> From the 2012 thread, it looks like the DelayBeforeStartup report might be
> encoded as hexadecimal:
>
>    0.440981 refresh_report_buffer: expected 3 bytes, but got 2 instead
>    0.441006 Report[err]: (2 bytes) => 0f 00
>    0.441024 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature,
> ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
>
>    0.445020 Report[get]: (*5 bytes*) => 10 *30 30 30 30*
>    0.445051 Path: UPS.PowerSummary.*DelayBeforeStartup*, Type: Feature,
> ReportID: 0x10, Offset: 0, Size: 32, Value: 12336
>

Here is my output:

   0.356896     Path: UPS.PowerSummary.*DelayBeforeShutdown*, Type:
Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.361823     refresh_report_buffer: expected 5 bytes, but got 3 instead
   0.361893     Report[err]: (3 bytes) => *10 00 00*
   0.361951     Path: UPS.PowerSummary.*DelayBeforeStartup*, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 32, Value: 0
   0.366816     refresh_report_buffer: expected 3 bytes, but got 2 instead
   0.366873     Report[err]: (2 bytes) => *11 dc*

It looks like my UPS with has another output. Probably, you were right and
we really have different behaviour for the same ID?..

You might be able to use "explore" mode in usbhid-ups to dump all of the
> variables to see what is missing from the driver.
>

I will do some exploration as soon as have direct access to the UPS.

Hope that PowerCOM team will make some clarification here.

2014-11-12 15:39 GMT+02:00 Charles Lepple <[email protected]>:

> On Nov 12, 2014, at 3:53 AM, Maksym Bodaniuk <[email protected]>
> wrote:
>
> Hi Charles,
>
> Sigh, I wish the vendors wouldn't change operation without changing 
> identifiers.
>
> Do you have any recommendations on how the driver should decide whether it is 
> an old 0x0004 or new 0x0004 device?
>
>
> No-no, there is no an old 0x0004 or new 0x0004 device, I guess that we
> have to handle general case for all 0d9f:0x0004 devices.
>
>
> You're right, I jumped to the wrong conclusion on that one.
>
> There was another thread about this, where it seems there are other
> mismatches between the report descriptor sizes, and what the UPS expects:
>
> http://article.gmane.org/gmane.comp.monitoring.nut.user/7662
>
> From PCM_USB_LIST_device2014.pdf attached by Alexey Morozov:
> "(VGD, VRT, RPT, .. and new UPS etc.) - 0X04.". According to this doc we
> can expect that all new PowerCOM devices will be shipped with ID
> 0X0d9f:0X04. For example, my Imperial IMD-825AP LCD has 0x0004, but an old
> examples of this model have 0Xa2.
>
> Also, lets take a look inside PCM_USB_protocol_2014.pdf:
> "16 0x8456 Delay Before Startup R/W *5 Byte*"
> And old specs for BNT protocol:
> "16  8456  DelayBeforeStartup *** R/W *2 Byte*"
> So, the length for DelayBeforeStartup report changed from 2 to 5 bytes.
>
>
> From the 2012 thread, it looks like the DelayBeforeStartup report might be
> encoded as hexadecimal:
>
>    0.440981 refresh_report_buffer: expected 3 bytes, but got 2 instead
>    0.441006 Report[err]: (2 bytes) => 0f 00
>    0.441024 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature,
> ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
>
>    0.445020 Report[get]: (*5 bytes*) => 10 *30 30 30 30*
>    0.445051 Path: UPS.PowerSummary.*DelayBeforeStartup*, Type: Feature,
> ReportID: 0x10, Offset: 0, Size: 32, Value: 12336
>
> You can try various encodings in
> drivers/powercom-hid.c:powercom_startup_fun().
>
> Or there was added a new report for example:
> "44 0x8436 Temperature R/O 2 Byte"
> This was missed in the old specification.
>
>
> You might be able to use "explore" mode in usbhid-ups to dump all of the
> variables to see what is missing from the driver.
>
> All these things lead me to thought that powercom hid driver should handle
> 0x0004 case more careful.
>
> Here is an older Powercom device with productId 00a2 - how does your output 
> of 'upsc' compare?
>
>
> Here is my output for 0x0004:
>
> :/etc/nut$ upsc powercom
> battery.charge: 100
> battery.charge.low: 15
> battery.charge.warning: 30
> battery.date: 2010/12/20
> battery.runtime: 800
> battery.type: PbAc
> device.mfr: POWERCOM Co.,LTD
> device.model: HID UPS Battery
> device.serial: 004-0D9F-000
> device.type: ups
> driver.flag.ignorelb: enabled
> driver.name: usbhid-ups
> driver.parameter.offdelay: 10
> driver.parameter.ondelay: 100
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.version: 2.6.4
> driver.version.data: PowerCOM HID 0.3
> driver.version.internal: 0.37
> input.frequency: 50.0
> input.voltage: 214.0
> input.voltage.nominal: 220
> output.frequency: 50.0
> output.voltage: 214.0
> output.voltage.nominal: 220
> ups.beeper.status: enabled
> ups.date: 2010/12/20
> ups.delay.shutdown: 20
> ups.delay.start: 60
> ups.load: 0
> ups.mfr: POWERCOM Co.,LTD
> ups.model: HID UPS Battery
> ups.productid: 0004
> ups.serial: 004-0D9F-000
> ups.status: OL
> ups.test.result: Done and passed
> ups.timer.shutdown: 0
> ups.timer.start: 0
> ups.vendorid: 0d9f
>
> On 11/12/2014 03:05 AM, Charles Lepple wrote:
>
> On Nov 11, 2014, at 3:30 PM, Maksym Bodaniuk <[email protected]> 
> <[email protected]> wrote:
>
>
> Dear Charles and Artem,
>
> I've recently bought a new PowerCom Imperial IMD825-AP LCD which identifies 
> itself as 0x0d9f:0x0004.
> At first glance it seems that usbhid-ups driver works fine. But when I tried 
> to shutdown UPS via DelayBeforeShutdown it started double beeping every 
> couple seconds for indefinite time (the same problem described by Vincenzo 
> Colonnella here: 
> http://lists.alioth.debian.org/pipermail/nut-upsdev/2013-February/006403.html).
>
> I suppose that recent protocol change affects a protocol specifications for 
> DelayBeforeShutdown and powercom_shutdown_info methods should be modified to 
> support 0x0004 devices. But unfortunately the protocol specifications 
> attached by Alexey Morozov didn't clarify much for me.
> My assumption here that PowerCom developers made a new devices with ID 
> 0x0d9f:0x0004 more compatible with USB HID PDC and therefore we do not need 
> any specific conversions for passed values anymore.
>
> Sigh, I wish the vendors wouldn't change operation without changing 
> identifiers.
>
> Do you have any recommendations on how the driver should decide whether it is 
> an old 0x0004 or new 0x0004 device?
>
> Here is an older Powercom device with productId 00a2 - how does your output 
> of 'upsc' compare?
>
>
>
> Best Regards,
> Maskym Bodaniuk
>
>
> --
> Charles Lepple
> clepple@gmail
>
>
>
>
   0.000000	debug level is '3'
   0.001321	upsdrv_initups...
   0.121217	Checking device (1D6B/0001) (005/001)
   0.121383	- VendorID: 1d6b
   0.121414	- ProductID: 0001
   0.121440	- Manufacturer: Linux 3.2.0-4-686-pae uhci_hcd
   0.121465	- Product: UHCI Host Controller
   0.121491	- Serial Number: 0000:00:1d.3
   0.121515	- Bus: 005
   0.121540	Trying to match device
   0.121587	Device does not match - skipping
   0.121626	Checking device (1D6B/0001) (004/001)
   0.121703	- VendorID: 1d6b
   0.121731	- ProductID: 0001
   0.121756	- Manufacturer: Linux 3.2.0-4-686-pae uhci_hcd
   0.121781	- Product: UHCI Host Controller
   0.121808	- Serial Number: 0000:00:1d.2
   0.121833	- Bus: 004
   0.121857	Trying to match device
   0.121884	Device does not match - skipping
   0.121917	Checking device (0D9F/0004) (003/004)
   0.162810	- VendorID: 0d9f
   0.162872	- ProductID: 0004
   0.162899	- Manufacturer: POWERCOM Co.,LTD
   0.162925	- Product: HID UPS Battery
   0.162954	- Serial Number: 004-0D9F-000
   0.162993	- Bus: 003
   0.163020	Trying to match device
   0.163060	disabling unconventional convertion for DelayBeforeShutdown
   0.163096	Device matches
   0.170842	HID descriptor, method 1: (9 bytes) => 09 21 00 01 00 01 22 c6 03
   0.170909	HID descriptor, method 2: (9 bytes) => 09 21 00 01 00 01 22 c6 03
   0.170937	HID descriptor length 966
   0.294835	Report Descriptor size = 966
   0.294921	Report Descriptor: (966 bytes) => 05 84 09 04 a1 01 09 24 a1 02 85 01 09 fe
   0.294968	 79 01 75 08 95 01 15 00 26 ff 00 b1 22 85 02 09 ff 79 02 b1 22 05 85 85 05
   0.295013	 09 89 79 04 b1 22 85 07 09 8b b1 22 85 08 09 2c 25 03 b1 22 85 09 09 83 25
   0.295056	 64 b1 22 09 67 b1 22 85 0e 09 66 81 22 09 66 b1 a2 85 0b 09 8c b1 22 85 0c
   0.295100	 09 29 b1 a2 85 0d 09 85 75 10 27 ff ff 00 00 b1 a2 85 37 09 68 81 22 09 68
   0.295143	 b1 a2 05 84 85 0f 09 57 75 10 16 00 00 27 ff ff 00 00 b1 a2 85 10 09 56 75
   0.295187	 20 16 00 00 27 9f 86 01 00 b1 a2 85 11 09 40 75 10 16 64 00 26 f0 00 b1 22
   0.295230	 85 12 09 30 75 10 16 00 00 26 40 01 b1 a2 85 2c 09 36 75 08 25 5a b1 a2 85
   0.295274	 13 09 5a 75 08 15 00 25 03 b1 a2 09 02 a1 02 05 85 85 0a 09 44 75 01 15 00
   0.295318	 25 01 81 a2 09 44 b1 a2 09 45 81 a2 09 45 b1 a2 09 d0 81 a2 09 d0 b1 a2 09
   0.295361	 d1 81 a2 09 d1 b1 a2 09 42 81 a2 09 42 b1 a2 09 43 81 a2 09 43 b1 a2 09 4b
   0.295404	 81 a2 09 4b b1 a2 09 db 81 a2 09 db b1 a2 05 84 09 68 81 a2 09 68 b1 a2 09
   0.295456	 69 81 a2 09 69 b1 a2 09 73 81 a2 09 73 b1 a2 09 65 81 a2 09 65 b1 a2 95 03
   0.295524	 81 01 b1 01 95 01 06 86 ff 09 80 81 a2 09 80 b1 a2 c0 c0 05 84 09 12 a1 00
   0.295573	 85 15 09 58 75 08 25 66 b1 a2 85 16 09 70 75 08 25 03 b1 a2 05 85 85 17 09
   0.295617	 85 75 10 27 ff ff 00 00 b1 a2 85 18 09 66 75 08 15 00 25 64 b1 a2 05 84 85
   0.295660	 19 09 40 75 10 16 00 0c 26 00 30 b1 22 85 1a 09 30 75 10 16 00 09 26 00 24
   0.295704	 b1 a2 85 1b 09 56 75 20 16 00 00 27 9f 86 01 00 b1 a2 85 2d 09 36 75 08 25
   0.295747	 5a b1 a2 c0 05 84 09 1a a1 00 85 1c 09 40 75 10 16 64 00 26 f0 00 b1 22 85
   0.295791	 1d 09 30 75 10 16 00 00 26 40 01 b1 a2 85 2e 09 30 75 10 16 00 00 26 40 01
   0.295834	 b1 a2 85 1e 09 32 75 08 15 00 25 46 b1 a2 c0 05 84 09 1c a1 00 85 2f 09 41
   0.295878	 75 08 15 01 25 0c b1 22 85 1f 09 35 75 08 15 00 25 64 b1 a2 85 20 09 40 75
   0.295921	 10 16 64 00 26 f0 00 b1 22 85 21 09 30 75 10 16 00 00 26 40 01 b1 a2 85 30
   0.295964	 09 42 75 08 15 32 25 3c b1 22 85 22 09 32 75 08 15 00 25 46 b1 a2 85 23 09
   0.296008	 57 75 08 15 00 25 12 b1 a2 85 24 09 56 75 20 16 00 00 27 9f 86 01 00 b1 a2
   0.296051	 c0 05 84 85 06 09 01 79 05 b1 a2 85 25 09 5a 75 08 15 00 25 03 b1 a2 09 02
   0.296095	 a1 02 05 85 85 26 09 44 75 01 15 00 25 01 b1 a2 09 45 b1 a2 09 d0 b1 a2 09
   0.296138	 d1 b1 a2 09 42 b1 a2 09 43 b1 a2 09 4b b1 a2 09 db b1 a2 05 84 09 68 b1 a2
   0.296182	 09 69 b1 a2 09 73 b1 a2 09 65 b1 a2 09 6e b1 a2 09 6f b1 a2 09 71 b1 a2 06
   0.296225	 86 ff 09 80 b1 a2 c0 85 27 05 84 09 69 75 08 15 00 25 01 b1 a2 09 1e a1 00
   0.296269	 85 a0 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 a1 09 01 75 08 95 07 15 00
   0.296350	 26 ff 00 b1 03 85 a2 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 a3 09 01 75
   0.296395	 08 95 07 15 00 26 ff 00 b1 03 85 a4 09 01 75 08 95 07 15 00 26 ff 00 b1 03
   0.296439	 85 a5 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 a6 09 01 75 08 95 07 15 00
   0.296483	 26 ff 00 b1 03 85 a7 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 a8 09 01 75
   0.296528	 08 95 07 15 00 26 ff 00 b1 03 85 a9 09 01 75 08 95 07 15 00 26 ff 00 b1 03
   0.296572	 85 aa 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 ab 09 01 75 08 95 07 15 00
   0.296616	 26 ff 00 b1 03 85 ac 09 01 75 08 95 07 15 00 26 ff 00 b1 03 85 ad 09 01 75
   0.296660	 08 95 07 15 00 26 ff 00 b1 03 85 ae 09 01 75 08 95 07 15 00 26 ff 00 b1 03
   0.296688	 c0 c0
   0.296972	disabling unconventional convertion for DelayBeforeShutdown
   0.297016	Using subdriver: PowerCOM HID 0.3
   0.301810	Report[get]: (2 bytes) => 01 01
   0.301853	Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
   0.306820	Report[get]: (2 bytes) => 02 02
   0.306892	Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 2
   0.311812	Report[get]: (2 bytes) => 05 04
   0.311881	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x05, Offset: 0, Size: 8, Value: 4
   0.316822	Report[get]: (2 bytes) => 07 01
   0.316926	Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 1
   0.321810	Report[get]: (2 bytes) => 08 02
   0.321863	Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 2
   0.326825	Report[get]: (3 bytes) => 09 64 64
   0.326906	Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x09, Offset: 0, Size: 8, Value: 100
   0.326938	Report[buf]: (3 bytes) => 09 64 64
   0.326975	Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x09, Offset: 8, Size: 8, Value: 100
   0.331821	Report[get]: (2 bytes) => 0e 64
   0.331919	Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
   0.331952	Report[buf]: (2 bytes) => 0e 64
   0.331989	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
   0.336811	Report[get]: (2 bytes) => 0b 1e
   0.336910	Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 30
   0.341807	Report[get]: (2 bytes) => 0c 0a
   0.341853	Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 10
   0.346821	Report[get]: (3 bytes) => 0d 94 3d
   0.346892	Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 16, Value: 15764
   0.351816	Report[get]: (3 bytes) => 37 20 03
   0.351876	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x37, Offset: 0, Size: 16, Value: 800
   0.351907	Report[buf]: (3 bytes) => 37 20 03
   0.351944	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x37, Offset: 0, Size: 16, Value: 800
   0.356814	Report[get]: (3 bytes) => 0f 00 00
   0.356896	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.361823	refresh_report_buffer: expected 5 bytes, but got 3 instead
   0.361893	Report[err]: (3 bytes) => 10 00 00
   0.361951	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x10, Offset: 0, Size: 32, Value: 0
   0.366816	refresh_report_buffer: expected 3 bytes, but got 2 instead
   0.366873	Report[err]: (2 bytes) => 11 dc
   0.366915	Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x11, Offset: 0, Size: 16, Value: 220
   0.371810	Report[get]: (3 bytes) => 12 d2 00
   0.371861	Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 16, Value: 210
   0.376837	libusb_get_report: No error
   0.376982	Can't retrieve Report 2c: Inappropriate ioctl for device
   0.377037	Path: UPS.PowerSummary.Temperature, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8
   0.381820	Report[get]: (2 bytes) => 13 01
   0.381921	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
   0.386831	Report[get]: (3 bytes) => 0a 0c 00
   0.386902	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x0a, Offset: 0, Size: 1, Value: 0
   0.386934	Report[buf]: (3 bytes) => 0a 0c 00
   0.386972	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 1, Value: 0
   0.387003	Report[buf]: (3 bytes) => 0a 0c 00
   0.387039	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x0a, Offset: 1, Size: 1, Value: 0
   0.387069	Report[buf]: (3 bytes) => 0a 0c 00
   0.387105	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x0a, Offset: 1, Size: 1, Value: 0
   0.387144	Report[buf]: (3 bytes) => 0a 0c 00
   0.387251	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x0a, Offset: 2, Size: 1, Value: 1
   0.387303	Report[buf]: (3 bytes) => 0a 0c 00
   0.387395	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0a, Offset: 2, Size: 1, Value: 1
   0.387445	Report[buf]: (3 bytes) => 0a 0c 00
   0.387499	Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, ReportID: 0x0a, Offset: 3, Size: 1, Value: 1
   0.387545	Report[buf]: (3 bytes) => 0a 0c 00
   0.387596	Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x0a, Offset: 3, Size: 1, Value: 1
   0.387637	Report[buf]: (3 bytes) => 0a 0c 00
   0.387704	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x0a, Offset: 4, Size: 1, Value: 0
   0.387734	Report[buf]: (3 bytes) => 0a 0c 00
   0.387770	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x0a, Offset: 4, Size: 1, Value: 0
   0.387802	Report[buf]: (3 bytes) => 0a 0c 00
   0.387842	Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, ReportID: 0x0a, Offset: 5, Size: 1, Value: 0
   0.387917	Report[buf]: (3 bytes) => 0a 0c 00
   0.387955	Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x0a, Offset: 5, Size: 1, Value: 0
   0.387987	Report[buf]: (3 bytes) => 0a 0c 00
   0.388023	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x0a, Offset: 6, Size: 1, Value: 0
   0.388053	Report[buf]: (3 bytes) => 0a 0c 00
   0.388089	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x0a, Offset: 6, Size: 1, Value: 0
   0.388120	Report[buf]: (3 bytes) => 0a 0c 00
   0.388157	Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input, ReportID: 0x0a, Offset: 7, Size: 1, Value: 0
   0.388187	Report[buf]: (3 bytes) => 0a 0c 00
   0.388223	Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Feature, ReportID: 0x0a, Offset: 7, Size: 1, Value: 0
   0.388254	Report[buf]: (3 bytes) => 0a 0c 00
   0.388290	Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Input, ReportID: 0x0a, Offset: 8, Size: 1, Value: 0
   0.388320	Report[buf]: (3 bytes) => 0a 0c 00
   0.388356	Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Feature, ReportID: 0x0a, Offset: 8, Size: 1, Value: 0
   0.388387	Report[buf]: (3 bytes) => 0a 0c 00
   0.388423	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x0a, Offset: 9, Size: 1, Value: 0
   0.388453	Report[buf]: (3 bytes) => 0a 0c 00
   0.388492	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x0a, Offset: 9, Size: 1, Value: 0
   0.388541	Report[buf]: (3 bytes) => 0a 0c 00
   0.388580	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x0a, Offset: 10, Size: 1, Value: 0
   0.388610	Report[buf]: (3 bytes) => 0a 0c 00
   0.388647	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x0a, Offset: 10, Size: 1, Value: 0
   0.388688	Report[buf]: (3 bytes) => 0a 0c 00
   0.388748	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x0a, Offset: 11, Size: 1, Value: 0
   0.388901	Report[buf]: (3 bytes) => 0a 0c 00
   0.388975	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x0a, Offset: 11, Size: 1, Value: 0
   0.389007	Report[buf]: (3 bytes) => 0a 0c 00
   0.389043	Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: Input, ReportID: 0x0a, Offset: 15, Size: 1, Value: 0
   0.389073	Report[buf]: (3 bytes) => 0a 0c 00
   0.389109	Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: Feature, ReportID: 0x0a, Offset: 15, Size: 1, Value: 0
   0.393817	Report[get]: (2 bytes) => 15 01
   0.393887	Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, Offset: 0, Size: 8, Value: 1
   0.398817	Report[get]: (2 bytes) => 16 0d
   0.398887	Path: UPS.Battery.Initialized, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 1
   0.403798	Report[get]: (3 bytes) => 17 94 3d
   0.403846	Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 15764
   0.408802	Report[get]: (2 bytes) => 18 64
   0.408881	Path: UPS.Battery.RemainingCapacity, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 100
   0.413814	refresh_report_buffer: expected 3 bytes, but got 2 instead
   0.413871	Report[err]: (2 bytes) => 19 dc
   0.413912	Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 3072
   0.418802	Report[get]: (3 bytes) => 1a d2 00
   0.418858	Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x1a, Offset: 0, Size: 16, Value: 8402
   0.423804	refresh_report_buffer: expected 5 bytes, but got 3 instead
   0.423859	Report[err]: (3 bytes) => 1b 00 00
   0.423899	Path: UPS.Battery.DelayBeforeStartup, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 32, Value: 0
   0.428799	libusb_get_report: No error
   0.428880	Can't retrieve Report 2d: Inappropriate ioctl for device
   0.428917	Path: UPS.Battery.Temperature, Type: Feature, ReportID: 0x2d, Offset: 0, Size: 8
   0.433817	refresh_report_buffer: expected 3 bytes, but got 2 instead
   0.433881	Report[err]: (2 bytes) => 1c dc
   0.433923	Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 220
   0.438810	Report[get]: (3 bytes) => 1d d2 00
   0.438880	Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, Offset: 0, Size: 16, Value: 210
   0.443797	libusb_get_report: No error
   0.443845	Can't retrieve Report 2e: Inappropriate ioctl for device
   0.443879	Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x2e, Offset: 0, Size: 16
   0.448813	Report[get]: (2 bytes) => 1e 32
   0.448906	Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, Offset: 0, Size: 8, Value: 50
   0.453811	libusb_get_report: No error
   0.453880	Can't retrieve Report 2f: Inappropriate ioctl for device
   0.453915	Path: UPS.Output.ConfigCurrent, Type: Feature, ReportID: 0x2f, Offset: 0, Size: 8
   0.458823	Report[get]: (2 bytes) => 1f 00
   0.458900	Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 0
   0.463825	refresh_report_buffer: expected 3 bytes, but got 2 instead
   0.463890	Report[err]: (2 bytes) => 20 dc
   0.463934	Path: UPS.Output.ConfigVoltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 220
   0.468816	Report[get]: (3 bytes) => 21 d2 00
   0.468911	Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, Offset: 0, Size: 16, Value: 210
   0.473796	libusb_get_report: No error
   0.473842	Can't retrieve Report 30: Inappropriate ioctl for device
   0.473876	Path: UPS.Output.ConfigFrequency, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8
   0.478822	Report[get]: (2 bytes) => 22 32
   0.478900	Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 50
   0.481827	libusb_get_report: error sending control message: Value too large for defined data type
   0.481877	Can't retrieve Report 23: Value too large for defined data type
   0.481911	Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 0x23, Offset: 0, Size: 8
   0.487812	refresh_report_buffer: expected 5 bytes, but got 3 instead
   0.487862	Report[err]: (3 bytes) => 24 00 00
   0.487948	Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID: 0x24, Offset: 0, Size: 32, Value: 0
   0.492809	refresh_report_buffer: expected 5 bytes, but got 2 instead
   0.492876	Report[err]: (2 bytes) => 06 05
   0.492915	Path: UPS.iName, Type: Feature, ReportID: 0x06, Offset: 0, Size: 32, Value: 5
   0.497820	Report[get]: (2 bytes) => 25 01
   0.497887	Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 0x25, Offset: 0, Size: 8, Value: 1
   0.502808	Report[get]: (3 bytes) => 26 0c 00
   0.502859	Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 0x26, Offset: 0, Size: 1, Value: 0
   0.502890	Report[buf]: (3 bytes) => 26 0c 00
   0.502925	Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID: 0x26, Offset: 1, Size: 1, Value: 0
   0.502955	Report[buf]: (3 bytes) => 26 0c 00
   0.502990	Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 0x26, Offset: 2, Size: 1, Value: 1
   0.503020	Report[buf]: (3 bytes) => 26 0c 00
   0.503055	Path: UPS.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x26, Offset: 3, Size: 1, Value: 1
   0.503086	Report[buf]: (3 bytes) => 26 0c 00
   0.503120	Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
   0.503150	Report[buf]: (3 bytes) => 26 0c 00
   0.503185	Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
   0.503215	Report[buf]: (3 bytes) => 26 0c 00
   0.503250	Path: UPS.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x26, Offset: 6, Size: 1, Value: 0
   0.503280	Report[buf]: (3 bytes) => 26 0c 00
   0.503314	Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, ReportID: 0x26, Offset: 7, Size: 1, Value: 0
   0.503344	Report[buf]: (3 bytes) => 26 0c 00
   0.503379	Path: UPS.PresentStatus.ShutdownRequested, Type: Feature, ReportID: 0x26, Offset: 8, Size: 1, Value: 0
   0.503409	Report[buf]: (3 bytes) => 26 0c 00
   0.503443	Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x26, Offset: 9, Size: 1, Value: 0
   0.503473	Report[buf]: (3 bytes) => 26 0c 00
   0.503508	Path: UPS.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x26, Offset: 10, Size: 1, Value: 0
   0.503538	Report[buf]: (3 bytes) => 26 0c 00
   0.503572	Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 0x26, Offset: 11, Size: 1, Value: 0
   0.503604	Report[buf]: (3 bytes) => 26 0c 00
   0.503652	Path: UPS.PresentStatus.Boost, Type: Feature, ReportID: 0x26, Offset: 12, Size: 1, Value: 0
   0.503690	Report[buf]: (3 bytes) => 26 0c 00
   0.503725	Path: UPS.PresentStatus.Buck, Type: Feature, ReportID: 0x26, Offset: 13, Size: 1, Value: 0
   0.503755	Report[buf]: (3 bytes) => 26 0c 00
   0.503790	Path: UPS.PresentStatus.Tested, Type: Feature, ReportID: 0x26, Offset: 14, Size: 1, Value: 0
   0.503820	Report[buf]: (3 bytes) => 26 0c 00
   0.503856	Path: UPS.PresentStatus.POWERCOM3, Type: Feature, ReportID: 0x26, Offset: 15, Size: 1, Value: 0
   0.508823	Report[get]: (2 bytes) => 27 00
   0.508914	Path: UPS.ShutdownImminent, Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 0
   0.513824	Report[get]: (8 bytes) => a0 10 00 64 69 69 32 ff
   0.513892	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa0, Offset: 0, Size: 8, Value: 16
   0.518817	Report[get]: (8 bytes) => a1 32 00 00 00 00 4b 48
   0.518876	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa1, Offset: 0, Size: 8, Value: 50
   0.523823	Report[get]: (8 bytes) => a2 00 00 00 ce 65 4a 12
   0.523880	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa2, Offset: 0, Size: 8, Value: 0
   0.528813	Report[get]: (8 bytes) => a3 40 3f b3 48 df 80 34
   0.528899	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa3, Offset: 0, Size: 8, Value: 64
   0.533834	Report[get]: (8 bytes) => a4 00 d9 85 c3 40 25 d6
   0.533913	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa4, Offset: 0, Size: 8, Value: 0
   0.538814	Report[get]: (8 bytes) => a5 09 50 8c 8a 83 ab cf
   0.538880	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa5, Offset: 0, Size: 8, Value: 9
   0.543809	Report[get]: (8 bytes) => a6 03 86 86 60 82 59 48
   0.543888	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa6, Offset: 0, Size: 8, Value: 3
   0.548817	Report[get]: (8 bytes) => a7 6c 65 67 ca e3 0f 34
   0.548897	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa7, Offset: 0, Size: 8, Value: 108
   0.553823	Report[get]: (8 bytes) => a8 c0 7c 93 cb 26 6e 01
   0.553892	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa8, Offset: 0, Size: 8, Value: 192
   0.558805	Report[get]: (8 bytes) => a9 04 52 af 2f 03 c9 8a
   0.558849	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xa9, Offset: 0, Size: 8, Value: 4
   0.563829	Report[get]: (8 bytes) => aa 28 18 fb ed 01 00 42
   0.563902	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xaa, Offset: 0, Size: 8, Value: 40
   0.568809	Report[get]: (8 bytes) => ab f8 00 e3 46 14 ab 11
   0.568876	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xab, Offset: 0, Size: 8, Value: 248
   0.573809	Report[get]: (8 bytes) => ac 0b 00 9d 15 f0 f5 01
   0.573865	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xac, Offset: 0, Size: 8, Value: 11
   0.578826	Report[get]: (8 bytes) => ad 82 40 df 90 ee 58 42
   0.578894	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xad, Offset: 0, Size: 8, Value: 130
   0.583815	refresh_report_buffer: expected 8 bytes, but got 2 instead
   0.583871	Report[err]: (2 bytes) => ae 00
   0.583915	Path: UPS.Flow.iName, Type: Feature, ReportID: 0xae, Offset: 0, Size: 8, Value: 0
Network UPS Tools - Generic HID driver 0.37 (2.6.4)
USB communication driver 0.32
   0.584023	Report descriptor retrieved (Reportlen = 966)
   0.584061	Found HID device
   0.584094	Detected a UPS: POWERCOM Co.,LTD/HID UPS Battery
   0.584247	Report[buf]: (3 bytes) => 0a 0c 00
   0.584286	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x0a, Offset: 2, Size: 1, Value: 1
   0.584332	Report[buf]: (3 bytes) => 0a 0c 00
   0.584364	Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x0a, Offset: 3, Size: 1, Value: 1
   0.584408	Report[buf]: (3 bytes) => 0a 0c 00
   0.584439	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x0a, Offset: 4, Size: 1, Value: 0
   0.584481	Report[buf]: (3 bytes) => 0a 0c 00
   0.584513	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 1, Value: 0
   0.584553	Report[buf]: (3 bytes) => 0a 0c 00
   0.584585	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x0a, Offset: 10, Size: 1, Value: 0
   0.584627	Report[buf]: (3 bytes) => 0a 0c 00
   0.584658	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x0a, Offset: 1, Size: 1, Value: 0
   0.584700	Report[buf]: (3 bytes) => 0a 0c 00
   0.584732	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x0a, Offset: 6, Size: 1, Value: 0
   0.584813	Report[buf]: (3 bytes) => 0a 0c 00
   0.584883	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x0a, Offset: 11, Size: 1, Value: 0
   0.584930	Report[buf]: (3 bytes) => 0a 0c 00
   0.584962	Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x0a, Offset: 5, Size: 1, Value: 0
   0.585005	Report[buf]: (3 bytes) => 0a 0c 00
   0.585040	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x0a, Offset: 9, Size: 1, Value: 0
   0.585084	Report[buf]: (3 bytes) => 26 0c 00
   0.585116	Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 0x26, Offset: 2, Size: 1, Value: 1
   0.585159	Report[buf]: (3 bytes) => 26 0c 00
   0.585191	Path: UPS.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x26, Offset: 3, Size: 1, Value: 1
   0.585233	Report[buf]: (3 bytes) => 26 0c 00
   0.585265	Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
   0.585304	Report[buf]: (3 bytes) => 26 0c 00
   0.585336	Path: UPS.PresentStatus.Boost, Type: Feature, ReportID: 0x26, Offset: 12, Size: 1, Value: 0
   0.585375	Report[buf]: (3 bytes) => 26 0c 00
   0.585440	Path: UPS.PresentStatus.Buck, Type: Feature, ReportID: 0x26, Offset: 13, Size: 1, Value: 0
   0.585483	Report[buf]: (3 bytes) => 26 0c 00
   0.585514	Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 0x26, Offset: 0, Size: 1, Value: 0
   0.585554	Report[buf]: (3 bytes) => 26 0c 00
   0.585586	Path: UPS.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x26, Offset: 10, Size: 1, Value: 0
   0.585627	Report[buf]: (3 bytes) => 26 0c 00
   0.585659	Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID: 0x26, Offset: 1, Size: 1, Value: 0
   0.585700	Report[buf]: (3 bytes) => 26 0c 00
   0.585732	Path: UPS.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x26, Offset: 6, Size: 1, Value: 0
   0.585808	Report[buf]: (3 bytes) => 26 0c 00
   0.585844	Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 0x26, Offset: 11, Size: 1, Value: 0
   0.585886	Report[buf]: (3 bytes) => 26 0c 00
   0.585918	Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
   0.585957	Report[buf]: (3 bytes) => 26 0c 00
   0.585989	Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x26, Offset: 9, Size: 1, Value: 0
   0.586031	Report[buf]: (2 bytes) => 0e 64
   0.586064	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
   0.586155	Report[buf]: (3 bytes) => 37 20 03
   0.586189	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x37, Offset: 0, Size: 16, Value: 800
   0.586239	Report[buf]: (3 bytes) => 17 94 3d
   0.586272	Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 15764
   0.586322	Report[buf]: (2 bytes) => 05 04
   0.586354	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x05, Offset: 0, Size: 8, Value: 4
   0.596879	Report[buf]: (2 bytes) => 13 01
   0.596945	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
   0.596997	Report[buf]: (2 bytes) => 1f 00
   0.597030	Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 0x1f, Offset: 0, Size: 8, Value: 0
   0.597081	Report[buf]: (3 bytes) => 0d 94 3d
   0.597115	Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 16, Value: 15764
   0.597161	Report[buf]: (2 bytes) => 15 01
   0.597193	Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, Offset: 0, Size: 8, Value: 1
   0.597256	Report[buf]: (5 bytes) => 10 00 00 00 00
   0.597289	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x10, Offset: 0, Size: 32, Value: 0
   0.597319	powercom_startup_fun: value = 0, buf = 0
   0.597382	Report[buf]: (3 bytes) => 0f 00 00
   0.597428	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.597460	powercom_shutdown_fun: value = 0, buf = 0
   0.597504	Report[buf]: (3 bytes) => 1d d2 00
   0.597538	Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, Offset: 0, Size: 16, Value: 210
   0.597598	Report[buf]: (3 bytes) => 1c dc 00
   0.597632	Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 220
   0.597694	Report[buf]: (2 bytes) => 1e 32
   0.597728	Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, Offset: 0, Size: 8, Value: 50
   0.597774	Report[buf]: (3 bytes) => 21 d2 00
   0.597807	Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, Offset: 0, Size: 16, Value: 210
   0.597854	Report[buf]: (3 bytes) => 20 dc 00
   0.597887	Path: UPS.Output.ConfigVoltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 220
   0.597933	Report[buf]: (2 bytes) => 22 32
   0.597965	Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 50
   0.598012	Report[buf]: (2 bytes) => 13 01
   0.598043	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1
   0.598083	Report[buf]: (2 bytes) => 15 01
   0.598115	Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, Offset: 0, Size: 8, Value: 1
   0.598273	Report[buf]: (5 bytes) => 10 00 00 00 00
   0.598308	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x10, Offset: 0, Size: 32, Value: 0
   0.598349	Report[buf]: (3 bytes) => 0f 00 00
   0.598381	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.598422	Report[buf]: (3 bytes) => 0f 00 00
   0.598492	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.598551	find_nut_info: unknown info type: load.off.delay
   0.598586	find_nut_info: unknown info type: load.off.delay
   0.598638	upsdrv_initinfo...
   0.598680	upsdrv_updateinfo...
   0.695834	Report[int]: (3 bytes) => 0a 0c 00
   0.695895	Got 13 HID objects...
   0.695928	Report[buf]: (3 bytes) => 0a 0c 00
   0.695967	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x0a, Offset: 0, Size: 1, Value: 0
   0.696001	Report[buf]: (3 bytes) => 0a 0c 00
   0.696038	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x0a, Offset: 1, Size: 1, Value: 0
   0.696070	Report[buf]: (3 bytes) => 0a 0c 00
   0.696107	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x0a, Offset: 2, Size: 1, Value: 1
   0.696138	Report[buf]: (3 bytes) => 0a 0c 00
   0.696175	Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, ReportID: 0x0a, Offset: 3, Size: 1, Value: 1
   0.696209	Report[buf]: (3 bytes) => 0a 0c 00
   0.696246	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x0a, Offset: 4, Size: 1, Value: 0
   0.696278	Report[buf]: (3 bytes) => 0a 0c 00
   0.696317	Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, ReportID: 0x0a, Offset: 5, Size: 1, Value: 0
   0.696366	Report[buf]: (3 bytes) => 0a 0c 00
   0.696404	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x0a, Offset: 6, Size: 1, Value: 0
   0.696437	Report[buf]: (3 bytes) => 0a 0c 00
   0.696473	Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input, ReportID: 0x0a, Offset: 7, Size: 1, Value: 0
   0.696501	NUT doesn't use this HID object
   0.696532	Report[buf]: (3 bytes) => 0a 0c 00
   0.696567	Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Input, ReportID: 0x0a, Offset: 8, Size: 1, Value: 0
   0.696594	NUT doesn't use this HID object
   0.696625	Report[buf]: (3 bytes) => 0a 0c 00
   0.696660	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x0a, Offset: 9, Size: 1, Value: 0
   0.696693	Report[buf]: (3 bytes) => 0a 0c 00
   0.696729	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x0a, Offset: 10, Size: 1, Value: 0
   0.696762	Report[buf]: (3 bytes) => 0a 0c 00
   0.696798	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x0a, Offset: 11, Size: 1, Value: 0
   0.696830	Report[buf]: (3 bytes) => 0a 0c 00
   0.696959	Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: Input, ReportID: 0x0a, Offset: 15, Size: 1, Value: 0
   0.696988	NUT doesn't use this HID object
   0.697016	Quick update...
   0.697048	Report[buf]: (3 bytes) => 0f 00 00
   0.697079	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.697108	powercom_shutdown_fun: value = 0, buf = 0
   0.697154	using 'battery.charge' to set battery low state
   0.697287	dstate_init: sock /var/run/nut/usbhid-ups-powercom open on fd 5
   0.697341	upsdrv_updateinfo...
   0.887828	Report[int]: (2 bytes) => 0e 64
   0.887889	Got 1 HID objects...
   0.887921	Report[buf]: (2 bytes) => 0e 64
   0.887961	Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
   0.887997	Quick update...
   0.888028	Report[buf]: (3 bytes) => 0f 00 00
   0.888060	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   0.888089	powercom_shutdown_fun: value = 0, buf = 0
   2.699190	upsdrv_updateinfo...
   2.871816	file_report_buffer: expected 0 bytes, but got 2 instead
   2.871920	Report[err]: (2 bytes) => 14 01
   2.871961	HIDGetEvents: unexpected input report (ignored)
   2.872001	Got 0 HID objects...
   2.872031	Quick update...
   2.876786	Report[get]: (3 bytes) => 0f 00 00
   2.876829	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   2.876889	powercom_shutdown_fun: value = 0, buf = 0
   4.701051	upsdrv_updateinfo...
   4.855815	Report[int]: (3 bytes) => 37 20 03
   4.855878	Got 1 HID objects...
   4.855911	Report[buf]: (3 bytes) => 37 20 03
   4.855951	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x37, Offset: 0, Size: 16, Value: 800
   4.855988	Quick update...
   4.860775	Report[get]: (3 bytes) => 0f 00 00
   4.860835	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   4.860902	powercom_shutdown_fun: value = 0, buf = 0
   6.702920	upsdrv_updateinfo...
   6.954778	libusb_get_interrupt: Connection timed out
   6.954861	Got 0 HID objects...
   6.954902	Quick update...
   6.959836	Report[get]: (3 bytes) => 0f 00 00
   6.959946	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   6.959987	powercom_shutdown_fun: value = 0, buf = 0
   8.704630	upsdrv_updateinfo...
   8.957753	libusb_get_interrupt: Connection timed out
   8.957820	Got 0 HID objects...
   8.957852	Quick update...
   8.962746	Report[get]: (3 bytes) => 0f 00 00
   8.962801	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
   8.962833	powercom_shutdown_fun: value = 0, buf = 0
  10.706401	upsdrv_updateinfo...
  10.958743	libusb_get_interrupt: Connection timed out
  10.958812	Got 0 HID objects...
  10.958843	Quick update...
  10.963739	Report[get]: (3 bytes) => 0f 00 00
  10.963807	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
  10.963840	powercom_shutdown_fun: value = 0, buf = 0
  12.708173	upsdrv_updateinfo...
  13.391725	libusb_get_interrupt: Connection timed out
  13.391793	Got 0 HID objects...
  13.391824	Quick update...
  13.396711	Report[get]: (3 bytes) => 0f 00 00
  13.396760	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
  13.396802	powercom_shutdown_fun: value = 0, buf = 0
  14.709517	upsdrv_updateinfo...
  14.775725	Report[int]: (3 bytes) => 0a 0c 00
  14.775792	Got 13 HID objects...
  14.775826	Report[buf]: (3 bytes) => 0a 0c 00
  14.775867	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x0a, Offset: 0, Size: 1, Value: 0
  14.775903	Report[buf]: (3 bytes) => 0a 0c 00
  14.775941	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x0a, Offset: 1, Size: 1, Value: 0
  14.775974	Report[buf]: (3 bytes) => 0a 0c 00
  14.776012	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x0a, Offset: 2, Size: 1, Value: 1
  14.776046	Report[buf]: (3 bytes) => 0a 0c 00
  14.776083	Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, ReportID: 0x0a, Offset: 3, Size: 1, Value: 1
  14.776118	Report[buf]: (3 bytes) => 0a 0c 00
  14.776155	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x0a, Offset: 4, Size: 1, Value: 0
  14.776189	Report[buf]: (3 bytes) => 0a 0c 00
  14.776226	Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, ReportID: 0x0a, Offset: 5, Size: 1, Value: 0
  14.776260	Report[buf]: (3 bytes) => 0a 0c 00
  14.776298	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x0a, Offset: 6, Size: 1, Value: 0
  14.776331	Report[buf]: (3 bytes) => 0a 0c 00
  14.776369	Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input, ReportID: 0x0a, Offset: 7, Size: 1, Value: 0
  14.776398	NUT doesn't use this HID object
  14.776430	Report[buf]: (3 bytes) => 0a 0c 00
  14.776467	Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type: Input, ReportID: 0x0a, Offset: 8, Size: 1, Value: 0
  14.776545	NUT doesn't use this HID object
  14.776581	Report[buf]: (3 bytes) => 0a 0c 00
  14.776622	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x0a, Offset: 9, Size: 1, Value: 0
  14.776656	Report[buf]: (3 bytes) => 0a 0c 00
  14.776693	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x0a, Offset: 10, Size: 1, Value: 0
  14.776727	Report[buf]: (3 bytes) => 0a 0c 00
  14.776764	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x0a, Offset: 11, Size: 1, Value: 0
  14.776798	Report[buf]: (3 bytes) => 0a 0c 00
  14.776835	Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: Input, ReportID: 0x0a, Offset: 15, Size: 1, Value: 0
  14.776898	NUT doesn't use this HID object
  14.776928	Quick update...
  14.776961	Report[buf]: (3 bytes) => 0f 00 00
  14.776993	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
  14.777024	powercom_shutdown_fun: value = 0, buf = 0
  16.711475	upsdrv_updateinfo...
  16.887712	Report[int]: (2 bytes) => 0e 64
  16.887777	Got 1 HID objects...
  16.887811	Report[buf]: (2 bytes) => 0e 64
  16.887851	Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100
  16.887887	Quick update...
  16.892686	Report[get]: (3 bytes) => 0f 00 00
  16.892738	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0
  16.892769	powercom_shutdown_fun: value = 0, buf = 0