Borrowing from our friends at Ask Ubuntu ( https://askubuntu.com/a/276637 )
there is. I've modified it for use with a Tripp Lite UPS and 3024 protocol
below. Try disconnect/reconnect after and see what happens.
:/etc/nut$ cat /etc/udev/rules.d/90-nut-ups.rules
# /etc/udev/rules.d/90-nut-ups.rules
ACTION=="add", \
SUBSYSTEM=="usb", \
ATTR{idVendor}=="09ae", ATTR{idProduct}=="3024", \
MODE="0660", GROUP="nut"
Thank you,
David Zomaya
Tripp Lite
________________________________
From: Tom Cooper <[email protected]>
Sent: Wednesday, May 20, 2020 2:02 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp
Lite Internet600U
Funny - I thought of that and had tried it. Didn't work
[cid:0.28869202910.3916900324392194752.17233779738__smiley__img__src]
I also moved it from the USB2 ports to the USB3 ports.
Same result.
I have not heard of udev, but after quick googling and glancing at an example,
/etc/udev/rules.d/99-com.rules
I am not convinced that I coule come up with a formula to make a working rule.
Is there a simple sample I can copy to help figure out elevated privileges?
---- On Wed, 20 May 2020 14:56:14 -0400 David Zomaya
<[email protected]> wrote ----
"Can't claim USB device [09ae:3024]: could not detach kernel driver from
interface 0: Operation not permitted"
Is probably an issue with NUT grabbing the UPS... can you disconnect and
reconnect the USB cable and try again?
If that fails, maybe a udev rule will help.
Thank you,
David Zomaya
Tripp Lite
<http://www.tripplite.com/>
________________________________
From: Tom Cooper <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 20, 2020 1:54:20 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp
Lite Internet600U
David,
I appreciate the quick feedback!
If I didn't fat finger any of the parameters you sent me, it's still not
working.
Here's the output from the attempt to start. (BTW - nothing appears in the
daemon.log when I use the upsdrvctl command.)
pi@elmer:/home/macbackup $ sudo vi /etc/nut/nut.conf
pi@elmer:/home/macbackup $ sudo vi /etc/nut/ups.conf
pi@elmer:/home/macbackup $ sudo vi /etc/nut/upsd.conf
pi@elmer:/home/macbackup $ sudo upsdrvctl start
Network UPS Tools - UPS driver controller 2.7.4
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [09ae:3024]: could not detach kernel driver from
interface 0: Operation not permitted
Driver failed to start (exit status=1)
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [09ae:3024]: could not detach kernel driver from
interface 0: Operation not permitted
Driver failed to start (exit status=1)
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [09ae:3024]: could not detach kernel driver from
interface 0: Operation not permitted
Driver failed to start (exit status=1)
---- On Wed, 20 May 2020 14:03:09 -0400 David Zomaya
<[email protected]<mailto:[email protected]>> wrote ----
My thoughts for a test:
*
Just have
MODE=standalone
in nut.conf
*
Put
[tripplite]
driver = usbhid-ups
port = auto
productid=3024
desc = "Tripp Lite Internet600U"
In ups.conf
*
Put
LISTEN 127.0.0.1 3493
LISTEN ::1 3493
[tripplite]
driver = usbhid-ups
port = auto
in upsd.conf
That may be suboptimal but will probably work for a test.
Side note: I use "upsdrvctl start/stop" to start and stop the driver.
Thank you,
David Zomaya
Tripp Lite
________________________________
From: Tom Cooper <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 20, 2020 12:55 PM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp
Lite Internet600U
David,
That's exciting - but I am not seeing similar results.
I *must* be doing something dumb - but I can't see it.
I've got nut-2.7.4-8 installed on my pi
Hope you can help.
Tom
pi@elmer:/home/macbackup $ lsusb | grep ipp
Bus 001 Device 004: ID 09ae:3024 Tripp Lite
pi@elmer:/home/macbackup $ sudo cat /etc/nut/nut.conf
# Network UPS Tools: example nut.conf
#
##############################################################################
# General section
##############################################################################
# The MODE determines which part of the NUT is to be started, and which
# configuration files must be modified.
#
# This file try to standardize the various files being found in the field, like
# /etc/default/nut on Debian based systems, /etc/sysconfig/ups on RedHat based
# systems, ... Distribution's init script should source this file to see which
# component(s) has to be started.
#
# The values of MODE can be:
# - none: NUT is not configured, or use the Integrated Power Management, or use
# some external system to startup NUT components. So nothing is to be started.
# - standalone: This mode address a local only configuration, with 1 UPS
# protecting the local system. This implies to start the 3 NUT layers (driver,
# upsd and upsmon) and the matching configuration files. This mode can also
# address UPS redundancy.
# - netserver: same as for the standalone configuration, but also need
# some more network access controls (firewall, tcp-wrappers) and possibly a
# specific LISTEN directive in upsd.conf.
# Since this MODE is opened to the network, a special care should be applied
# to security concerns.
# - netclient: this mode only requires upsmon.
#
# IMPORTANT NOTE:
# This file is intended to be sourced by shell scripts.
# You MUST NOT use spaces around the equal sign!
MODE=none
[tripplite]
driver = usbhid-ups
port = auto
productid=3024
desc = "Tripp Lite Internet600U"
pi@elmer:/home/macbackup $ sudo systemctl start nut-driver
Job for nut-driver.service failed because the control process exited with error
code.
See "systemctl status nut-driver.service" and "journalctl -xe" for details.
>From the log file:
May 20 13:51:47 elmer systemd[1]: Starting Network UPS Tools - power device
driver controller...
May 20 13:51:47 elmer upsdrvctl[2658]: This TrippLite device (09ae:3024) is not
(or perhaps not yet) supported
May 20 13:51:47 elmer upsdrvctl[2658]: by usbhid-ups. Please make sure you have
an up-to-date version of NUT. If
May 20 13:51:47 elmer upsdrvctl[2658]: this does not fix the problem, try
running the driver with the
May 20 13:51:47 elmer upsdrvctl[2658]: '-x productid=3024' option. Please
report your results to the NUT user's
May 20 13:51:47 elmer upsdrvctl[2658]: mailing list
<[email protected]<mailto:[email protected]>>.
May 20 13:51:47 elmer upsdrvctl[2658]: Network UPS Tools - Generic HID driver
0.41 (2.7.4)
May 20 13:51:47 elmer upsdrvctl[2658]: USB communication driver 0.33
May 20 13:51:47 elmer upsdrvctl[2658]: No matching HID UPS found
May 20 13:51:47 elmer upsdrvctl[2658]: Driver failed to start (exit status=1)
May 20 13:51:52 elmer upsdrvctl[2658]: This TrippLite device (09ae:3024) is not
(or perhaps not yet) supported
May 20 13:51:52 elmer upsdrvctl[2658]: by usbhid-ups. Please make sure you have
an up-to-date version of NUT. If
May 20 13:51:52 elmer upsdrvctl[2658]: this does not fix the problem, try
running the driver with the
May 20 13:51:52 elmer upsdrvctl[2658]: '-x productid=3024' option. Please
report your results to the NUT user's
May 20 13:51:52 elmer upsdrvctl[2658]: mailing list
<[email protected]<mailto:[email protected]>>.
May 20 13:51:52 elmer upsdrvctl[2658]: Network UPS Tools - Generic HID driver
0.41 (2.7.4)
May 20 13:51:52 elmer upsdrvctl[2658]: USB communication driver 0.33
May 20 13:51:52 elmer upsdrvctl[2658]: No matching HID UPS found
May 20 13:51:52 elmer upsdrvctl[2658]: Driver failed to start (exit status=1)
May 20 13:51:58 elmer upsdrvctl[2658]: This TrippLite device (09ae:3024) is not
(or perhaps not yet) supported
May 20 13:51:58 elmer upsdrvctl[2658]: by usbhid-ups. Please make sure you have
an up-to-date version of NUT. If
May 20 13:51:58 elmer upsdrvctl[2658]: this does not fix the problem, try
running the driver with the
May 20 13:51:58 elmer upsdrvctl[2658]: '-x productid=3024' option. Please
report your results to the NUT user's
May 20 13:51:58 elmer upsdrvctl[2658]: mailing list
<[email protected]<mailto:[email protected]>>.
May 20 13:51:58 elmer upsdrvctl[2658]: Network UPS Tools - Generic HID driver
0.41 (2.7.4)
May 20 13:51:58 elmer upsdrvctl[2658]: USB communication driver 0.33
May 20 13:51:58 elmer upsdrvctl[2658]: No matching HID UPS found
May 20 13:51:58 elmer systemd[1]: nut-driver.service: Control process exited,
code=exited, status=1/FAILURE
May 20 13:51:58 elmer upsdrvctl[2658]: Driver failed to start (exit status=1)
May 20 13:51:58 elmer upsdrvctl[2658]: Network UPS Tools - UPS driver
controller 2.7.4
May 20 13:51:58 elmer systemd[1]: nut-driver.service: Failed with result
'exit-code'.
May 20 13:51:58 elmer systemd[1]: Failed to start Network UPS Tools - power
device driver controller.
---- On Wed, 20 May 2020 13:46:09 -0400 David Zomaya
<[email protected]<mailto:[email protected]>> wrote ----
Tested a Ubuntu 18.04 LTS virtual machine with NUT 2.7.4 and a 3024 protocol
Tripp Lite UPS (mine is a INTERNET550U, but same protocol)
:/etc/nut$ lsusb | grep Tripp
Bus 002 Device 004: ID 09ae:3024 Tripp Lite
I it got generally working (outputting reasonable responses to upsc, although
there are some issues with variables like frequency) by adding productid=3024
to my ups.conf. Like this:
[TrippLiteUPS3024]
driver = usbhid-ups
port = auto
productid=3024
Here is the upsc output:
:/etc/nut$ sudo upsc TrippLiteUPS3024
Init SSL without certificate database
battery.charge: 100
battery.charge.warning: 30
battery.runtime: 1850
battery.type: PbAc
battery.voltage: 0.0
battery.voltage.nominal: 12.0
device.mfr: Tripp Lite
device.model: INTERNET550U
device.serial: 2951EVLBC87B503245
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 3024
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: TrippLite HID 0.82
driver.version.internal: 0.41
input.frequency: 6010.0
input.transfer.high: 145.0
input.transfer.low: 95.0
input.voltage: 0.0
input.voltage.nominal: 120
output.current: 0.0
output.frequency: 6010.0
output.frequency.nominal: 60
output.voltage: 0.0
output.voltage.nominal: 120
ups.beeper.status: disabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: Tripp Lite
ups.model: INTERNET550U
ups.power: 0.0
ups.power.nominal: 550
ups.productid: 3024
ups.serial: 2951EVLBC87B503245
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.timer.start: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0
:/etc/nut$
Tom: Let me know if this helps you.
List in general: would this help solve general 3024 issues?
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Nut-upsuser
<nut-upsuser-bounces+david_zomaya=tripplite....@alioth-lists.debian.net<mailto:[email protected]>>
on behalf of David Zomaya
Sent: Wednesday, May 20, 2020 8:49 AM
To: Tom Cooper
Cc: nut-upsuser
Subject: [POSSIBLE FRAUD] Re: [Nut-upsuser] [EXTERNAL] Re: Help with Tripp Lite
Internet600U
Will do. Ball in my court for now.
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Tom Cooper <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 20, 2020 8:47:28 AM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [EXTERNAL] Re: [Nut-upsuser] Help with Tripp Lite Internet600U
That would be great. If there is something I can do to collect data or
troubleshoot, please let me know.
---- On Wed, 20 May 2020 08:51:14 -0400 David Zomaya
<[email protected]<mailto:[email protected]>> wrote ----
I'm still working remotely, but I should be able to get something set up soon.
I'll reply all here once I have something to report.
Thank you,
David Zomaya
Tripp Lite<http://www.tripplite.com/>
________________________________
From: Tom Cooper <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 20, 2020 7:48:32 AM
To: David Zomaya
Cc: nut-upsuser
Subject: Re: [EXTERNAL] Re: [Nut-upsuser] Help with Tripp Lite Internet600U
I'm running Raspbian Buster, but given that the error seems to be "higher
order" than a hardware issue - one of parsing the protocol? I suspect that
Ubuntu would be a decent "lookalike" to model the issue.
---- On Tue, 19 May 2020 22:31:56 -0400 David Zomaya
<[email protected]<mailto:[email protected]>> wrote ----
If I installed and tested against Ubuntu, how useful would that be in general
and in this specific case?
I think we've seen a few reports of issues with the newer 3024 protocols and
I'd like to help get them sorted out.
Thank you,
David Zomaya
Tripp Lite
________________________________
From: Nut-upsuser
<nut-upsuser-bounces+david_zomaya=tripplite....@alioth-lists.debian.net<mailto:[email protected]>>
on behalf of Charles Lepple <[email protected]<mailto:[email protected]>>
Sent: Tuesday, May 19, 2020 9:24 PM
To: Tom Cooper
Cc: nut-upsuser
Subject: [EXTERNAL] Re: [Nut-upsuser] Help with Tripp Lite Internet600U
This is an EXTERNAL email. Please take a moment and think before clicking any
links or opening any attachments from this email. If suspicious, please
forward to [email protected]<mailto:[email protected]> for review.
______________________________________________________________________
On May 19, 2020, at 9:21 PM, Tom Cooper
<[email protected]<mailto:[email protected]>> wrote:
>
> Bus 001 Device 004: ID 09ae:3024 Tripp Lite
>
We have only had reports of success with protocol 2010 of INTERNET600U (which
would be 09ae:2010 in lsusb).
More details:
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_pipermail_nut-2Dupsuser_2020-2DApril_011803.html&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=PY3fmIYRp20XyPJAWtuIoMta82maER1CGSdOB3x6HEM&s=9Ri1IbEOy_cyZZctw4a1IFxUMKAIwhu2xTRnjanyorI&e=
_______________________________________________
Nut-upsuser mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=PY3fmIYRp20XyPJAWtuIoMta82maER1CGSdOB3x6HEM&s=374XOzWi2asZji_KmGBZFGWtzgxtuHrjfrzcGP8Fsvw&e=
_______________________________________________
Nut-upsuser mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=PY3fmIYRp20XyPJAWtuIoMta82maER1CGSdOB3x6HEM&s=374XOzWi2asZji_KmGBZFGWtzgxtuHrjfrzcGP8Fsvw&e=
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
________________________________
This message is for the addressee's use only. It may contain confidential
information. If you receive this message in error, please delete it and notify
the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no
responsibility for viruses which may infect an email sent to you from Tripp
Lite and which damage your electronic systems or information. It is your
responsibility to maintain virus detection systems to prevent damage to your
electronic systems and information.
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser