Hi Jim

As per NUT HW compatibility list, the driver should be blazer_usb:
http://www.networkupstools.org/stable-hcl.html

We are currently merging a new driver to replace blazer_* and would also
appreciate feedback on this if you can.

Cheers,
Arno
--
(sent from my eeePad... please excuse my brevity)
Le 9 nov. 2013 14:25, "Jim Klimov" <[email protected]> a écrit :

> Hello all,
>
>   I am trying to set up my brother's UPS (remotely over internet)
> on an OpenIndiana-based storage box. According to him, the UPS is
> probably an Ippon Back Power Pro 600 dated around 2003 (battery
> recently replaced), and it has an USB connection.
>
>  Sorry for a relatively long post with a log of my successes and
> failures, in the hopes that someone would point out what I did
> wrong. I guess this is among my first experiences with USB in
> Solaris - for a decade we had either serial or snmp UPSes :)
>
>  I have found some assorted blog posts, following which I found
> that the proper driver nowadays is blazer_usb (and earlier versions
> of NUT had an ippon driver, which was AFAIK serial-only). However
> I can't get the blazer_usb driver to recognize this UPS, and there
> are some other problems. Another driver says it found the UPS, but
> I am not sure about its correctness :)
>
>   Main question is if this is some mistake of mine, an OS specific
> thing, or just that this particular UPS is not supported (or maybe
> its mgmt parts are broken - who knows, so far they haven't been
> tested in any other OS)?
>
>   For the record, here's what I did so far:
>
> 1) Installed the GCC-based development environment in OI, libusb
>    and other packages that the build wanted
>
> 2) Compiled nut-2.6.5 (with the patch mentioned a week ago)
>
> 3) Installed NUT in the global zone, and defined the ups.conf entry:
>
> [ippon]
>         driver = blazer_usb
>         port = auto
>         desc = "Ippon Pro 600 USB"
>
> [hid]
>         driver = usbhid-ups
>         port = auto
>
>
> 4) The interesting part is about getting USB to be found at all :)
>
> Do credit where credit is due - some helpful posts were:
> http://barbz.com.au/blog/?p=407
> http://www.mail-archive.com/[email protected].
> debian.org/msg06556.html
>
>
> # /usr/sbin/cfgadm -lv usb8/5
> Ap_Id                          Receptacle   Occupant     Condition
> Information
> When         Type         Busy     Phys_Id
>
> usb8/5                         connected    configured   ok
> Mfg: OMRON  Product: 87XXUPS  NConfigs: 1  Config: 0  <no cfg str descr>
> unavailable  usb-input    n        /devices/pci@0,0/pci103c,1609@12:5
>
> # prtconf -v | ggrep -B20 -A20 OMRON | egrep "value='(NAME|usb)"
>
>                         value='NAME= ugen0 Power' + '0=USB D3 State' +
> '3=USB D0 State'
>                         value='usb6da,3.0' + 'usb6da,3' +
> 'usbif6da,class3.0.0' + 'usbif6da,class3.0' + 'usbif6da,class3' +
> 'usbif,class3.0.0' + 'usbif,class3.0' + 'usbif,class3' + 'usb,device'
>
>
> So this UPS has VendorID 06DA, ProductID 0003.
>
> # rem_drv ugen
> # add_drv -i '"usb6da,3.0"' -m '* 0666 nobody nobody' ugen
>
> # dmesg | tail
> ...
> Nov  9 15:42:10 n54l usba: [ID 912658 kern.info] USB 1.10 device
>   (usb6da,3) operating at low speed (USB 1.x) on USB 1.10 root hub:
>   input@5, ugen0 at bus address 2
>
> Nov  9 15:42:10 n54l usba: [ID 349649 kern.info]        OMRON 87XXUPS
>
> Nov  9 15:42:10 n54l genunix: [ID 936769 kern.info] ugen0 is
>   /pci@0,0/pci103c,1609@12/input@5
>
>
> However, the UPS is *usually* not found at all:
>
> root@n54l:/# /usr/local/ups/bin/usbhid-ups -DDDD -a hid
>
> Network UPS Tools - Generic HID driver 0.37 (2.6.5)
> USB communication driver 0.31
>    0.000000     debug level is '4'
>    0.001180     upsdrv_initups...
>    0.002196     No appropriate HID device found
>    0.002241     No matching HID UPS found
>
>
> root@n54l:/# /usr/local/ups/bin/blazer_usb -DDDD -a ippon
>
> Network UPS Tools - Megatec/Q1 protocol USB driver 0.09 (2.6.5)
>    0.000000     debug level is '4'
>    0.001235     No appropriate HID device found
>    0.001287     No supported devices found. Please check your device
> availability with 'lsusb' and make sure you have an up-to-date version
> of NUT. If this does not help, try running the driver with at least
> 'subdriver', 'vendorid' and 'productid' options specified. Please refer
> to the man page for details about these options (man 8 blazer).
>
>
>
> I wrote that it is *usually* not found, because early in my tests
> (i.e. soon after boot) it was actually discovered as a device on
> the USB bus, but with no details and unrecognized as a known UPS.
>
> Actually, I've tracked this down to the USB device nodes changing
> ownership from nobody:nobody to root:root during blazer_ups driver
> startup :\ I am so far at a loss as to "The why". Even weirder,
> sometimes the device links get gone as well, and this recovers them:
>
> # devfsadm -Cv
> devfsadm[5083]: verbose: symlink /dev/usb/6da.3/0/devstat ->
> ../../../../devices/pci@0,0/pci103c,1609@12/input@5:6da.3.devstat
> devfsadm[5083]: verbose: symlink /dev/usb/6da.3/0/cntrl0 ->
> ../../../../devices/pci@0,0/pci103c,1609@12/input@5:6da.3.cntrl0
> devfsadm[5083]: verbose: symlink /dev/usb/6da.3/0/cntrl0stat ->
> ../../../../devices/pci@0,0/pci103c,1609@12/input@5:6da.3.cntrl0stat
> devfsadm[5083]: verbose: symlink /dev/usb/6da.3/0/if0in1 ->
> ../../../../devices/pci@0,0/pci103c,1609@12/input@5:6da.3.if0in1
> devfsadm[5083]: verbose: symlink /dev/usb/6da.3/0/if0in1stat ->
> ../../../../devices/pci@0,0/pci103c,1609@12/input@5:6da.3.if0in1stat
>
>
> Running as root does work around the former problem, but the UPS
> is still not recognized by any of the protocols:
>
> # /usr/local/ups/bin/blazer_usb -DDDD -a ippon -u root
> Network UPS Tools - Megatec/Q1 protocol USB driver 0.09 (2.6.5)
>    0.000000     debug level is '4'
>    0.022634     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    0.045564     - VendorID: 06da
>    0.045663     - ProductID: 0003
>    0.045733     - Manufacturer: OMRON
>    0.045788     - Product: 87XXUPS
>    0.045841     - Serial Number: unknown
>    0.045899     - Bus: /dev/usb
>    0.045951     Trying to match device
>    0.046011     Device matches
>    0.046187     Trying megatec protocol...
>    0.049547     send: Q1
>    0.101572     read: (217.0 2
>    0.101674     blazer_status: short reply
>    0.101733     Status read 1 failed
>    1.266722     send: I/O error
>    1.266900     blazer_status: short reply
>    1.266956     Status read 2 failed
>    1.267648     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    1.271661     - VendorID: 06da
>    1.271763     - ProductID: 0003
>    1.271823     - Manufacturer: unknown
>    1.271877     - Product: unknown
>    1.271925     - Serial Number: unknown
>    1.271974     - Bus: /dev/usb
>    1.272020     Trying to match device
>    1.272074     Device does not match - skipping
>    1.272175     No appropriate HID device found
>    1.272256     blazer_status: short reply
>    1.272309     Status read 3 failed
>    1.272358     Trying mustek protocol...
>    1.272933     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    1.277622     - VendorID: 06da
>    1.277670     - ProductID: 0003
>    1.277693     - Manufacturer: unknown
>    1.277715     - Product: unknown
>    1.277734     - Serial Number: unknown
>    1.277756     - Bus: /dev/usb
>    1.277774     Trying to match device
>    1.277793     Device does not match - skipping
>    1.277838     No appropriate HID device found
>    1.277861     blazer_status: short reply
>    1.277885     Status read 1 failed
>    1.278143     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    1.282635     - VendorID: 06da
>    1.282726     - ProductID: 0003
>    1.282782     - Manufacturer: unknown
>    1.282829     - Product: unknown
>    1.282881     - Serial Number: unknown
>    1.282932     - Bus: /dev/usb
>    1.282979     Trying to match device
>    1.283026     Device does not match - skipping
>    1.283124     No appropriate HID device found
>    1.283224     blazer_status: short reply
>    1.283273     Status read 2 failed
>    1.283866     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    1.288638     - VendorID: 06da
>    1.288727     - ProductID: 0003
>    1.288779     - Manufacturer: unknown
>    1.288829     - Product: unknown
>    1.288881     - Serial Number: unknown
>    1.288927     - Bus: /dev/usb
>    1.288975     Trying to match device
>    1.289028     Device does not match - skipping
>    1.289123     No appropriate HID device found
>    1.289189     blazer_status: short reply
>    1.289239     Status read 3 failed
>    1.289285     Trying megatec/old protocol...
>    1.289829     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    1.290230     Failed to open device, skipping. (I/O error)
>    1.290291     No appropriate HID device found
>    1.290339     blazer_status: short reply
>    1.290388     Status read 1 failed
>    1.300475     No appropriate HID device found
>    1.300572     blazer_status: short reply
>    1.300622     Status read 2 failed
>    1.321620     No appropriate HID device found
>    1.321719     blazer_status: short reply
>    1.321772     Status read 3 failed
>    1.321827     Trying zinto protocol...
>    1.322081     No appropriate HID device found
>    1.322144     blazer_status: short reply
>    1.322192     Status read 1 failed
>    1.322417     No appropriate HID device found
>    1.322479     blazer_status: short reply
>    1.322530     Status read 2 failed
>    1.322747     No appropriate HID device found
>    1.322808     blazer_status: short reply
>    1.322860     Status read 3 failed
>    1.322909     No supported UPS detected
>
>
> # /usr/local/ups/bin/usbhid-ups -DDDD -a hid -u root
> Network UPS Tools - Generic HID driver 0.37 (2.6.5)
> USB communication driver 0.31
>    0.000000     debug level is '4'
>    0.000342     upsdrv_initups...
>    0.021748     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    0.044606     - VendorID: 06da
>    0.044658     - ProductID: 0003
>    0.044679     - Manufacturer: OMRON
>    0.044709     - Product: 87XXUPS
>    0.044730     - Serial Number: unknown
>    0.044753     - Bus: /dev/usb
>    0.044778     Trying to match device
>    0.044805     This Liebert device (06da:0003) is not (or perhaps not
> yet) supported by usbhid-ups. Please make sure you have an up-to-date
> version of NUT. If this does not fix the problem, try running the
> driver with the '-x productid=0003' option. Please report your results
> to the NUT user's mailing list <[email protected]>.
>
>    0.044833     Device does not match - skipping
>    0.044891     No appropriate HID device found
>    0.044923     No matching HID UPS found
>
>
> (no idea why liebert comes up - vendor id?)
>
> # /usr/local/ups/bin/usbhid-ups -DDDD -a hid -u root -x productid=0003
> Network UPS Tools - Generic HID driver 0.37 (2.6.5)
> USB communication driver 0.31
>    0.000000     debug level is '4'
>    0.000739     upsdrv_initups...
>    0.022865     Checking device (06DA/0003) (/dev/usb/6da.3/0)
>    0.045791     - VendorID: 06da
>    0.045896     - ProductID: 0003
>    0.045958     - Manufacturer: OMRON
>    0.046020     - Product: 87XXUPS
>    0.046073     - Serial Number: unknown
>    0.046136     - Bus: /dev/usb
>    0.046189     Trying to match device
>    0.046282     Device matches
>    0.051733     HID descriptor, method 1: (9 bytes) => 09 21 11 01 00 01
> 22 1b 00
>    0.051848     i=0, extra[i]=09, extra[i+1]=21
>    0.051920     HID descriptor, method 2: (9 bytes) => 09 21 11 01 00 01
> 22 1b 00
>    0.051978     HID descriptor length 27
>    0.058714     Report Descriptor size = 27
>    0.058817     Report Descriptor: (27 bytes) => 06 00 ff 09 01 a1 01 09
> 02 15 00 26 ff 00
>    0.058887      75 08 95 08 81 82 09 02 95 08 91 82 c0
>    0.059102     Using subdriver: Liebert HID 0.3
>    0.059195     Entering libusb_get_report
>    0.060809     libusb_get_report: I/O error
>    0.060914     Can't retrieve Report 00: I/O error
>    0.060993     Path: ff000001.ff000002, Type: Input, ReportID: 0x00,
> Offset: 0, Size: 8
>    0.061057     Entering libusb_get_report
>    0.061850     libusb_get_report: I/O error
>    0.061954     Can't retrieve Report 00: I/O error
>    0.062024     Path: ff000001.ff000002, Type: Output, ReportID: 0x00,
> Offset: 0, Size: 8
>    0.062132     Report descriptor retrieved (Reportlen = 27)
>    0.062189     Found HID device
>    0.062245     Detected a UPS: OMRON/87XXUPS
>    0.062316     string_to_path: depth = 3
>    0.062443     string_to_path: depth = 3
>    0.062521     string_to_path: depth = 3
>    0.062588     string_to_path: depth = 3
>    0.062663     string_to_path: depth = 3
>    0.062727     string_to_path: depth = 3
>    0.062800     string_to_path: depth = 4
>    0.062867     string_to_path: depth = 4
>    0.062936     string_to_path: depth = 4
>    0.063001     string_to_path: depth = 4
>    0.063069     string_to_path: depth = 4
>    0.063133     string_to_path: depth = 4
>    0.063195     find_nut_info: unknown info type: load.off.delay
>    0.063249     find_nut_info: unknown info type: load.on.delay
>    0.063305     find_nut_info: unknown info type: load.off.delay
>    0.063381     upsdrv_initinfo...
>    0.063452     upsdrv_updateinfo...
>    0.063507     Not using interrupt pipe...
>    0.063559     Quick update...
>    0.064358     dstate_init: sock /var/state/ups/usbhid-ups-hid open on fd
> 7
>    0.064417     upsdrv_updateinfo...
>    0.064442     Not using interrupt pipe...
>    0.064466     Quick update...
>    2.064222     upsdrv_updateinfo...
>    2.064347     Not using interrupt pipe...
>    2.064421     Quick update...
>    4.063982     upsdrv_updateinfo...
>    4.064080     Not using interrupt pipe...
>    4.064108     Quick update...
> (this goes on forever)
>
> However (after starting upsd) it seems that the UPS is seen somehow:
>
> #  /usr/local/ups/bin/upsc hid@localhost
>
> device.mfr: OMRON
> device.model: 87XXUPS
> device.type: ups
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.productid: 0003
> driver.version: 2.6.5
> driver.version.data: Liebert HID 0.3
> driver.version.internal: 0.37
> ups.mfr: OMRON
> ups.model: 87XXUPS
> ups.productid: 0003
> ups.status: OB
> ups.vendorid: 06da
>
>
> I am puzzled why it is considered "OB" for example, which makes this
> information somewhat useless for automated shutdowns...
>
> It is indeed quite possible, that this particular piece of hardware is
> just not supported by NUT and there are few-to-no problems regarding
> the OS/Software side of my setup... I'd welcome confirmations though :)
> And ideas about the volatility of device node setup (disappearance of
> symlinks and changes of ownership with blazer_usb - but not with the
> usbhid-ups driver) are also welcome.
>
> Also, for the record, it is very inconvenient that starting an UPS
> driver requires an entry in the ups.conf nowadays - basically, to
> find a matching driver I'd have to make dozens of such entries and
> see if any of them works... I'm lucky I got a possible hit on my
> second attempt.
>
> Thanks,
> //Jim Klimov
>
>
> _______________________________________________
> Nut-upsdev mailing list
> [email protected]
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev
>
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to