On Sun, 21 Jun 2020, Henning Ryll wrote:

My configuration is working so far. I can check values with upsc and I'm getting mails, when the power line ist disconnected and reconneted.

Do you also get a mail for LB status ?

Shutting down the machine works if I do this via console with 'upsmon -c fsd'.
But no automatic shutdown :(

Did you intend to get an automatic shutdown on LB with this configuration?

If I try to set battery.runtime.low > 300 I get an error. See below.
 
# upsd -V
Network UPS Tools upsd 2.7.4
 
# upsrw -s battery.runtime.low=301 -u admin -p aXXX apcsmartups
Unexpected response from upsd: ERR INVALID-VALUE
 
# upsrw -s battery.runtime.low=301 -u admin -p aXXX apcsmartups
OK
 
# upsc apcsmartups
battery.alarm.threshold: 0
battery.charge: 073.0
battery.charge.restart: 00
battery.date: 19/25/10
battery.packs: 000
battery.runtime: 11400
battery.runtime.low: 300
battery.voltage: 25.24
battery.voltage.nominal: 024

It's surprising not to see battery.charge.low . Is this implied by battery.runtime.low ?

Roger