As per request by Arnaud in the users list
Device manufacturer: Apollo
Device name: 1085VC (Retailer's product page:
http://shop.esquire.co.za/ProductDescription.aspx?id=583072)
upsc on mains power:
> $ upsc apollo
> battery.voltage: 13.50
> battery.voltage.nominal: 12.0
> beeper.status: enabled
> device.mfr:
> device.model:
> device.type: ups
> driver.name: blazer_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.6.3
> driver.version.internal: 0.04
> input.current.nominal: 3.0
> input.frequency: 50.0
> input.frequency.nominal: 50
> input.voltage: 225.0
> input.voltage.fault: 225.0
> input.voltage.nominal: 230
> output.voltage: 225.0
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.firmware: B1.12_APFB
> ups.load: 12
> ups.mfr:
> ups.model:
> ups.productid: 5161
> ups.status: OL
> ups.temperature: 31.0
> ups.type: offline / line interactive
> ups.vendorid: 0665
>
After killing power:
> Broadcast Message from nut@xxxx
>
> (somewhere) at 10:01 ...
>
UPS apollo@localhost on battery
upsc on battery power:
> $ upsc apollo
> battery.voltage: 12.30
> battery.voltage.nominal: 12.0
> beeper.status: enabled
> device.mfr:
> device.model:
> device.type: ups
> driver.name: blazer_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.6.3
> driver.version.internal: 0.04
> input.current.nominal: 3.0
> input.frequency: 0.0
> input.frequency.nominal: 50
> input.voltage: 0.0
> input.voltage.fault: 0.0
> input.voltage.nominal: 230
> output.voltage: 230.0
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.firmware: B1.12_APFB
> ups.load: 12
> ups.mfr:
> ups.model:
> ups.productid: 5161
> ups.status: OB
> ups.temperature: 31.0
> ups.type: offline / line interactive
> ups.vendorid: 0665
Shutdown sequence (test)
> $ sudo upsdrvctl -t shutdown
> Network UPS Tools - UPS driver controller 2.6.3
> *** Testing mode: not calling exec/kill
> 0.000000
> If you're not a NUT core developer, chances are that you're told to enable
> debugging
> to see why a driver isn't working for you. We're sorry for the confusion,
> but this is
> the 'upsdrvctl' wrapper, not the driver you're interested in.
> Below you'll find one or more lines starting with 'exec:' followed by an
> absolute
> path to the driver binary and some command line option. This is what the
> driver
> starts and you need to copy and paste that line and append the debug flags
> to that
> line (less the 'exec:' prefix).
> 0.000380 Shutdown UPS: apollo
> 0.000419 exec: /lib/nut/blazer_usb -a apollo -k
Forced shutdown:
> $ sudo upsmon -c fsd
> Network UPS Tools upsmon 2.6.3
>
>
> Broadcast Message from nut@xxxx
>
> (somewhere) at 10:27 ...
>
>
>
> UPS apollo@localhost: forced shutdown in progress
>
>
>
>
>
> Broadcast Message from nut@xxxx?u?
>
> (somewhere) at 10:28 ...
>
>
>
> Executing automatic power-fail shutdown
>
>
>
>
>
>
>
> Broadcast Message from nut@xxxx?{?
>
> (somewhere) at 10:28 ...
>
>
>
> Auto logout and shutdown proceeding
>
>
>
>
>
> Broadcast Message from nut@xxxx
>
> (somewhere) at 10:28 ...
>
>
>
> Executing automatic power-fail shutdown
>
>
>
>
>
>
>
> Broadcast Message from nut@xxxx
>
> (somewhere) at 10:28 ...
>
>
>
> Auto logout and shutdown proceeding
>
>
>
> Broadcast message from root@xxxx
> (unknown) at 10:28 ...
> The system is going down for halt NOW!
> Broadcast message from root@xxxx
> (unknown) at 10:28 ...
> The system is going down for halt NOW!
UPS Switched off
> Broadcast Message from nut@xxxx
>
> (somewhere) at 10:32 ...
>
>
>
> UPS apollo@localhost on battery
> Broadcast Message from nut@xxxx
>
> (somewhere) at 11:03 ...
>
>
>
> UPS apollo@localhost battery is low
>
>
>
>
>
> Broadcast Message from nut@xxxx
>
> (somewhere) at 11:03 ...
>
>
>
> Executing automatic power-fail shutdown
>
>
>
>
>
>
>
> Broadcast Message from nut@xxxx
>
> (somewhere) at 11:03 ...
>
>
>
> Auto logout and shutdown proceeding
>
>
>
> Broadcast message from root@xxxx
> (unknown) at 11:03 ...
>
Shutdown successfully
Cheers
Mike
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev