OK, reporting back. I edited ups.conf again and set ondelay to 0 again. At the same time I defined offdelay as 60. After this I rebooted the pi and - tata - it works. I did at last three test circuits (pulling the cord), NUT shuts down system on low battery, 60 seconds later UPS loses power. After the unit is on line again power returns and everything is coming up as expected.
So far I am satisfied with this setting, hopefully it will work that way in case of a real power down. Thanks a lot for your patience. And thanks a lot for the software itself. -----Ursprüngliche Nachricht----- Von: Nut-upsuser Im Auftrag von EP Gesendet: Sonntag, 27. Oktober 2019 14:28 An: [email protected] Betreff: Re: [Nut-upsuser] Problems with NUT on Raspberry Pi I checked it with the Windows machine. There are nearly no parameters to set directly to the ups. The only thing to set is the low battery-state. All other settings seem to run on the windows machine only. Ups.delay.start was set to 30 after Windows-configuration. The rest seems to be unattended: Init SSL without certificate database battery.charge: 64 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 960 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 13.4 battery.voltage.nominal: 12 device.mfr: CPS device.model: OR600ELCDRM1U device.type: ups driver.name: usbhid-ups driver.parameter.ondelay: -1 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 10 driver.parameter.port: auto driver.parameter.synchronous: no driver.version: 2.7.4 driver.version.data: CyberPower HID 0.4 driver.version.internal: 0.41 input.transfer.high: 263 input.transfer.low: 160 input.voltage: 233.0 input.voltage.nominal: 230 output.voltage: 233.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 40 ups.mfr: CPS ups.model: OR600ELCDRM1U ups.productid: 0601 ups.realpower.nominal: 360 ups.status: OL CHRG ups.test.result: Done and passed ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 Any suggestions? I can't believe I am the only guy using this unit and facing these problems. -----Ursprüngliche Nachricht----- Von: Nut-upsuser Im Auftrag von Roger Price Gesendet: Sonntag, 27. Oktober 2019 11:56 An: [email protected] Betreff: Re: [Nut-upsuser] Problems with NUT on Raspberry Pi On Sun, 27 Oct 2019, EP wrote: > I can't imagine that's the way cyberpower wants their unit to work. > With this behavior the unit does exactly the opposite of what it is > built for. It doesn't protect your equipment. It will destroy it > because the server which was just shutted down cleanly will boot again > on a battery-powererd ups. What a crap. > > But I am not finished at all because I can't believe there is no > solution for this problem. Perhaps it's time to borrow a Windows PC and try the software that comes with the UPS. Roger _______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser _______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser _______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser