On Sat, 16 Feb 2019, James wrote:

Now it says:
battery.runtime: 1170
The display on the UPS fluctuates between 16-19 minutes.

ups.load says 30 constantly and The display on the UPS says 30% so I think that is correct.

battery.runtime is in seconds, so that agrees with the UPS display as
well.

How you find out your battery was manufactured in 2012?

APC batteries have a smart chip that records stuff like that and can
be read by the UPS.  Another possibility, is that they "refilled"
an old case.  The end result was a substandard (but working - and
cheap) battery.

How would I know if is the UPS?

That fluctuating runtime sounds suspicious - although the load is also
fluctuating between 32 and 28 in your examples.  Maybe the lower
runtime is a consequence of the higher load?  Why is your load varying?
It might be something plugged into the UPS.  Maybe your server makes
the load difference when CPUs are maxed out?

--
              Stuart D. Gathman <[email protected]>
"Confutatis maledictis, flamis acribus addictis" - background song for
a Microsoft sponsored "Where do you want to go from here?" commercial.

_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser