Hi Michael,

2012/11/17 michael <[email protected]>

> Manufacturer: Aviem Power RT 1000-3000VA
> Description: Rack/Tower Intelligent Online LCD UPS.
>
> connected with serial cable.
>
> #upsc
>
> battery.voltage: 24.96
> battery.voltage.low: 21.5
> battery.voltage.nominal: 24.0
> beeper.status: enabled
> device.mfr:
> device.model:
> device.type: ups
> driver.name: blazer_ser
> driver.parameter.pollinterval: 2
> driver.parameter.port: /dev/ttyUSB1
> driver.version: 2.6.3
> driver.version.internal: 1.51
> input.current.nominal: 5.0
> input.frequency: 50.0
> input.frequency.nominal: 50
> input.voltage: 224.3
> input.voltage.fault: 0.0
> input.voltage.nominal: 220
> output.voltage: 230.7
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.firmware: R1.1.1
> ups.load: 11
> ups.mfr:
> ups.model:
> ups.status: OL BYPASS
> ups.temperature: 35.0
> ups.type: online
>
> #cat /var/log/syslog | grep upsd
> Nov 17 17:27:31 a upsd[1625]: listening on 127.0.0.1 port 3493
> Nov 17 17:27:31 a upsd[1625]: listening on ::1 port 3493
> Nov 17 17:27:31 a upsd[1625]: Connected to UPS [aviem]: blazer_ser-aviem
> Nov 17 17:27:31 a upsd[1626]: Startup successful
> Nov 17 17:27:31 a upsd[1626]: User [email protected] logged into UPS
> [aviem]
>
> Successful Shutdown with these settings:
>
> #cat /etc/nut/ups.conf
> driver = blazer_ser
> port = /dev/ttyUSB1
> default.battery.voltage.low = 21.5
>
> upsmon shutdowns the system at around 23v without setting
> default.battery.voltage.low. although, seems the ups sends a shutdown
> signal at around 22v. anyway 21.5 seems reasonable.
>

thanks for your report, I've just committed the following entry to the HCL:

# <manufacturer>    <device type>    <support level>    <model name>
<model extra>    <driver [parameters]>
"Aviem Systems"    "ups"    "2"    "Aviem Power RT 1000-3000VA"    ""
"blazer_ser"

http://trac.networkupstools.org/projects/nut/changeset/3782

cheers,
Arnaud
-- 
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to