On Sun, 21 Jun 2020, Henning Ryll wrote:
My configuration is working so far. I can check values with upsc and I'm getting mails, when the power line ist disconnected and reconneted.
Do you also get a mail for LB status ?
Shutting down the machine works if I do this via console with 'upsmon -c fsd'. But no automatic shutdown :(
Did you intend to get an automatic shutdown on LB with this configuration?
If I try to set battery.runtime.low > 300 I get an error. See below. # upsd -V Network UPS Tools upsd 2.7.4 # upsrw -s battery.runtime.low=301 -u admin -p aXXX apcsmartups Unexpected response from upsd: ERR INVALID-VALUE # upsrw -s battery.runtime.low=301 -u admin -p aXXX apcsmartups OK # upsc apcsmartups battery.alarm.threshold: 0 battery.charge: 073.0 battery.charge.restart: 00 battery.date: 19/25/10 battery.packs: 000 battery.runtime: 11400 battery.runtime.low: 300 battery.voltage: 25.24 battery.voltage.nominal: 024
It's surprising not to see battery.charge.low . Is this implied by battery.runtime.low ?
Roger