CyberPower Battery Backup with Surge Protection, model LE825G
Appears to function properly with the driver listed on the HCL for the
Cyber Power Systems ups 2 685AVR USB (usbhid-ups).
Tested with shutdown mode "UPS Goes On Battery" with a 5 second timer
and the system successfully shutdown as expected.
upsc output:
upsc ups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 1110
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 8.7
battery.voltage.nominal: 12
device.mfr: CPS
device.model: CP825AVR-G
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ugen2.3
driver.version: 2.6.5
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.37
input.transfer.high: 140
input.transfer.low: 90
input.voltage: 126.0
input.voltage.nominal: 120
output.voltage: 126.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 29
ups.mfr: CPS
ups.model: CP825AVR-G
ups.productid: 0501
ups.realpower.nominal: 450
ups.status: OL
ups.timer.shutdown: -1
ups.timer.start: 0
ups.vendorid: 0764
Product page:
http://www.cyberpowersystems.com/products/ups-systems/retail-products/LE825G.html
Operating environment: FreeNAS-9.1.1-RELEASE-x64 (a752d35)
System: Dell Inspiron 660s, Pentium G2030 @ 3.00GHz, 4GB Memory