On Jun 3, 2014, at 5:16 PM, Shen Chuan wrote:

> We have an Eaton 3S 550 UPS using NUT tool to send power loss event. By 
> default the power voltage threshold is set to 85 volts. If the voltage is 
> less than 85 volts, it will trigger ONBATT event from NUT. Is there a way in 
> NUT we can change the threshold from 85 volts to a lower voltage like 40 
> volts?

It might be possible with upsrw - try modifying "input.transfer.low" and 
"input.transfer.boost.low".

However, 40V to 110-120V is a long way to boost. Is this UPS rated for such a 
wide voltage range?

You could also check for sensitivity settings. I don't know about the 3S in 
particular, but theoretically, usbhid-ups supports those sorts of settings.

-- 
Charles Lepple
clepple@gmail