Hi Stuart, Charles and the list,


2015-03-29 14:17 GMT+02:00 Stuart Henderson <[email protected]>:

> On 2015/03/28 20:02, Charles Lepple wrote:
> > On Mar 25, 2015, at 9:21 PM, Stuart Henderson <[email protected]>
> wrote:
> >
> > > Hi, the diff inline below adds a new subdriver for snmp-ups to support
> > > Huawei UPS, based on an observed walk from a UPS5000-E with a few bits
> > > filled in from the MIBs (copy at http://junkpile.org/HUAWEI_UPS_MIB/).
> > > Sample output from upsc follows the diff.
> >
> > Hi Stuart,
> >
> > Thanks for the patch. It builds cleanly for me, so I have no problems
> > merging it.
> >
> > The only two things that jump out at me could probably be addressed
> > with documentation. Is there a low battery alarm? If not, we should
> > probably mention somewhere that people will need to either synthesize
> > a LB status with one or both of 'override.battery.charge.low' and
> > 'override.battery.runtime.low'.
>
> I didn't notice anything that looks like a low battery alarm in the
> Huawei MIB, though it does also return a value in
> UPS-MIB::upsBatteryStatus.0
> so perhaps a LB alarm will be signalled there; I see that in mge-mib.c
> the status appears to be generated from a combination of ietf and private
> MIB but there is a comment "FIXME: the below may introduce status
> redundancy,
> that needs to be * adressed by the driver, as for usbhid-ups!" so I wasn't
> sure the best approach here.
>
> Unfortunately it isn't really possible to test low battery in my
> environment,
> I'd need to override the generator autostart/ATS which I don't think I'd
> get approval for (my main aim with this UPS is to use NUT to act as an
> abstraction layer so that it can be monitored alongside a couple of
> more "normal" UPS, rather than specifically to trigger shutdowns).
>

first comment:
it would have been great if you used the SNMP subdriver generator [1]
It creates a dump of the whole structure pointed by the sysOID, and help to
track the remaining unimplemented features...


> >                                 (Or they can shut down when it first
> > transfers to battery, but this sounds like the sort of UPS that would
> > keep going for a while.)
>
> Indeed, it is a bit larger than anything I've dealt with before, you
> may have noticed the battery V in my sample output ;-)
>
> > There also seem to be a few commands in the MIB, but none are
> > implemented here. The only ones that people might be expecting are the
> > shutdown.reboot and shutdown.stayoff, although I haven't used the SNMP
> > driver to see how well those work in general. Not strictly necessary
> > to implement, but we should probably take this opportunity to point
> > out in the snmp-ups man page that if there are no shutdown.* commands
> > listed in the upscmd output, there is a potential for a race condition
> > if the power comes back early.
>
> There's a hwUpsCtrlPowerOff command and a RW hwUpsCtrlPowerOffDelay
> variable, but the mib isn't clear about whether this would be
> "shutdown.stayoff" or "shutdown.return", I'll see if I can find more
> information about this in the manuals.
>
> I don't see a power-on delay in the vendor mib so I think shutdown.reboot
> may not be possible.
>
> There is also a battery test command, which would be a bit easier for
> me to test, I'll try and look at that sometime.
>

also, would be great if you could post (either public/private, but
compressed) or point to the MIB file, for putting on the Protocols page [2]


> > Arnaud, as maintainer of snmp-ups, any thoughts here?
>
> Thanks for the review Charles, and I'd be interested to hear any
> comments from Arnaud.
>

this version of the SNMP driver is getting too old and not flexible enough.
Keep in mind that there is a rewrite scheduled [3]
However, for now, you may want to have a look at [4]. This implementation
is not perfect, but will give you some ideas.
I still have to find a better way to link and use the commands with the
matching delays.
But it's generally a default behavior of SNMP agent (i.e. first set the
delay, then execute the command)

Thanks for your contribution,
cheers,
Arno
--
[1]
http://www.networkupstools.org/docs/developer-guide.chunked/ar01s04.html#snmp-subdrivers
https://github.com/networkupstools/nut/blob/master/scripts/subdriver/gen-snmp-subdriver.sh
[2] http://www.networkupstools.org/ups-protocols.html
[3] https://github.com/networkupstools/nut/issues/20
[4]
https://github.com/networkupstools/nut/blob/master/drivers/powerware-mib.c#L314
-- 
Eaton Data Center Automation - Opensource Leader
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to