On Aug 30, 2012, at 5:18 AM, Petr Topiarz wrote:

> UPS - CYBERPOWER CPS DX600E
> 
> upsc usb@localhost
> battery.charge: 100
> battery.charge.low: 10
> battery.charge.warning: 20
> battery.mfr.date: CPS
> battery.runtime: 1650
> battery.runtime.low: 300
> battery.type: PbAcid
> battery.voltage: 4.8
> battery.voltage.nominal: 12
> device.mfr: CPS
> device.model: DX600E
> device.type: ups
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: /dev/ugen0.00
> driver.version: 2.6.3-Unversioned directory
> driver.version.data: CyberPower HID 0.3
> driver.version.internal: 0.35
> input.transfer.high: 0
> input.transfer.low: 0
> input.voltage: 230.0
> input.voltage.nominal: 230
> output.voltage: 239.0
> ups.beeper.status: enabled
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.load: 21
> ups.mfr: CPS
> ups.model: DX600E
> ups.productid: 0501
> ups.realpower.nominal: 360
> ups.status: OL
> ups.timer.shutdown: -60
> ups.timer.start: 0
> ups.vendorid: 0764

Which OS is this? Looks like *BSD or Solaris?

Also, can you provide a few more details from this* list? In particular, it is 
helpful to know if the shutdown sequence works.

* http://www.networkupstools.org/stable-hcl.html#footnotes

> Nut-upsdev mailing list
> [email protected]
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to