On 1/22/19 10:06 PM, Charles Lepple wrote:
> On Jan 22, 2019, at 4:37 PM, Phil Stracchino <[email protected]> wrote:
>> Is there any practical benefit to getting the SNMP network card for it
>> unless I plan to monitor it via SNMP, or can any monitoring and
>> management I need to do be done perfectly well via serial, as on my APCs?
> 
> For CyberPower, a SNMP card might be your best bet. I don't have specific 
> experience with the RMCARD205 that they recommend on their website, but most 
> vendors seem to be able to get SNMP right. If nothing else, SNMP card 
> firmware is usually upgradeable.
> 
> If you are mainly concerned about shutdowns when the UPS signals a low 
> battery alert, then there is a good chance that the PR3000LCD* models are all 
> supported equally well by the usbhid-ups driver. However, you may want to 
> check the issue list if you are planning to depend on another threshold for 
> shutdown: 
> https://github.com/networkupstools/nut/issues?q=is%3Aissue+is%3Aopen+label%3A%22CyberPower+%28CPS%29%22
> 
> Also, you mentioned serial monitoring. I am not as familiar with serial 
> CyberPower models, but take note of the support description here:
> 
> https://networkupstools.org/docs/man/powerpanel.html#_support_status
> 
> Most of the serial-connected CPS models have lower compatibility ratings due 
> to this lack of public information:
> 
> https://networkupstools.org/stable-hcl.html?manufacturer=Cyber%20Power%20Systems

Thanks, Charles.  Good information.

I'll go ahead and add the SNMP card based on that recommendation.


-- 
  Phil Stracchino
  Babylon Communications
  [email protected]
  [email protected]
  Landline: +1.603.293.8485
  Mobile:   +1.603.998.6958