On Wed, 2018-05-09 at 14:02:43 +0000, Pilch, Alexander wrote: > Yes both UPS units are on different power supplies. MINSUPPLIES is set to 1. > Afaik NUT waits for OB and LB before shutting down the system. Is there a way > to change this behavior to only wait for OB?
set the "low" limit to 100% > Then I would use FINALDELAY in case the power outage doesn't last long. > > I already tried to change the battery.runtime.low setting over the > webinterface of the CS121 (snmp is readonly) but with our AEG UPS, this > didn't work as expected(seems like a firmware bug) and I need to work around > this problem. override.battery.charge.low (in ups.conf) may help? (See also ignorelb.) > I'm already in contact with AEG but I also have a bunch of UPS units from > other manufacturers to cover with the same controller card and different > (potentially buggy) firmware... CS121, you say? I've seen some ugly behaviour of those. As long as you don't plan / aren't authorized to actually shut down the UPS itself, don't modify anything, neither via SNMP (it's good to have r/o access only) nor via web interface. Using the override, NUT can declare a LB condition on its own (hint: for testing you may even set the percentage to 105). HTH, Steffen _______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser