OK, reporting back. 

I edited ups.conf again and set ondelay to 0 again. At the same time I defined 
offdelay as 60. After this I rebooted the pi and - tata - it works. 
I did at last three test circuits (pulling the cord), NUT shuts down system on 
low battery, 60 seconds later UPS loses power. After the unit is on line again 
power returns and everything is coming up as expected. 

So far I am satisfied with this setting, hopefully it will work that way in 
case of a real power down. 

Thanks a lot for your patience. And thanks a lot for the software itself. 



-----Ursprüngliche Nachricht-----
Von: Nut-upsuser Im Auftrag von EP
Gesendet: Sonntag, 27. Oktober 2019 14:28
An: [email protected]
Betreff: Re: [Nut-upsuser] Problems with NUT on Raspberry Pi

I checked it with the Windows machine. There are nearly no parameters to set 
directly to the ups. The only thing to set is the low battery-state. All other 
settings seem to run on the windows machine only. 
Ups.delay.start was set to 30 after Windows-configuration. The rest seems to be 
unattended: 

Init SSL without certificate database
battery.charge: 64
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 960
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 13.4
battery.voltage.nominal: 12
device.mfr: CPS
device.model: OR600ELCDRM1U
device.type: ups
driver.name: usbhid-ups
driver.parameter.ondelay: -1
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 10
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: CyberPower HID 0.4
driver.version.internal: 0.41
input.transfer.high: 263
input.transfer.low: 160
input.voltage: 233.0
input.voltage.nominal: 230
output.voltage: 233.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 40
ups.mfr: CPS
ups.model: OR600ELCDRM1U
ups.productid: 0601
ups.realpower.nominal: 360
ups.status: OL CHRG
ups.test.result: Done and passed
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Any suggestions? I can't believe I am the only guy using this unit and facing 
these problems. 


-----Ursprüngliche Nachricht-----
Von: Nut-upsuser Im Auftrag von Roger Price
Gesendet: Sonntag, 27. Oktober 2019 11:56
An: [email protected]
Betreff: Re: [Nut-upsuser] Problems with NUT on Raspberry Pi

On Sun, 27 Oct 2019, EP wrote:

> I can't imagine that's the way cyberpower wants their unit to work. 
> With this behavior the unit does exactly the opposite of what it is 
> built for. It doesn't protect your equipment. It will destroy it 
> because the server which was just shutted down cleanly will boot again 
> on a battery-powererd ups. What a crap.
>
> But I am not finished at all because I can't believe there is no 
> solution for this problem.

Perhaps it's time to borrow a Windows PC and try the software that comes with 
the UPS.   Roger

_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to