Hi Martin
2012/12/14 Martin Sarsale | Properati <[email protected]>
> Lyonn CTB-1200
>
> root@frambuesa:~# upsc lyonn@localhost
> battery.voltage: 27.20
> battery.voltage.nominal: 24.0
> beeper.status: enabled
> device.type: ups
> driver.name: blazer_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.4.3
> driver.version.internal: 0.03
> input.current.nominal: 5.0
> input.frequency: 49.9
> input.frequency.nominal: 50
> input.voltage: 213.3
> input.voltage.fault: 213.3
> input.voltage.nominal: 220
> output.voltage: 213.8
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.load: 10
> ups.productid: 5161
> ups.status: OL
> ups.type: offline / line interactive
> ups.vendorid: 0665
>
>
> I'm not sure what you expect with "shutdown sequence testing results"
> ("it worked ok", or something else? :)
>
a statement that it indeed work, as per the shutdown procedure, is enough.
after all, if it crashes the protected system, you'll probably be the first
victim ;)
I've just committed a clarified wording (r3835) to make it more obvious,
thanks:
http://trac.networkupstools.org/projects/nut/changeset/3835
before adding a new entry to the HCL, could you please point us at the
manufacturer website?
all I can find is solytec.com.ar, and no special refs apart from tags/meta!
Thanks for all your work!
>
thanks for the thanks ;)
cheers,
Arno
--
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr
_______________________________________________
Nut-upsdev mailing list
[email protected]