On Wed, 12 Aug 2020, Manuel Wolfshant wrote:
So nut on Synology believes that it is a good idea to trigger a FSD 30 secs
AFTER switching back to line power when in fact it should CANCEL any shutdown
in progress. Unless you have the willingness to search & fix whatever
stupidities they do in their unorthodox use of nut... just use a sane version
Agreed. Could this be the cause of the unexpected shutdowns? In Synology's
function UPSShutdown :
OL=0
LB=0
while [ $OL -ne 2 -a $LB -ne 2 ]; do
sleep 10
St=`UPSStatusGet`
Function UPSStatusGet returns the current value of ups.status. Consider the case
where upsc returns [OL CHRG], the following code will set LB to 2 after 20 sec
even though the UPS is online.
if [ "$St" = "OL" ]; then
OL=`expr $OL + 1`
LB=0
else
LB=`expr $LB + 1`
OL=0
fi
echo "OL=$OL LB=$LB" >> $SZF_SAFEMODE
done
if [ $OL -eq 2 ]; then
synologset1 sys warn 0x11300012
echo "UPS back to On-Line and reboot." >> $SZF_SAFEMODE
$SYNOBOOTBIN --unset-safe-shutdown
telinit 6
The following code is executed leading to a shutdown via the flag SZF_SAFEMODE:
elif [ $LB -eq 2 ]; then
touch /var/.NormalShutdown
if [ $UPSSafeShutdown -eq 0 ]; then
echo "Waiting UPS exhausted." >> $SZF_SAFEMODE
SYSLOG "Waiting UPS exhausted."
else
echo "UPS safe shutdown." >> $SZF_SAFEMODE
SYSLOG "UPS safe shutdown."
I will write a more complete report on Synology's Safe Mode, but I would
recommend treating the NAS as a slave and running a correctly configured NUT in
one of the Ubuntu machines. Todd, if you need more detailed examples of NUT
configurations, see http://rogerprice.org/NUT/ConfigExamples.A5.pdf
Roger
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser