On Nov 21, 2015, at 2:06 PM, john hart <[email protected]> wrote:
> 
> 1.  When communications are lost, instead of shutting down immediately why 
> not set a flag and then stop the driver and then restart the driver.  If 
> communication is not re-established, and the flag was set, then shut down the 
> system.  Perhaps this is already being done.

This is not likely to be implemented any time soon. It is too dependent on 
distribution-related things, like how the driver is launched.

Our preference is to fix the driver so that it reconnects itself, but the 
maintainer of the blazer_* drivers has not worked on NUT for several years 
(hence the move to nutdrv_qx).

> 2.  In my case, when the shutdown occurs due to loss of communication, the 
> NUT software tries to turn off the UPS.  It can't do that because there is no 
> communication.  This cause the shutdown process to hang up for some period of 
> time.  In my opinion this is not good because the system may crash during 
> that period when it is hung.  The software should skip trying to shut off the 
> UPS and just execute a normal shutdown.

NUT cannot foresee every kind of communication failure, and most of the drivers 
already have timeouts built in. As a backup, the distribution startup/shutdown 
scripts should probably have timeouts as well - this used to be implemented as 
a delay between sending SIGTERM and SIGKILL.

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to