On Sat, 16 Feb 2019, James wrote:
Now it says:
battery.runtime: 1170
The display on the UPS fluctuates between 16-19 minutes.
ups.load says 30 constantly and The display on the UPS says 30% so I think
that is correct.
battery.runtime is in seconds, so that agrees with the UPS display as
well.
How you find out your battery was manufactured in 2012?
APC batteries have a smart chip that records stuff like that and can
be read by the UPS. Another possibility, is that they "refilled"
an old case. The end result was a substandard (but working - and
cheap) battery.
How would I know if is the UPS?
That fluctuating runtime sounds suspicious - although the load is also
fluctuating between 32 and 28 in your examples. Maybe the lower
runtime is a consequence of the higher load? Why is your load varying?
It might be something plugged into the UPS. Maybe your server makes
the load difference when CPUs are maxed out?
--
Stuart D. Gathman <[email protected]>
"Confutatis maledictis, flamis acribus addictis" - background song for
a Microsoft sponsored "Where do you want to go from here?" commercial.