Hi All,

  I put my Compaq R3000 UPS on NUT.

Every once in a while the battery alarm light turns on, on the front of the UPS. Maybe once every couple of days or so. When that happens
I get the following output in /var/log/messages:

Sep 22 01:51:46 mail upscode2[90734]: Unknown response to UPDS: .20 MOUL1
Sep 22 01:51:46 mail upscode2[90734]: Unknown response to UPDS: 0119.20 MOIL1 Sep 22 01:51:46 mail upscode2[90734]: Unknown response to UPDS: 0015.57 MOPL1 Sep 22 01:51:46 mail upscode2[90734]: Unknown response to UPDS: 0001.82 MOSL1 Sep 22 01:51:46 mail upscode2[90734]: Unknown response to UPDS: 0001.83 MOFFF Sep 22 01:51:49 mail upscode2[90734]: Communications with UPS lost: Empty value from UPS for UPDS 0060.00! Sep 22 01:51:49 mail upsd[90736]: Data for UPS [R3000] is stale - check driver
Sep 22 01:51:53 mail upscode2[90734]: Communications with UPS re-established
Sep 22 01:51:53 mail upsd[90736]: UPS [R3000] data is no longer stale


I just replaced the batteries in this UPS about 5 months ago.  Does the
fact that battery.charge equal 92.7 have anything to do with this?

Here's the status output:

root@mail:/var/log # upsc R3000@localhost
battery.capacity.nominal: 17.00
battery.charge: 92.7
battery.runtime: 420
battery.voltage: 55.20
battery.voltage.maximum: 56.40
battery.voltage.minimum: 40.00
battery.voltage.nominal: 48.00
device.mfr: unknown
device.model: UPS 3000 VA FW -0026
device.serial: E00202401
device.type: ups
driver.name: upscode2
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/cuau0
driver.version: 2.6.5
driver.version.internal: 0.88
input.phases: 1
input.voltage: 121.00
input.voltage.maximum: 145.00
input.voltage.minimum: 84.00
input.voltage.nominal: 120.00
output.current: 15.15
output.current.maximum: 28.50
output.current.nominal: 25.00
output.frequency: 60.00
output.frequency.maximum: 63.00
output.frequency.minimum: 57.00
output.phases: 1
output.power: 1.82
output.realpower: 1810.00
output.realpower.nominal: 2250.00
output.voltage: 121.00
output.voltage.maximum: 128.00
output.voltage.minimum: 108.00
output.voltage.nominal: 120.00
ups.delay.reboot: 060
ups.delay.shutdown: 180
ups.load: 60.6
ups.mfr: unknown
ups.model: UPS 3000 VA FW -0026
ups.power.nominal: 3000.00
ups.serial: E00202401
ups.status: OL
root@mail:/var/log #


Thanks,
Ted

_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to