subtree. Please send it in compressed form.
Ok. Attached. And the MIB can be found at
ftp://ftp.apc.com/apc/public/software/pnetmib/mib/404/powernet404.mib
Cheers,
Hong-Gunn
>
> otherwise, your patch looks great!
> thanks for your contrib,
> Arnaud
> --
> Linux / Unix / Opensource Engineering Expert - Eaton -
> http://opensource.eaton.com
> Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org
> Debian Developer - http://www.debian.org
> Free Software Developer - http://arnaud.quette.free.fr
SNMPv2-SMI::enterprises.318.1.1.1.1.1.1.0 = STRING: "Smart-UPS 1500"
SNMPv2-SMI::enterprises.318.1.1.1.1.1.2.0 = STRING: "ADL03"
SNMPv2-SMI::enterprises.318.1.1.1.1.2.1.0 = STRING: "653.13.I"
SNMPv2-SMI::enterprises.318.1.1.1.1.2.2.0 = STRING: "09/27/06"
SNMPv2-SMI::enterprises.318.1.1.1.1.2.3.0 = STRING: "AS0640220851"
SNMPv2-SMI::enterprises.318.1.1.1.2.1.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.2.1.2.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.1.1.1.2.1.3.0 = STRING: "02/27/12"
SNMPv2-SMI::enterprises.318.1.1.1.2.2.1.0 = Gauge32: 100
SNMPv2-SMI::enterprises.318.1.1.1.2.2.2.0 = Gauge32: 33
SNMPv2-SMI::enterprises.318.1.1.1.2.2.3.0 = Timeticks: (552000) 1:32:00.00
SNMPv2-SMI::enterprises.318.1.1.1.2.2.4.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.2.2.5.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.2.2.8.0 = INTEGER: 27
SNMPv2-SMI::enterprises.318.1.1.1.2.2.9.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.2.2.10.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.2.3.1.0 = Gauge32: 1000
SNMPv2-SMI::enterprises.318.1.1.1.2.3.2.0 = Gauge32: 333
SNMPv2-SMI::enterprises.318.1.1.1.2.3.4.0 = INTEGER: 274
SNMPv2-SMI::enterprises.318.1.1.1.2.3.5.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.2.3.6.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.3.1.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.3.2.1.0 = Gauge32: 240
SNMPv2-SMI::enterprises.318.1.1.1.3.2.2.0 = Gauge32: 241
SNMPv2-SMI::enterprises.318.1.1.1.3.2.3.0 = Gauge32: 233
SNMPv2-SMI::enterprises.318.1.1.1.3.2.4.0 = Gauge32: 50
SNMPv2-SMI::enterprises.318.1.1.1.3.2.5.0 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.1.1.3.3.1.0 = Gauge32: 2404
SNMPv2-SMI::enterprises.318.1.1.1.3.3.2.0 = Gauge32: 2419
SNMPv2-SMI::enterprises.318.1.1.1.3.3.3.0 = Gauge32: 2332
SNMPv2-SMI::enterprises.318.1.1.1.3.3.4.0 = Gauge32: 500
SNMPv2-SMI::enterprises.318.1.1.1.4.1.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.4.1.2.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.4.2.1.0 = Gauge32: 240
SNMPv2-SMI::enterprises.318.1.1.1.4.2.2.0 = Gauge32: 50
SNMPv2-SMI::enterprises.318.1.1.1.4.2.3.0 = Gauge32: 15
SNMPv2-SMI::enterprises.318.1.1.1.4.2.4.0 = Gauge32: 0
SNMPv2-SMI::enterprises.318.1.1.1.4.3.1.0 = Gauge32: 2404
SNMPv2-SMI::enterprises.318.1.1.1.4.3.2.0 = Gauge32: 500
SNMPv2-SMI::enterprises.318.1.1.1.4.3.3.0 = Gauge32: 156
SNMPv2-SMI::enterprises.318.1.1.1.4.3.4.0 = Gauge32: 6
SNMPv2-SMI::enterprises.318.1.1.1.5.1.1.0 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.2.1 = STRING: "Device 1"
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.2.2 = STRING: "Device 2"
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.2.3 = STRING: "Device 3"
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.2.4 = STRING: "Device 4"
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.3.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.3.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.3.3 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.3.4 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.4.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.4.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.4.3 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.1.2.1.4.4 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.1.0 = INTEGER: 230
SNMPv2-SMI::enterprises.318.1.1.1.5.2.2.0 = INTEGER: 265
SNMPv2-SMI::enterprises.318.1.1.1.5.2.3.0 = INTEGER: 208
SNMPv2-SMI::enterprises.318.1.1.1.5.2.4.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.5.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.6.0 = INTEGER: 15
SNMPv2-SMI::enterprises.318.1.1.1.5.2.7.0 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.1.1.5.2.8.0 = Timeticks: (12000) 0:02:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.9.0 = Timeticks: (6000) 0:01:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.10.0 = Timeticks: (18000) 0:03:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.11.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.12.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.13.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.13.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.14.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.15.0 = Hex-STRING: 01 00 00 00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.8 = INTEGER: 8
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.1.9 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.1 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.2 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.2
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.3 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.3
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.4 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.5
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.5 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.6
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.6 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.8
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.7 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.9
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.8 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.10
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.2.9 = OID:
SNMPv2-SMI::enterprises.318.1.1.1.5.2.14
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.1 = STRING: "Not Configurable"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.2 = STRING: "253, 257, 261, 265
Vac"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.3 = STRING: "196, 200, 204, 208
Vac"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.4 = STRING: "0 , 30 seconds"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.5 = STRING: "00, 15, 30, 45, 60,
75, 90 percent"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.6 = STRING: "02, 05, 08, 11, 14,
17, 20, 23 minutes"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.7 = STRING: "000, 060, 120, 180,
240, 300, 360, 420 seconds"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.8 = STRING: "000, 090, 180, 270,
360, 450, 540, 630 seconds"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.16.1.3.9 = STRING: "Not Configurable"
SNMPv2-SMI::enterprises.318.1.1.1.5.2.17.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.2.18.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.19.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.20.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.21.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.2.22.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.2.23.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.2.24.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.25.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.2.26.0 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.1.1.5.2.27.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.5.2.28.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.5.2.30.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.1.1.1.5.2.31.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.5.2.34.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.6.1.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.2.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.3.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.4.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.5.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.6.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.7.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.8.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.6.2.9.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.7.2.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.7.2.2.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.7.2.3.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.7.2.4.0 = STRING: "06/24/2012"
SNMPv2-SMI::enterprises.318.1.1.1.7.2.5.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.7.2.6.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.7.2.7.0 = STRING: "Unknown"
SNMPv2-SMI::enterprises.318.1.1.1.8.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.9.1.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.10.1.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.10.1.2.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.10.1.3.0 = INTEGER: 120
SNMPv2-SMI::enterprises.318.1.1.1.10.1.4.0 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.1.10.1.5.0 = IpAddress: 224.0.0.100
SNMPv2-SMI::enterprises.318.1.1.1.10.1.6.0 = STRING: "::0"
SNMPv2-SMI::enterprises.318.1.1.1.10.2.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.11.1.1.0 = STRING:
"0001010000000000001000000000000000000000000000000000000000000000"
SNMPv2-SMI::enterprises.318.1.1.1.11.2.1.0 = STRING:
"00000000000000000000000000000000"
SNMPv2-SMI::enterprises.318.1.1.1.11.2.2.0 = ""
SNMPv2-SMI::enterprises.318.1.1.1.11.2.3.0 = ""
SNMPv2-SMI::enterprises.318.1.1.1.11.2.4.0 = ""
SNMPv2-SMI::enterprises.318.1.1.1.11.2.5.0 = ""
SNMPv2-SMI::enterprises.318.1.1.1.11.2.6.0 = ""
SNMPv2-SMI::enterprises.318.1.1.1.12.1.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.12.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.12.3.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.1.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.2.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.2.2.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.2.2.1.3.1 = STRING: "NA"
SNMPv2-SMI::enterprises.318.1.1.1.13.2.2.1.4.1 = STRING: "NA"
SNMPv2-SMI::enterprises.318.1.1.1.13.2.2.1.5.1 = STRING: "NA"
SNMPv2-SMI::enterprises.318.1.1.1.13.2.2.1.6.1 = STRING: "NA"
SNMPv2-SMI::enterprises.318.1.1.1.13.3.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.2.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.2.1.3.1 = ""
SNMPv2-SMI::enterprises.318.1.1.1.13.4.2.1.4.1 = ""
SNMPv2-SMI::enterprises.318.1.1.1.13.4.2.1.5.1 = ""
SNMPv2-SMI::enterprises.318.1.1.1.13.4.2.1.6.1 = ""
SNMPv2-SMI::enterprises.318.1.1.1.13.4.3.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.2.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.3.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.4.0 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.5.0 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.6.0 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.4.1.7.0 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.5.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.3.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.4.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.5.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.6.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.6.1.7.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.7.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.3.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.4.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.5.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.6.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.8.1.7.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.9.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.10.1.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.10.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.10.1.3.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.13.4.11.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.12.1.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.12.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.12.1.3.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.13.4.13.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.3.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.4.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.5.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.6.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.14.1.7.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.15.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.16.1.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.16.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.16.1.3.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.13.4.16.1.4.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.16.1.5.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.17.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.18.1.1.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.18.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.18.1.3.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.1.13.4.19.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.1.13.4.21.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.3.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.4.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.5.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.6.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.22.1.7.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.23.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.3.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.4.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.5.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.6.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.1.13.4.24.1.7.1 = STRING: "Not available"
SNMPv2-SMI::enterprises.318.1.1.3.1.2.1.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.3.1.2.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.2.1 = STRING: "Temp Sensor 1"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.2.2 = STRING: "Temp Sensor 2"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.3.1 = INTEGER: 40
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.3.2 = INTEGER: 40
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.4.1 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.4.2 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.5.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.5.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.6.1 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.6.2 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.7.1 = INTEGER: 30
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.7.2 = INTEGER: 30
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.8.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.8.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.9.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.9.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.10.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.10.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.11.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.11.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.12.1 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.12.2 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.13.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.13.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.14.1 = INTEGER: 90
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.14.2 = INTEGER: 90
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.15.1 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.15.2 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.16.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.16.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.17.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.17.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.18.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.18.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.19.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.19.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.20.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.20.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.21.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.21.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.22.1 = STRING: "Temp Sensor 1 Loc"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.22.2 = STRING: "Temp Sensor 2 Loc"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.2.1 = STRING: "Contact 1"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.2.2 = STRING: "Contact 2"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.2.3 = STRING: "Contact 3"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.2.4 = STRING: "Contact 4"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.3.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.3.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.3.3 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.3.4 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.4.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.4.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.4.3 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.4.4 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.5.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.5.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.5.3 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.5.4 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.6.1 = STRING: "Contact Location"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.6.2 = STRING: "Contact Location"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.6.3 = STRING: "Contact Location"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.4.1.6.4 = STRING: "Contact Location"
SNMPv2-SMI::enterprises.318.1.1.10.1.3.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.3.2.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.3.4.0 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.1.25.1.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.25.2.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.25.3.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.4.1.1.0 = STRING:
"00000000000000000000000000000000"
SNMPv2-SMI::enterprises.318.1.4.1.2.0 = ""
SNMPv2-SMI::enterprises.318.1.4.1.3.0 = ""
SNMPv2-SMI::enterprises.318.1.4.1.4.0 = ""
SNMPv2-SMI::enterprises.318.1.4.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.2.1.2.1 = STRING: "Smart-UPS"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.3.1 = STRING: "xxxxxxxxxxxxxx"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.4.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.2.1.5.1 = STRING: "Smart-UPS 1500"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.6.1 = STRING: "1"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.7.1 = STRING: "xxxxxxxxxx01"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.8.1 = INTEGER: 255
SNMPv2-SMI::enterprises.318.1.4.2.2.1.9.1 = STRING: "xxxxxxxxxx"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.10.1 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.4.2.2.1.11.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.2.1.12.1 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.2.1.13.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.2.1.14.1 = STRING: "SB-1"
SNMPv2-SMI::enterprises.318.1.4.2.3.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.4.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.4.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.4.1.2.1 = STRING: "ZA1126012136"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.2.2 = STRING: "ZA1126012136"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.3.1 = STRING: "apc_hw05_aos_517.bin"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.3.2 = STRING: "apc_hw05_sumx_517.bin"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.4.1 = STRING: "v5.1.7"
SNMPv2-SMI::enterprises.318.1.4.2.4.1.4.2 = STRING: "v5.1.7"
SNMPv2-SMI::enterprises.318.1.4.2.5.0 = INTEGER: 19
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.8 = INTEGER: 8
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.9 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.10 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.11 = INTEGER: 11
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.12 = INTEGER: 12
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.13 = INTEGER: 13
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.14 = INTEGER: 14
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.15 = INTEGER: 15
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.16 = INTEGER: 16
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.17 = INTEGER: 17
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.18 = INTEGER: 18
SNMPv2-SMI::enterprises.318.1.4.2.6.1.1.19 = INTEGER: 19
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.8 = INTEGER: 8
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.9 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.10 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.11 = INTEGER: 11
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.12 = INTEGER: 12
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.13 = INTEGER: 13
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.14 = INTEGER: 14
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.15 = INTEGER: 15
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.16 = INTEGER: 16
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.17 = INTEGER: 17
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.18 = INTEGER: 18
SNMPv2-SMI::enterprises.318.1.4.2.6.1.2.19 = INTEGER: 19
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.1 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.2 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.3 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.4 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.5 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.6 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.7 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.8 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.9 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.10 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.11 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.12 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.13 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.14 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.15 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.16 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.17 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.18 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.3.19 = STRING: "0"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.1 = STRING: "MTYx"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.2 = STRING: "MjM="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.3 = STRING: "ODA="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.4 = STRING: "NjAwMA=="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.5 = STRING: "NjAwMA=="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.6 = STRING: "NDQz"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.7 = STRING: "MjI="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.8 = STRING: "MjI="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.9 = STRING: "MTIz"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.10 = STRING: "MjU="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.11 = STRING: "MjE="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.12 = STRING: "MjE="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.13 = STRING: "Njg="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.14 = STRING: "NTQ2"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.15 = STRING: "MTgxMg=="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.16 = STRING: "MTYx"
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.17 = STRING: "MjE="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.18 = STRING: "MjE="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.4.19 = STRING: "OTk1MQ=="
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.1 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.3 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.4 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.5 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.6 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.7 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.8 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.9 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.10 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.11 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.12 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.13 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.14 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.15 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.16 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.17 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.18 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.6.1.5.19 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.7.0 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.4.2.8.1.1.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.1 = STRING: "power"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.2 = STRING: "env"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.3 = STRING: "env"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.4 = STRING: "env"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.5 = STRING: "env"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.6 = STRING: "env"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.2.7 = STRING: "env"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.1 = STRING: "ups"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.2 = STRING: "mon"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.3 = STRING: "sensor"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.4 = STRING: "sensor"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.5 = STRING: "mon"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.6 = STRING: "sensor"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.3.7 = STRING: "sensor"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.1 = STRING: "mxsu"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.2 = STRING: "emups"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.3 = STRING: "thext"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.4 = STRING: "inpext"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.5 = STRING: "uio"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.6 = STRING: "uio"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.4.7 = STRING: "thuio"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.1 = STRING: "3u"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.2 = STRING: "3b"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.3 = STRING: "3e"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.4 = STRING: "3c"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.5 = STRING: "1b"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.6 = STRING: "1a"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.5.7 = STRING: "1a"
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.4.2.8.1.6.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.4.2.9.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.4.2.10.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.4.2.12.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.4.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.4.4.3.0 = STRING: "<ip>:<port>, <type>"
SNMPv2-SMI::enterprises.318.1.4.4.4.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.4.5.1.0 = INTEGER: 21
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.5 = INTEGER: 5
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.6 = INTEGER: 6
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.7 = INTEGER: 7
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.8 = INTEGER: 8
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.9 = INTEGER: 9
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.10 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.11 = INTEGER: 11
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.12 = INTEGER: 12
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.13 = INTEGER: 13
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.14 = INTEGER: 14
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.15 = INTEGER: 15
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.16 = INTEGER: 16
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.17 = INTEGER: 17
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.18 = INTEGER: 18
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.19 = INTEGER: 19
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.20 = INTEGER: 20
SNMPv2-SMI::enterprises.318.1.4.5.2.1.1.21 = INTEGER: 21
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.1 = INTEGER: 258
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.2 = INTEGER: 259
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.3 = INTEGER: 263
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.4 = INTEGER: 265
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.5 = INTEGER: 267
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.6 = INTEGER: 269
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.7 = INTEGER: 271
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.8 = INTEGER: 276
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.9 = INTEGER: 277
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.10 = INTEGER: 281
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.11 = INTEGER: 293
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.12 = INTEGER: 294
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.13 = INTEGER: 296
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.14 = INTEGER: 298
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.15 = INTEGER: 303
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.16 = INTEGER: 312
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.17 = INTEGER: 328
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.18 = INTEGER: 309
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.19 = INTEGER: 374
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.20 = INTEGER: 378
SNMPv2-SMI::enterprises.318.1.4.5.2.1.2.21 = INTEGER: 565
SNMPv2-SMI::enterprises.318.1.4.6.1.1.0 = Hex-STRING: 07 00 00 00
SNMPv2-SMI::enterprises.318.1.4.7.1.0 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.7.3.0 = INTEGER: 4
SNMPv2-SMI::enterprises.318.1.4.7.4.0 = INTEGER: 3
SNMPv2-SMI::enterprises.318.1.4.7.5.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.1.1.0 = INTEGER: 4
SNMPv2-SMI::enterprises.318.2.1.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.2.1.2.1.1.3 = INTEGER: 3
SNMPv2-SMI::enterprises.318.2.1.2.1.1.4 = INTEGER: 4
SNMPv2-SMI::enterprises.318.2.1.2.1.2.1 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.1.2.1.2.2 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.1.2.1.2.3 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.1.2.1.2.4 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.1.2.1.3.1 = STRING: "public"
SNMPv2-SMI::enterprises.318.2.1.2.1.3.2 = STRING: "public"
SNMPv2-SMI::enterprises.318.2.1.2.1.3.3 = STRING: "public"
SNMPv2-SMI::enterprises.318.2.1.2.1.3.4 = STRING: "public"
SNMPv2-SMI::enterprises.318.2.1.2.1.4.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.1.2.1.4.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.1.2.1.4.3 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.1.2.1.4.4 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.1.2.1.5.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.5.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.5.3 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.5.4 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.6.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.6.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.6.3 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.2.1.6.4 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.3.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.2.1.4.0 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.1.5.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.1.6.1.0 = STRING: "07/06/2012"
SNMPv2-SMI::enterprises.318.2.1.6.2.0 = STRING: "18:10:50"
SNMPv2-SMI::enterprises.318.2.2.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.2.3.1.0 = INTEGER: 247380
SNMPv2-SMI::enterprises.318.2.3.2.0 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.3.3.0 = STRING: "225920"
SNMPv2-SMI::enterprises.318.2.3.4.0 = Gauge32: 0
SNMPv2-SMI::enterprises.318.2.3.5.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.2.3.6.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.3.7.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.2.3.8.0 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.3.9.0 = IpAddress: 0.0.0.0
SNMPv2-SMI::enterprises.318.2.3.10.0 = STRING: "202708"
SNMPv2-SMI::enterprises.318.2.3.11.0 = STRING: "Requested Reset"
SNMPv2-SMI::enterprises.318.2.3.12.0 = Gauge32: 0
SNMPv2-SMI::enterprises.318.2.3.13.0 = Gauge32: 0
SNMPv2-SMI::enterprises.318.2.3.14.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.2.3.15.0 = Timeticks: (0) 0:00:00.00
SNMPv2-SMI::enterprises.318.2.4.1.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.2.4.2.1.1.0 = STRING: "Unknown"
SNMPv2-SMI::enterprises.318.2.4.2.2.1.0 = STRING: "0.0.0.0"
SNMPv2-SMI::enterprises.318.2.4.2.3.1.0 = STRING: "***"
SNMPv2-SMI::enterprises.318.2.4.2.3.2.0 = STRING: "***"
SNMPv2-SMI::enterprises.318.2.4.2.3.3.0 = STRING: "***"
SNMPv2-SMI::enterprises.318.2.4.3.1.0 = INTEGER: 1
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev