On Jan 10, 2014, at 12:58 PM, Elliot Dierksen wrote: > I am using NUT 2.6.5 as part of FreeNAS 9.2.0. I am using an APC Smart-UPS > 5000 RM DL4 with a AP9619 network management card. NUT properly detects > when the UPS goes on battery and initiates a shutdown after the configured > time. The problem I have is that I am using a 208V unit on a 240V circuit. > That means the normal state for the UPS is "TRIM". NUT doesn't treat that > as an on line condition, so the system shuts down every time there is a > power failure.
I'm confused. When the snmp-ups driver starts, does it immediately see the TRIM state and initiate a shutdown, or does this only happen after going on battery once? Other SNMP sub-drivers map the "TRIM" status to "OL TRIM", so I suspect the same could be done for the 'apcc' MIB setting. > I realize what I am doing is a bit of a kludge, but I can't > get a 208V circuit easily in my house. > > I am also getting these messages whenever NUT starts > > "[CR-UPS] Warning: excessive poll failures, limiting error reporting" >From a quick look at the code, it's possible that the MIB auto-detection is >pushing the error count over the limit. What configuration variables do you >have in ups.conf? -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev