On Tue, 31 Dec 2019, David White wrote:

... But it did not actually turn off the UPS at all. The UPS kept beeping and I had to turn it off manually.

I thought that NUT would handle this. But perhaps it cannot for my unit? Or perhaps I have things improperly configured? Any suggestions? Thanks and happy new year!

        ########### /etc/nut/upsmon.conf ###########
MONITOR belkinusb@localhost 1 local_mon ********* master
MINSUPPLIES 1
SHUTDOWNCMD "/sbin/shutdown -h +0"
NOTIFYCMD /home/android/nutShutdown.sh
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower
NOTIFYMSG ONBATT        "UPS %s on battery"
NOTIFYFLAG ONBATT       WALL+EXEC
RBWARNTIME 43200
NOCOMMWARNTIME 300
FINALDELAY 5

        ########### /etc/nut/upssched.conf ###########
CMDSCRIPT /bin/upssched-cmd

Happy New Year David!, The command "/sbin/upsdrvctl shutdown" turns off the UPS unit, but this is not being executed. How do you plan to shut down on power failure? Will you wait for upsd's [LB] status or use a timer? The simplest is to wait for [LB], but the upsmon.conf contains no declarations for NOTIFYFLAG LOWBATT.

The script /home/android/nutShutdown.sh will be called when wall power fails, but nut-report was unable to show its contents. Should nutShutdown.sh perform the system shutdown?

Perhaps a more complete set of NOTIFYFLAG and NOTIFYMSG declarations will make things clearer. I would also recommend adding the SYSLOG option to the declarations.

Do you shutdown using systemd?