Hello,

I have been using NUT for a short period of time and have some questions regarding the UPS reboot signal that I can't figure out. Have tried some googling and reading the DOCs but I am struggling to understand how some variables / things are supposed to work, so would appreciate any help with any of the following questions.

I am running NUT on standalone mode on a linux machine (lets call it M1), connected via USB to the APC UPS. There is another Windows computer connected on the UPS (refer to as M2), which when not used is suspended. The windows machine (M2) is not managed by NUT due to not finding a NUT windows client but that's a separate thing.

My use case. When power is off the UPS should run till battery charge gets to 30%, then the shutdowncmd will issue a suspend to M1. UPS should continue running till power is back or battery runs out, as such the UPS should never be restarted or shutdown by NUT as that would kill the suspending. The UPS even at 30% should last couple of hours with M1,M2 suspended and power cuts at worst last 30min. Obviously I accept the fact that if the battery runs out it will greatly reduce the lifespan of the battery.

# ups.conf:

[apc1400]
        driver = usbhid-ups
        port = auto


# upsc apc1400:

Init SSL without certificate database
battery.charge: 62
battery.charge.low: 30
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2018/03/27
battery.runtime: 316
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 26.6
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Back-UPS XS 1400U
device.serial: 3B1740X16183
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: APC HID 0.96
driver.version.internal: 0.41
input.sensitivity: medium
input.transfer.high: 280
input.transfer.low: 155
input.voltage: 230.0
input.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 926.T2 .I
ups.firmware.aux: T2
ups.load: 53
ups.mfr: American Power Conversion
ups.mfr.date: 2017/10/06
ups.model: Back-UPS XS 1400U
ups.productid: 0002
ups.realpower.nominal: 700
ups.serial: 3B1740X16183
ups.status: OL CHRG
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d


I have issued upsrw -s battery.charge.low=30 apc1400 and set SHUTDOWNCMD "/bin/systemctl suspend" to reflect the above, so when battery.charge reaches 30% or available battery runtime is 120sec the computer should suspend, which it has done multiple times.

I am trying to understand what controls/triggers the UPS reboot signal.
1. Have had the UPS reboot while on power and 100% battery when manually restarting M1 for updates taking down both M1 (during boot, so the signal was delayed?) & M2 (was running). Have tried to reproduce it while writing this with a manual reboot / suspend to no avail. 2. UPS takes ~30min to reach 40% battery with M1 running and M2 suspended. After manually suspending M1 15min in a power cut (took place yesterday), after couple of minutes the UPS rebooted. When the power came back the UPS reported 57% battery charge, so it didn't even reach LB either from battery.charge.low and couldn't have been battery.runtime.low if I have understood the setting correctly. This has happened a total of 2 times iirc.

I can't figure out which settings cause the reboots. Would setting ups.timer.reboot to -1 stop it from happening regardless the cause of triggering a UPS reboot? Though I would prefer understanding what is the cause.

# OS:
  Ubuntu 18.04

# uname -a
Linux amdx4 4.15.0-112-generic #113-Ubuntu SMP Thu Jul 9 23:41:39 UTC 2020 x86_64 x86_64 x86_64 GNU/Linux

# apt policy nut:
  Installed: 2.7.4-5.1ubuntu2
  Candidate: 2.7.4-5.1ubuntu2

# UPS Model:
  APC Back-UPS 1400 (BX1400U-GR)

# Driver debug log:

Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.000000     debug level is '2'
   0.001039     upsdrv_initups...
   0.253805     Checking device (1D6B/0001) (007/001)
   0.329676     - VendorID: 1d6b
   0.329700     - ProductID: 0001
   0.329708     - Manufacturer: unknown
   0.329712     - Product: unknown
   0.329723     - Serial Number: unknown
   0.329735     - Bus: 007
   0.329746     - Device release number: 0415
   0.329749     Trying to match device
   0.329761     Device does not match - skipping
   0.329776     Checking device (1D6B/0001) (006/001)
   0.405652     - VendorID: 1d6b
   0.405690     - ProductID: 0001
   0.405717     - Manufacturer: unknown
   0.405728     - Product: unknown
   0.405734     - Serial Number: unknown
   0.405740     - Bus: 006
   0.405745     - Device release number: 0415
   0.405749     Trying to match device
   0.405762     Device does not match - skipping
   0.405783     Checking device (1D6B/0001) (005/001)
   0.481626     - VendorID: 1d6b
   0.481657     - ProductID: 0001
   0.481660     - Manufacturer: unknown
   0.481663     - Product: unknown
   0.481666     - Serial Number: unknown
   0.481669     - Bus: 005
   0.481672     - Device release number: 0415
   0.481674     Trying to match device
   0.481683     Device does not match - skipping
   0.481696     Checking device (051D/0002) (004/002)
   0.499538     - VendorID: 051d
   0.499597     - ProductID: 0002
   0.499608     - Manufacturer: American Power Conversion
   0.499615     - Product: Back-UPS XS 1400U  FW:926.T2 .I USB FW:T2
   0.499621     - Serial Number: 3B1740X16183
   0.499637     - Bus: 004
   0.499642     - Device release number: 0106
   0.499647     Trying to match device
   0.499662     Device matches
   0.501409     HID descriptor length 1028
   0.546337     Report Descriptor size = 1028
   0.546726     Using subdriver: APC HID 0.96
   0.546732     104 HID objects found
0.548374 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1 0.552380 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 2 0.555357 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 4 0.560374 Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x04, Offset: 0, Size: 8, Value: 3 0.564363 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x05, Offset: 0, Size: 8, Value: 1 0.569387 Path: UPS.PowerSummary.Charging, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.569424 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.569498 Path: UPS.PowerSummary.Discharging, Type: Input, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.569517 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.569534 Path: UPS.PowerSummary.APCStatusFlag, Type: Input, ReportID: 0x06, Offset: 16, Size: 8, Value: 8 0.569548 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8 0.572386 Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, ReportID: 0x07, Offset: 0, Size: 16, Value: 19270 0.577386 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x08, Offset: 0, Size: 16, Value: 24 0.581404 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 27.09 0.585403 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 8, Value: 3 0.588459 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 2 0.593408 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0c, Offset: 0, Size: 8, Value: 100 0.593517 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 100 0.593558 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x0c, Offset: 8, Size: 16, Value: 540 0.593588 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x0c, Offset: 8, Size: 16, Value: 540 0.597506 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 100 0.602393 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 100 0.605388 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 50 0.610393 Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 1 0.614391 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 10 0.618401 Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 1 0.621398 Path: UPS.PowerSummary.ACPresent, Type: Input, ReportID: 0x13, Offset: 0, Size: 8, Value: 1 0.621499 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1 0.626402 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 0.626439 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 0.626450 Path: UPS.PowerSummary.ShutdownImminent, Type: Input, ReportID: 0x14, Offset: 8, Size: 8, Value: 0 0.626455 Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, ReportID: 0x14, Offset: 8, Size: 8, Value: 0 0.631388 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 0.635356 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x16, Offset: 0, Size: 1, Value: 0 0.635381 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 0 0.635389 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 0.635401 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 0.635412 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x16, Offset: 2, Size: 1, Value: 1 0.635421 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1 0.635429 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Input, ReportID: 0x16, Offset: 3, Size: 1, Value: 1 0.635438 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1 0.635447 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x16, Offset: 4, Size: 1, Value: 0 0.635456 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0 0.635465 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x16, Offset: 5, Size: 1, Value: 0 0.635474 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0 0.635482 Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, ReportID: 0x16, Offset: 6, Size: 1, Value: 0 0.635491 Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0 0.635500 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x16, Offset: 7, Size: 1, Value: 0 0.635508 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x16, Offset: 7, Size: 1, Value: 0 0.635517 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x16, Offset: 8, Size: 1, Value: 0 0.635526 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0 0.635535 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x16, Offset: 9, Size: 1, Value: 0 0.635543 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x16, Offset: 9, Size: 1, Value: 0 0.635552 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Input, ReportID: 0x16, Offset: 10, Size: 1, Value: 0 0.635561 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, Type: Feature, ReportID: 0x16, Offset: 10, Size: 1, Value: 0 0.638381 Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 120 0.643414 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2 0.647381 Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 24, Value: 599297 0.651362 Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 19579 0.654351 Path: UPS.Battery.Test, Type: Input, ReportID: 0x21, Offset: 0, Size: 8, Value: 6 0.654379 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6 0.659393 Path: UPS.Battery.RemainingCapacity, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 100 0.664436 Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: 0x23, Offset: 0, Size: 16, Value: 540 0.668434 Path: UPS.Battery.RemainingTimeLimit, Type: Feature, ReportID: 0x24, Offset: 0, Size: 16, Value: 120 0.671407 Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, Offset: 0, Size: 16, Value: 24 0.676397 Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, Offset: 0, Size: 16, Value: 27.09 0.680414 Path: UPS.Battery.ff860024, Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 241 0.684411 Path: UPS.Battery.ff860018, Type: Feature, ReportID: 0x28, Offset: 0, Size: 32, Value: 0 0.687357 Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 230 0.692379 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 232 0.697371 Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x32, Offset: 0, Size: 16, Value: 155 0.701381 Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x33, Offset: 0, Size: 16, Value: 280 0.704382 Path: UPS.Input.ff860024, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 129 0.709363 Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, Offset: 0, Size: 8, Value: 1 0.713331 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 0 0.717383 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 0.720381 Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1 0.726432 Path: UPS.APCGeneralCollection.DelayBeforeShutdown, Type: Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: -1 0.730420 Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 0x50, Offset: 0, Size: 8, Value: 51 0.734407 Path: UPS.PowerConverter.ff860024, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 126 0.737374 Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, ReportID: 0x52, Offset: 0, Size: 16, Value: 700 0.742362 Path: UPS.ff860001.ff860023, Type: Feature, ReportID: 0x60, Offset: 0, Size: 16, Value: 0 0.746395 Path: UPS.ff860001.ff860026, Type: Feature, ReportID: 0x61, Offset: 0, Size: 8, Value: 154 0.750367 Path: UPS.ff860001.ff860025, Type: Feature, ReportID: 0x62, Offset: 0, Size: 32, Value: 0 0.753390 Path: UPS.iProduct, Type: Feature, ReportID: 0x7f, Offset: 0, Size: 8, Value: 5 0.759405 Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, ReportID: 0x7e, Offset: 0, Size: 8, Value: 6 0.763352 Path: UPS.iSerialNumber, Type: Feature, ReportID: 0x7d, Offset: 0, Size: 8, Value: 2 0.767345 Path: UPS.iManufacturer, Type: Feature, ReportID: 0x7c, Offset: 0, Size: 8, Value: 3 0.770390 Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, Offset: 0, Size: 16, Value: 19270 0.775354 Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 0x7a, Offset: 0, Size: 1, Value: 0 0.775390 Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID: 0x7a, Offset: 1, Size: 1, Value: 0 0.775405 Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 0x7a, Offset: 2, Size: 1, Value: 1 0.775413 Path: UPS.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x7a, Offset: 3, Size: 1, Value: 1 0.775447 Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x7a, Offset: 4, Size: 1, Value: 0 0.775483 Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x7a, Offset: 5, Size: 1, Value: 0 0.775501 Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x7a, Offset: 6, Size: 1, Value: 0 0.775514 Path: UPS.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x7a, Offset: 7, Size: 1, Value: 0 0.775527 Path: UPS.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x7a, Offset: 8, Size: 1, Value: 0 0.775542 Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 0x7a, Offset: 9, Size: 1, Value: 0 0.775555 Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, ReportID: 0x7a, Offset: 10, Size: 1, Value: 0 0.779345 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 0, Size: 8, Value: 0 0.783334 Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 0x78, Offset: 0, Size: 8, Value: 2 0.786380 Path: UPS.ff860029, Type: Feature, ReportID: 0x75, Offset: 0, Size: 16, Value: 98 0.792428 Path: UPS.ff86002a, Type: Feature, ReportID: 0x74, Offset: 0, Size: 32, Value: 0
   0.792564     Report descriptor retrieved (Reportlen = 1028)
   0.792587     Found HID device
0.792598 Detected a UPS: American Power Conversion/Back-UPS XS 1400U FW:926.T2 .I USB FW:T2 0.792668 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 100 0.792725 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 10 0.792783 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 50 0.792843 Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID: 0x23, Offset: 0, Size: 16, Value: 540 0.792917 Path: UPS.Battery.RemainingTimeLimit, Type: Feature, ReportID: 0x24, Offset: 0, Size: 16, Value: 120 0.792987 Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x26, Offset: 0, Size: 16, Value: 27.09 0.793044 Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 0x25, Offset: 0, Size: 16, Value: 24 0.793124 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 4 0.796431 Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 19579 0.796509 Path: UPS.Battery.APCBattReplaceDate, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 24, Value: 599297 0.796543 Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 0x50, Offset: 0, Size: 8, Value: 51 0.796599 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 0.796691 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 0.796713 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6 0.796735 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2 0.796762 Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x7b, Offset: 0, Size: 16, Value: 19270 0.796798 Path: UPS.PowerConverter.ConfigActivePower, Type: Feature, ReportID: 0x52, Offset: 0, Size: 16, Value: 700 0.796836 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1 0.796860 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 0.796883 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 0 0.796906 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x16, Offset: 5, Size: 1, Value: 0 0.796929 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0 0.796951 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x16, Offset: 9, Size: 1, Value: 0 0.796974 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x16, Offset: 8, Size: 1, Value: 0 0.796998 Path: UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, ReportID: 0x16, Offset: 6, Size: 1, Value: 0 0.797024 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: Feature, ReportID: 0x16, Offset: 3, Size: 1, Value: 1 0.797047 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.797067 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.797090 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1 0.797110 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 0.797129 Path: UPS.PowerSummary.ShutdownImminent, Type: Feature, ReportID: 0x14, Offset: 8, Size: 8, Value: 0 0.797144 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8 0.797161 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 0 0.797178 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 0 0.797197 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 232 0.797219 Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 230 0.797260 Path: UPS.Input.LowVoltageTransfer, Type: Feature, ReportID: 0x32, Offset: 0, Size: 16, Value: 155 0.797284 Path: UPS.Input.HighVoltageTransfer, Type: Feature, ReportID: 0x33, Offset: 0, Size: 16, Value: 280 0.797319 Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x35, Offset: 0, Size: 8, Value: 1 0.797398 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6 0.797428 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6 0.797489 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 6 0.797505 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 0, Size: 8, Value: 0 0.797520 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x79, Offset: 0, Size: 8, Value: 0 0.797551 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 0.797580 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 0.797640 Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1 0.797658 Path: UPS.APCGeneralCollection.APCDelayBeforeShutdown, Type: Feature, ReportID: 0x41, Offset: 0, Size: 16, Value: -1 0.797672 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 0.797698 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2 0.797717 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2 0.797736 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2 0.797755 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2 0.797775 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x18, Offset: 0, Size: 8, Value: 2
   0.797794     find_nut_info: unknown info type: load.on.delay
   0.797807     find_nut_info: unknown info type: load.on.delay
   0.797824     upsdrv_initinfo...
   0.797835     upsdrv_updateinfo...
   0.805383     Got 3 HID objects...
0.805426 Path: UPS.PowerSummary.Charging, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.805462 Path: UPS.PowerSummary.Discharging, Type: Input, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.805472 Path: UPS.PowerSummary.APCStatusFlag, Type: Input, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
   0.805480     Quick update...
0.805485 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 0.805493 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 0.805499 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1 0.805505 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 0.805510 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 0 0.805515 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0 0.805521 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.805526 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.805531 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1 0.805536 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 0.805542 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8 0.805637 dstate_init: sock /var/run/nut/usbhid-ups-apc1400 open on fd 5
   0.805651     upsdrv_updateinfo...
   0.813354     Got 3 HID objects...
0.813398 Path: UPS.PowerSummary.Charging, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.813420 Path: UPS.PowerSummary.Discharging, Type: Input, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.813469 Path: UPS.PowerSummary.APCStatusFlag, Type: Input, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
   0.813483     Quick update...
0.813494 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 0.813513 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 0.813527 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1 0.813562 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 0.813574 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 0 0.813588 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0 0.813597 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 0.813607 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 0.813617 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1 0.813627 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 0.813639 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
   2.807708     upsdrv_updateinfo...
   2.813358     Got 2 HID objects...
2.813489 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x0c, Offset: 0, Size: 8, Value: 100 2.813534 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x0c, Offset: 8, Size: 16, Value: 540
   2.813559     Quick update...
2.817362 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: -1 2.823353 Path: UPS.APCGeneralCollection.APCDelayBeforeReboot, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 0 2.827345 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x16, Offset: 2, Size: 1, Value: 1 2.827411 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x16, Offset: 1, Size: 1, Value: 0 2.827507 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x16, Offset: 0, Size: 1, Value: 0 2.827543 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x16, Offset: 4, Size: 1, Value: 0 2.831359 Path: UPS.PowerSummary.Charging, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 0 2.831428 Path: UPS.PowerSummary.Discharging, Type: Feature, ReportID: 0x06, Offset: 8, Size: 8, Value: 0 2.834366 Path: UPS.PowerSummary.ACPresent, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 1 2.839367 Path: UPS.PowerSummary.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 0 2.839452 Path: UPS.PowerSummary.APCStatusFlag, Type: Feature, ReportID: 0x06, Offset: 16, Size: 8, Value: 8
   4.809750     upsdrv_updateinfo...


 Let me know if there is some information missing and thank you.

_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser