On Wed, 2018-05-09 at 14:02:43 +0000, Pilch, Alexander wrote:
> Yes both UPS units are on different power supplies. MINSUPPLIES is set to 1.
> Afaik NUT waits for OB and LB before shutting down the system. Is there a way 
> to change this behavior to only wait for OB?

set the "low" limit to 100%

> Then I would use FINALDELAY in case the power outage doesn't last long.
> 
> I already tried to change the battery.runtime.low setting over the 
> webinterface of the CS121 (snmp is readonly) but with our AEG UPS, this 
> didn't work as expected(seems like a firmware bug) and I need to work around 
> this problem.

override.battery.charge.low (in ups.conf) may help? (See also ignorelb.)

> I'm already in contact with AEG but I also have a bunch of UPS units from 
> other manufacturers to cover with the same controller card and different 
> (potentially buggy) firmware...

CS121, you say? I've seen some ugly behaviour of those.
As long as you don't plan / aren't authorized to actually shut down the UPS 
itself,
don't modify anything, neither via SNMP (it's good to have r/o access only) nor
via web interface.

Using the override, NUT can declare a LB condition on its own (hint: for testing
you may even set the percentage to 105).

HTH,
 Steffen