Charles,

We saw some changes. I've included some pipes of before and after the
unplug. It smells like hex code to me in the debug area.

Thanks,
Mike

On Fri, May 25, 2018 at 4:20 PM, Michael <[email protected]> wrote:

> Charles,
>
> I followed the instructions on github, and my upsc UPSNAME command output
> did not change (I don't have any statuses for the ups.status line).
>
> The output is as follows:
>
> upsc Tripp-Lite
> Init SSL without certificate database
> battery.voltage.nominal: 48
> device.mfr: Tripp Lite
> device.model: TRIPP LITE UPS
> device.type: ups
> driver.name: tripplite_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.synchronous: no
> driver.version: 2.7.4-480-g14301bdb
> driver.version.internal: 0.29
> input.voltage.nominal: 208
> outlet.1.desc: Load 1
> outlet.1.id: 1
> outlet.1.switch: 1
> outlet.1.switchable: 1
> outlet.2.desc: Load 2
> outlet.2.id: 2
> outlet.2.switch: 1
> outlet.2.switchable: 1
> outlet.3.desc: Load 3
> outlet.3.id: 3
> outlet.3.switch: 1
> outlet.3.switchable: 1
> outlet.4.desc: Load 4
> outlet.4.id: 4
> outlet.4.switch: 1
> outlet.4.switchable: 1
> outlet.5.desc: Load 5
> outlet.5.id: 5
> outlet.5.switch: 1
> outlet.5.switchable: 1
> outlet.6.desc: Load 6
> outlet.6.id: 6
> outlet.6.switch: 1
> outlet.6.switchable: 1
> outlet.7.desc: Load 7
> outlet.7.id: 7
> outlet.7.switch: 1
> outlet.7.switchable: 1
> outlet.8.desc: Load 8
> outlet.8.id: 8
> outlet.8.switch: 1
> outlet.8.switchable: 1
> outlet.9.desc: Load 9
> outlet.9.id: 9
> outlet.9.switchable: 0
> ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
> ups.debug.D: 36 45 38 37 0d 00 00 '6E87...'
> ups.debug.L: 31 35 35 41 30 31 0d '155A01.'
> ups.debug.load_banks: 8
> ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
> ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
> ups.debug.S: 31 34 30 30 30 30 0d '140000.'
> ups.debug.T: 39 46 32 35 38 31 0d '9F2581.'
> ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
> ups.delay.shutdown: 64
> ups.firmware: F1114.A
> ups.firmware.aux: protocol 0005
> ups.id: 65535
> ups.mfr: Tripp Lite
> ups.model: TRIPP LITE UPS
> ups.power.nominal: 500
> ups.productid: 0001
> ups.status:
> ups.vendorid: 09ae
>
>
> We are going to pull the plug on the UPS, and I will run the command
> again. I'm hoping the changes in the output will be enough to reverse
> engineer this with you.
>
> Thanks,
> Mike
>
> On Fri, May 11, 2018 at 8:50 PM, Charles Lepple <[email protected]> wrote:
>
>> On May 8, 2018, at 10:05 PM, Charles Lepple <[email protected]> wrote:
>> >
>> >> I'm new to this, so let me know what you need from me and I will try
>> my best. This UPS does power our production servers, so shutting things
>> down aren't an easy task, but this weekend might open up some opportunity
>> for that if need be. If I need to test it by unplugging the main power,
>> that I can do without problems.
>> >
>> > The first thing to try is building the latest NUT code from source.
>> Version 2.7.4 is the latest released version, but after that, we'll switch
>> to a new branch to add in the features for protocol 0005. Here are some
>> instructions (not yet tested for Ubuntu 18.04):
>> >
>> > https://github.com/networkupstools/nut/wiki/Building-NUT-on-
>> Debian,-Raspbian-and-Ubuntu
>> >
>> > There is always some level of risk with testing new code on an UPS, but
>> if things didn't shut down before, you should be okay. You can try building
>> this week, but I'd still wait until the weekend to test the new driver.
>> >
>> If you have a chance to build the master branch to test, you can also try
>> the tripplite_0005 branch. I need to dig out the OMNIVS1000 for regression
>> testing, and of course I don't have a SU5000 to test with, but it should
>> work based on the debug information you provided.
>
>
>
battery.voltage.nominal: 48
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4-480-g14301bdb
driver.version.internal: 0.29
input.voltage.nominal: 208
outlet.1.desc: Load 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.desc: Load 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
outlet.3.desc: Load 3
outlet.3.id: 3
outlet.3.switch: 1
outlet.3.switchable: 1
outlet.4.desc: Load 4
outlet.4.id: 4
outlet.4.switch: 1
outlet.4.switchable: 1
outlet.5.desc: Load 5
outlet.5.id: 5
outlet.5.switch: 1
outlet.5.switchable: 1
outlet.6.desc: Load 6
outlet.6.id: 6
outlet.6.switch: 1
outlet.6.switchable: 1
outlet.7.desc: Load 7
outlet.7.id: 7
outlet.7.switch: 1
outlet.7.switchable: 1
outlet.8.desc: Load 8
outlet.8.id: 8
outlet.8.switch: 1
outlet.8.switchable: 1
outlet.9.desc: Load 9
outlet.9.id: 9
outlet.9.switchable: 0
ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
ups.debug.D: 30 30 37 44 0d 00 00 '007D...'
ups.debug.L: 31 39 30 30 30 30 0d '190000.'
ups.debug.load_banks: 8
ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
ups.debug.S: 31 34 30 31 30 30 0d '140100.'
ups.debug.T: 39 45 30 30 30 31 0d '9E0001.'
ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
ups.delay.shutdown: 64
ups.firmware: F1114.A
ups.firmware.aux: protocol 0005
ups.id: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 500
ups.productid: 0001
ups.status: 
ups.vendorid: 09ae
battery.voltage.nominal: 48
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4-480-g14301bdb
driver.version.internal: 0.29
input.voltage.nominal: 208
outlet.1.desc: Load 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.desc: Load 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
outlet.3.desc: Load 3
outlet.3.id: 3
outlet.3.switch: 1
outlet.3.switchable: 1
outlet.4.desc: Load 4
outlet.4.id: 4
outlet.4.switch: 1
outlet.4.switchable: 1
outlet.5.desc: Load 5
outlet.5.id: 5
outlet.5.switch: 1
outlet.5.switchable: 1
outlet.6.desc: Load 6
outlet.6.id: 6
outlet.6.switch: 1
outlet.6.switchable: 1
outlet.7.desc: Load 7
outlet.7.id: 7
outlet.7.switch: 1
outlet.7.switchable: 1
outlet.8.desc: Load 8
outlet.8.id: 8
outlet.8.switch: 1
outlet.8.switchable: 1
outlet.9.desc: Load 9
outlet.9.id: 9
outlet.9.switchable: 0
ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
ups.debug.D: 30 30 37 44 0d 00 00 '007D...'
ups.debug.L: 31 39 30 30 30 30 0d '190000.'
ups.debug.load_banks: 8
ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
ups.debug.S: 31 34 30 31 30 30 0d '140100.'
ups.debug.T: 39 45 30 30 30 31 0d '9E0001.'
ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
ups.delay.shutdown: 64
ups.firmware: F1114.A
ups.firmware.aux: protocol 0005
ups.id: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 500
ups.productid: 0001
ups.status: 
ups.vendorid: 09ae
battery.voltage.nominal: 48
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4-480-g14301bdb
driver.version.internal: 0.29
input.voltage.nominal: 208
outlet.1.desc: Load 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.desc: Load 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
outlet.3.desc: Load 3
outlet.3.id: 3
outlet.3.switch: 1
outlet.3.switchable: 1
outlet.4.desc: Load 4
outlet.4.id: 4
outlet.4.switch: 1
outlet.4.switchable: 1
outlet.5.desc: Load 5
outlet.5.id: 5
outlet.5.switch: 1
outlet.5.switchable: 1
outlet.6.desc: Load 6
outlet.6.id: 6
outlet.6.switch: 1
outlet.6.switchable: 1
outlet.7.desc: Load 7
outlet.7.id: 7
outlet.7.switch: 1
outlet.7.switchable: 1
outlet.8.desc: Load 8
outlet.8.id: 8
outlet.8.switch: 1
outlet.8.switchable: 1
outlet.9.desc: Load 9
outlet.9.id: 9
outlet.9.switchable: 0
ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
ups.debug.D: 30 30 37 43 0d 00 00 '007C...'
ups.debug.L: 31 39 30 30 30 30 0d '190000.'
ups.debug.load_banks: 8
ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
ups.debug.S: 31 34 30 31 30 30 0d '140100.'
ups.debug.T: 39 45 30 30 30 31 0d '9E0001.'
ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
ups.delay.shutdown: 64
ups.firmware: F1114.A
ups.firmware.aux: protocol 0005
ups.id: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 500
ups.productid: 0001
ups.status: 
ups.vendorid: 09ae
battery.voltage.nominal: 48
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4-480-g14301bdb
driver.version.internal: 0.29
input.voltage.nominal: 208
outlet.1.desc: Load 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.desc: Load 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
outlet.3.desc: Load 3
outlet.3.id: 3
outlet.3.switch: 1
outlet.3.switchable: 1
outlet.4.desc: Load 4
outlet.4.id: 4
outlet.4.switch: 1
outlet.4.switchable: 1
outlet.5.desc: Load 5
outlet.5.id: 5
outlet.5.switch: 1
outlet.5.switchable: 1
outlet.6.desc: Load 6
outlet.6.id: 6
outlet.6.switch: 1
outlet.6.switchable: 1
outlet.7.desc: Load 7
outlet.7.id: 7
outlet.7.switch: 1
outlet.7.switchable: 1
outlet.8.desc: Load 8
outlet.8.id: 8
outlet.8.switch: 1
outlet.8.switchable: 1
outlet.9.desc: Load 9
outlet.9.id: 9
outlet.9.switchable: 0
ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
ups.debug.D: 30 30 37 43 0d 00 00 '007C...'
ups.debug.L: 31 39 30 30 30 30 0d '190000.'
ups.debug.load_banks: 8
ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
ups.debug.S: 31 34 30 31 30 30 0d '140100.'
ups.debug.T: 39 46 30 30 30 31 0d '9F0001.'
ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
ups.delay.shutdown: 64
ups.firmware: F1114.A
ups.firmware.aux: protocol 0005
ups.id: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 500
ups.productid: 0001
ups.status: 
ups.vendorid: 09ae
battery.voltage.nominal: 48
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4-480-g14301bdb
driver.version.internal: 0.29
input.voltage.nominal: 208
outlet.1.desc: Load 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.desc: Load 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
outlet.3.desc: Load 3
outlet.3.id: 3
outlet.3.switch: 1
outlet.3.switchable: 1
outlet.4.desc: Load 4
outlet.4.id: 4
outlet.4.switch: 1
outlet.4.switchable: 1
outlet.5.desc: Load 5
outlet.5.id: 5
outlet.5.switch: 1
outlet.5.switchable: 1
outlet.6.desc: Load 6
outlet.6.id: 6
outlet.6.switch: 1
outlet.6.switchable: 1
outlet.7.desc: Load 7
outlet.7.id: 7
outlet.7.switch: 1
outlet.7.switchable: 1
outlet.8.desc: Load 8
outlet.8.id: 8
outlet.8.switch: 1
outlet.8.switchable: 1
outlet.9.desc: Load 9
outlet.9.id: 9
outlet.9.switchable: 0
ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
ups.debug.D: 30 30 38 30 0d 00 00 '0080...'
ups.debug.L: 31 39 31 34 30 30 0d '191400.'
ups.debug.load_banks: 8
ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
ups.debug.S: 31 34 30 31 30 30 0d '140100.'
ups.debug.T: 39 46 30 30 30 31 0d '9F0001.'
ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
ups.delay.shutdown: 64
ups.firmware: F1114.A
ups.firmware.aux: protocol 0005
ups.id: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 500
ups.productid: 0001
ups.status: 
ups.vendorid: 09ae
battery.voltage.nominal: 48
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.type: ups
driver.name: tripplite_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4-480-g14301bdb
driver.version.internal: 0.29
input.voltage.nominal: 208
outlet.1.desc: Load 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.desc: Load 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
outlet.3.desc: Load 3
outlet.3.id: 3
outlet.3.switch: 1
outlet.3.switchable: 1
outlet.4.desc: Load 4
outlet.4.id: 4
outlet.4.switch: 1
outlet.4.switchable: 1
outlet.5.desc: Load 5
outlet.5.id: 5
outlet.5.switch: 1
outlet.5.switchable: 1
outlet.6.desc: Load 6
outlet.6.id: 6
outlet.6.switch: 1
outlet.6.switchable: 1
outlet.7.desc: Load 7
outlet.7.id: 7
outlet.7.switch: 1
outlet.7.switchable: 1
outlet.8.desc: Load 8
outlet.8.id: 8
outlet.8.switch: 1
outlet.8.switchable: 1
outlet.9.desc: Load 9
outlet.9.id: 9
outlet.9.switchable: 0
ups.debug.0: 00 05 58 58 58 58 0d '..XXXX.'
ups.debug.D: 36 45 38 37 0d 00 00 '6E87...'
ups.debug.L: 31 33 35 41 30 31 0d '135A01.'
ups.debug.load_banks: 8
ups.debug.M: 30 30 37 31 0d 00 00 '0071...'
ups.debug.P: 30 35 30 30 0d 00 00 '0500...'
ups.debug.S: 31 34 30 30 30 30 0d '140000.'
ups.debug.T: 39 46 32 35 37 31 0d '9F2571.'
ups.debug.V: 33 30 38 38 0d 00 00 '3088...'
ups.delay.shutdown: 64
ups.firmware: F1114.A
ups.firmware.aux: protocol 0005
ups.id: 65535
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power.nominal: 500
ups.productid: 0001
ups.status: 
ups.vendorid: 09ae
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to