Greg,

I'm still not 100% on what is going on, but after comparing the call stack with 
a debug session here, I think I have at least identified why I wasn't seeing 
similar behavior.

There are two ways that the driver can get information from the UPS: asking the 
UPS for a specific report (which returns one or more values), and checking the 
interrupt pipe (which the UPS can fill with whatever has changed). With the 
interrupt pipe results, the driver has to do an additional HID table lookup to 
determine exactly what is being returned.

It looks like the driver is processing the latter case when it throws that 
error. I wasn't seeing that here, apparently because my MGE UPS on FreeBSD is 
never getting anything via the interrupt pipe. (The driver falls back to the 
polling method.)

I might have some time later to reconnect that UPS to a Linux system and see if 
the error crops up there. However, I have a suspicion that the bug is triggered 
because the first entry in the Tripp Lite table has a conversion function, and 
when the table lookup fails (your UPS does not have the HID item corresponding 
to a manufacturer's part number), the lookup function incorrectly returns that 
first table entry by default.

- Charles

On Jun 10, 2015, at 12:18 PM, Greg Hersch <[email protected]> wrote:

> 
> And here are the logs and GDB output from the reconfigured/recompiled 
> CFLAGS=-G program. You will notice i made a change to the version definition 
> of tripplite-hid.c just to make sure i am working with the updated version.
> 
> On Tue, 9 Jun 2015, Charles Lepple wrote:
> 
>> On Jun 9, 2015, at 4:55 PM, Greg Hersch wrote:
>> 
>>> (gdb) bt
>>> #0  libusb_get_string (udev=0x43110, StringIdx=0, buf=0x40204 <buf>
>>> "", buflen=20) at libusb.c:496
>>> #1  0x00015330 in HIDGetIndexString (udev=<optimized out>,
>>> Index=<optimized out>, buf=0x40204 <buf> "", buflen=<optimized out>)
>>> at libhid.c:407
>>> #2  0x00012e18 in ups_infoval_set (item=0x3ee48 <tripplite_hid2nut>,
>>> value=<optimized out>) at usbhid-ups.c:1552
>>> #3  0x00013da8 in upsdrv_updateinfo () at usbhid-ups.c:835
>>> #4  0x00012410 in main (argc=<optimized out>, argv=<optimized out>) at
>>> main.c:708
>> 
>> You did everything right on the backtrace, but that is puzzling.
>> 
>> At #2, ups_infoval_set() apparently calls HIDGetIndexString(), but I don't 
>> see where it does that in the code. There must be some pointers, or 
>> something.
>> 
>> The easiest thing might be to crank the debug output up a bit more (5x -D, 
>> even) but since that will be a bit more output, please redirect it to a 
>> file, and gzip the log before attaching it. Doesn't need to be long, just 
>> enough to see one or two errors.
>> 
>> Another idea is to recompile without optimizations, to see if that helps the 
>> gdb backtrace. NUT apparently sets CFLAGS=-O if it is not set already, so 
>> adding "CFLAGS=-g" to the ./configure line should do it.
>> 
>> Arnaud, am I missing something obvious here? After making "device.part" 
>> HU_STATIC, there shouldn't be any other string descriptors retrieved in 
>> drivers/tripplite-hid.c.
>> 
>> -- 
>> Charles Lepple
>> clepple@gmail
>> 
>> 
>> 
> <typescript-GDB-withCFLAGchange.gz><typescript_LOG_withCFLAG.gz>


_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to