Yet again, sorry for the delay - I hope the UPS is still alive. >> I noticed that your UPS seems to support the 'M' command as a query of >> some sort (it replies '0'): now I'm curious as to what it does mean. >> >> It could be the 0-9 index of the user-settable voltage limits, page 19 of: >> http://www.gruberpower.com/pdf-files/Best%20Power%20Patriot%20Pro%20II%20User%20Manual.pdf >> Could you try and change it and see what happens to the 'M' reply? > > It seems to match. I can do some variac testing some other time, but the > current setting (0) corresponds to the LED pattern for the first entry in the > table. When I incremented it a few times, it increased. >
Implemented: https://github.com/zykh/nut/tree/bestups Before I merge it (well.. provided that it works..), I'd like to know a couple of things more: 1. does the load.off command ('S00R0000') work? 2. does the 'C' command (mapped as shutdown.stop and load.on) turn the load on if executed while the ups.delay.start time elapses after having fired a shutdown.return? 3. (OK, I lied - 3 things more) does the shutdown.stayoff command ('SnR0000') work? Thanks for your patience, Charles. _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev