On 2019-04-02 10:35 p.m., Charles Lepple wrote:
On Apr 2, 2019, at 9:42 PM, James wrote:
I switched my desktop with my raspberry pi because I thought my desktop ups had
a larger capacity.
Now the ups.load of each is not what it was (it should be).
Note that ups.load is a percentage of "full load", which is up to each UPS
vendor to define. (Some vendors use different margins, and I don't know that we have done
a thorough check to see how well the load percentage tracks Watts or VA ratings when
those are available.) If I am reading the model numbers correctly, you have an 850 VA CPS
UPS, and a 550 VA APC, so at the very least, you would need to convert to a unit like VA
to be able to compare the two directly. Or you can compare the numbers on one UPS with
the two different loads.
The APC starts out with a load of 6 and a runtime of 98 minutes. It then
changes to a load of 3 and a runtime of 147 minutes (not quite double). If
nothing is plugged in, do you get a load of 0? If so, consider that the control
electronics will require a certain amount of current from the battery just to
keep the output running, and it may be in the same ballpark as a load of 3-6%.
Bear in mind the precision and accuracy of these measurements are not
guaranteed by the vendor. Two points may determine a line, but this is an
inverse relationship, so a small change in load means a larger change in
runtime. You could add a dummy load and see if it tracks linearly up from there.
The CPS UPS seems to be in a similar situation. Starting with a load of 19%, it
estimates a runtime of 45 minutes. A load of 9% yields 86 minutes, or nearly
double.
In both cases, you may want to check the owner's manual to see if the vendor
has typical runtimes. The UPS electronics are probably sized for 20-100% load,
given the use case of several minutes on battery to let a generator kick in, or
allow an orderly shutdown.
Since I can't rely on the estimated runtime, is it reasonable to assume
that my raspberry pi will run longer on the CPS compared to the APC?
Is there a way to see the time elapsed between when the pi goes on UPS
and when it shuts down?